[Equest-users] Modeling Light Shelves for Reduction inCooling/Heating Load?
Nick Caton
ncaton at smithboucher.com
Mon Aug 23 12:49:10 PDT 2010
Perhaps these are the answers you're seeking:
1. Building shades and their respective reflectance properties do
affect the modeled behavior of space daylighting systems in eQuest
models. Be sure to pay close attention to all three values (and their
associated help files) on the right of the following image - they may
all play a part depending on what exactly you're trying to model.
2. Based on your query, a caution: eQuest's results do not have
any inherent degree of accuracy/in-accuracy with regard to the modeled
energy consumption resulting from daylighting controls - that depends
pretty much entirely on how closely you define the daylighting systems'
behavior to reality. If you have a program which you perceive to be
producing more accurate hourly percentage consumptions for your spaces,
then by all means - there's nothing stopping you from defining a
schedule in eQuest to match the other program's results.
I expect you mean to say you're utilizing another program to accurately
determine the behavior of daylight in response to adding/modifying light
shelves, but if you are indeed using another program to determine annual
hourly behavior with a weather file, I'd be very interested to hear more
about it!
Best of luck,
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nilay
R. Desai
Sent: Monday, August 23, 2010 11:35 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Modeling Light Shelves for Reduction
inCooling/Heating Load?
E.G. Would it be accurate to model an external light shelve as a
horizontal building shade with a high reflectance value on the skyward
facing surface? I understand the day lighting benefit in Equest would be
inaccurate, but we are using separate software to obtain accurate day
lighting results. Thanks!
Nilay Desai
P 626.351.8881 Ext. 237
ndesai at ttgcorp.com <mailto:klowe at tmadtg.com>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100823/cdef5659/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 13601 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100823/cdef5659/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100823/cdef5659/attachment.jpeg>
More information about the Equest-users
mailing list