[Equest-users] LEED submission and warnings
Sheila
sheila at energyopportunities.com
Fri Aug 27 11:48:42 PDT 2010
Good afternoon Amber,
The warnings of "cooling (or heating ) may be undersized" are very
common (and often meaningless) warnings in eQuest, and the reviewers are
aware of this.
If the T24 compliance forms say that the building complies, then there
is no need to worry about these warnings.
If using ASHRAE compliance, as long as the unmet load hours are below
300 for each building, again, there is no need to worry. If there are
excessive unmet load hours, only then should you go back in and manually
increase the capacity of the appropriate coil as allowed in G3.1.2.2.
A word of caution: Increasing the coil capacity should only be employed
as a last resort for reducing the unmet load hours. It is important to
understand why the unmet load hours are showing up. There are many
sources of error in eQuest which result in unmet load hours which cannot
be corrected just by increasing the coil capacity. Often, mis-matched
schedules are the source of unmet load hours and increased coil sizes do
not reduce the number of unmet load hours.
A couple examples:
1. The temperature schedule setting is set to the occupied temperature
of 75F, but the fan is scheduled off that hour
2. The temperature schedule gradually increases the tstat setting to
mimic optimum start, but the OA schedule has full OA coming in during
that optimum start.
I hope this helps.
Regards,
Sheila Sagerer
Energy Engineer, EIT, LEED AP
Energy Opportunities, Inc, a 7group company
Phone: 717-880-9069
www.sevengroup.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Amber
Welsh
Sent: Friday, August 27, 2010 1:58 PM
To: EQUEST
Subject: [Equest-users] LEED submission and warnings
Hi all,
I am preparing a model showing T-24 compliance that will also be
submitted for LEED. The model passes T-24. However, I have about 10
warnings saying some systems may have undersized cooling and some have
undersized heating. As long as it complies, do the warnings matter?
Will someone reviewer make me go back and try and change system sizing
to get rid of warning? Thank you!!
Amber Welsh, P.E. | Associate
LEED(r) Accredited Professional
397 5th Street NE,
Atlanta, GA 30308
(v) 404.810.9020
(c) 678.488.1967
timmonsdesigneng.com <http://timmonsdesigneng.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100827/0fdd73eb/attachment.htm>
More information about the Equest-users
mailing list