[Equest-users] eQuest fan Power
ashu gupta
kce2 at kamalcogentenergy.com
Tue Feb 9 21:05:32 PST 2010
Hi Scott,
In Baseline system, First of all you have to calculate Fan BHP as per G
3.12.9, and then with the help of calculated BHP you can derive the Fan
power (kW) as per section G3.1.29, then you can calculate the kW/CFM for
each system.
Now, you can put this kW/CFM multiplier in eQuest at Design kW/CFM in system
tab/Fan/Fan Flow parameters (Sample attached).
If kW/CFM tab is not activate on your system, go on side tab static (in WG)
and do default, then kW/CFM tab will be activate.
I hope this helps!
Thanks,
Ashu Gupta,
Project Engineer,
Kamal Cogent Energy,
Kamal Ratan Chanbers 1st Floor,
Opp. GPO, M.I. Road,
Jaipur 302001
Ph 141 2373185(W)
Ph 9251665008(M)
<mailto:kce2 at kamalcogentenergy.com> kce2 at kamalcogentenergy.com
<http://www.kamalcogentenergy.com> www.kamalcogentenergy.com
_____
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Tomlinson,
Scott
Sent: Wednesday, February 10, 2010 1:00 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] eQuest fan Power
From: Tomlinson, Scott
Sent: Tuesday, February 09, 2010 2:07 PM
To: 'equest-users at lists.onebuilding.org'
Subject: eQuest fan Power
Hello all,
Can anyone tell me how to enter the Supply fan power, in watts, and the
brake horsepower of the baseline fans into my model? I calculated them
according to ASHRAE 90.1, but can't figure out what to do with them now.
- Thank you,
__________________________________________
Scott Tomlinson, PE, LEED-AP
Mechanical
Symmes Maini & McKee Associates, Inc.
1000 Massachusetts Avenue, Cambridge, MA 02138
t: 617.520.9438
http://intranet/Images/USGBC.jpg
f: 617.354.5758
stomlinson at smma.com
www.smma.com <http://www.smma.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100210/59bfdbc7/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 14792 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100210/59bfdbc7/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Fan KW.JPG
Type: image/jpeg
Size: 77391 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100210/59bfdbc7/attachment-0001.jpeg>
More information about the Equest-users
mailing list