[Equest-users] Occupancy Sensors
Mark Nieman
MARKN at McKinstry.com
Mon Aug 30 15:51:52 PDT 2010
I have done this in the past with a multiplier, say a 10% reduction with
occupancy sensor vs. without. Here's an example where I've used a global
parameter to use 90% of the baseline values. The #pa("Light OS Occ
Factor") pulls the variable Light OS Occ Factor from the global
parameter.
$ ---------------------------------------------------------
$ Global Parameters
$ ---------------------------------------------------------
PARAMETER
"Light OS Occ Factor" = 0.9 ..
$ ---------------------------------------------------------
$ Day Schedules
$ ---------------------------------------------------------
"Lt OS WD" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0, &D, &D, &D, &D, {.1*#pa("Light OS Occ
Factor")},
&D, {.3*#pa("Light OS Occ Factor")},
{.9*#pa("Light OS Occ Factor")}, &D, &D, &D, &D, &D, &D, &D,
&D,
{.5*#pa("Light OS Occ Factor")}, {.3*#pa("Light OS Occ
Factor")},
&D, {.2*#pa("Light OS Occ Factor")}, &D,
{.1*#pa("Light OS Occ Factor")}, 0 )
..
"Lt OS Sat" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0, &D, &D, &D, &D, &D,
{.1*#pa("Light OS Occ Factor")}, &D,
{.3*#pa("Light OS Occ Factor")}, &D, &D, &D,
{.15*#pa("Light OS Occ Factor")}, &D, &D, &D, &D, 0 )
..
Mark Nieman, PE, CEM | McKinstry | Sr. Energy Engineer
d 206.832.8152 | m 206.510.4760 | f 206.832.8552
FOR THE LIFE OF YOUR BUILDING
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Charles
Welch
Sent: Monday, August 30, 2010 2:21 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Occupancy Sensors
Anybody know a good way to handle occupancy sensors in rooms?
Thanks,
Charles Welch
This email is the property of McKinstry or one of its affiliates and may contain confidential and/or privileged information. If you are not the intended recipient or have received this e-mail in error please notify the sender immediately and delete this e-mail.
Any unauthorized copying, disclosure or distribution of the material in this e-mail is strictly forbidden.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100830/1da01571/attachment.htm>
More information about the Equest-users
mailing list