[Equest-users] GSHP-Error
Zareh, Hassan
Hassan.Zareh at stantec.com
Tue Feb 2 10:45:21 PST 2010
Al,
eQUEST doesn't autosize the Ground Loop HX, so you have to define the
GLHX for eQUEST. You can either use some software packags like GLD or do
trial and error by changing the number of borefield and the length of
each whole to size your GLHX in GLHX window in eQUEST.
Hope this helps.
Hassan
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Al
Rahbar
Sent: Tuesday, February 02, 2010 1:31 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] GSHP-Error
I receive the following error message when attempting to run
simulation:
Ground-loop HX: GLHX (VertWell-CM)
is undersized for the load and is producing an extreme
temperature of 151F. Mon/Day/Hr: 6/ 3/17
I need help.
Al R. Rahbar, EIT
BAA Mechanical Engineers, Inc.
500 Bishop St.
Suite F-3
Atlanta, Georgia 30318
T. 404 355-0050 ext. 218
F. 404 355-1050
alr at baamech.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100202/d4d91b6d/attachment.htm>
More information about the Equest-users
mailing list