[Equest-users] "Layer by Layer Construction" errors
Sheila
sheila at energyopportunities.com
Fri Aug 27 12:13:53 PDT 2010
Hi Charles,
If all materials in your layers use the simplified resistance entry
format, there is no mass associated with the wall. When using the layer
methodology, you must use the "properties" format for the majority of
your materials. The properties format includes specific heat and
density input values. The layer constructions require specific heat and
densities in order to take thermal mass into account in the load and
energy balance calculations. If you do not want the thermal mass taken
into account, you can use a simplified construction and specify a user
defined U-value. Keep in mind that Appendix G requires thermal mass
calculations to be done for both the Proposed and Baseline buildings.
Simplified constructions should only be used during very early schematic
design runs for quick snapshots.
Regards,
Sheila Sagerer
Energy Engineer, EIT, LEED AP
Energy Opportunities, Inc, a 7group company
Phone: 717-880-9069
www.sevengroup.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Charles
Welch
Sent: Friday, August 27, 2010 2:53 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] "Layer by Layer Construction" errors
When I am creating a wall and choose "Layer-by-Layer Construction" as my
input and specify a resistance, my runs come up with the following
error:
WALL has no heat capacuty. U_VALUE used
Any ideas where I am going wrong here?
Thanks,
Charles Welch