[Equest-users] Modeling Variable Speed Air Cooled Screw Chillers
Brian Fountain
bfountain at greensim.com
Wed Aug 18 10:45:35 PDT 2010
On the energy design resources website (www.energydesignresources.com)
there is a design guideline called "HVAC Simulation Guidelines" which
includes a section on "energy efficient chillers" and has a procedure
for developing custom chiller curves for DOE-2 -- including a table to
send to the manufacturer to get the required information.
There is also the CoolTools spreadsheet tool which also generates the
DOE-2 curve coefficients -- but I haven't played with it much so will
let others comment on its use/applicability to screw compressors.
On 8/18/2010 1:26 PM, Mohammad Almasri wrote:
> Dear Paul,
> how I can get those data points to build the EIR-fPLR&DT curve? is it
> available in the manuals and chillers data sheets? or I should ask it
> from the suppliers directly?
>
> Please advice,
>
> Mohammad Al-Masri
> Simulation Engineer
> LEED AP BD+C, CAPM
>
> On Tue, Aug 17, 2010 at 4:45 PM, Paul Riemer
> <Paul.Riemer at dunhameng.com <mailto:Paul.Riemer at dunhameng.com>> wrote:
>
> If you ask a manufacturer's rep how a chiller unloads at part
> load, the answer might be "good". So I suggest you specifically
> request part load points at 10% intervals with and without AHRI
> condenser relief. That should enable you to make or confirm both
> the EIR-fPLR&DBT and the EIR-fCHWT&DBT curves.
>
> If you want to go even deeper, you could ask for those part load
> points at different chilled water supply temperatures and then
> make or confirm a Cap-fCHWT&DBT curve. That seems like
> overachieving to me, but my chilled water supply temperatures
> rarely deviate very far from AHRI standard conditions.
>
> Good luck,
>
> *Paul Riemer, PE, LEED AP*
>
> Associate / Mechanical
>
> Direct: 612-465-7696
>
> *DUNHAM*
> Celebrating 50 Years of Service
>
> *From:* equest-users-bounces at lists.onebuilding.org
> <mailto:equest-users-bounces at lists.onebuilding.org>
> [mailto:equest-users-bounces at lists.onebuilding.org
> <mailto:equest-users-bounces at lists.onebuilding.org>] *On Behalf Of
> *Carol Gardner
> *Sent:* Tuesday, August 17, 2010 9:22 AM
> *To:* Mohammad Almasri
> *Cc:* eQUEST-users at onebuilding.org
> <mailto:eQUEST-users at onebuilding.org>
> *Subject:* Re: [Equest-users] Modeling Variable Speed Air Cooled
> Screw Chillers
>
> Mohammad,
>
> You will need to ask the manufacturer for information on how the
> chiller unloads at part load so you can create an EIR-FPLR curve
> of your own. That shouldn't be too hard. It looks like there's no
> problem with having the water from the chillers flow using
> variable speed pumps so that part's there if you want it. Let me
> know if you need help creating a curve.
>
> Carol
>
> On Tue, Aug 17, 2010 at 1:54 AM, Mohammad Almasri
> <malmasri at ems-int.com <mailto:malmasri at ems-int.com>> wrote:
>
> Hi all,
>
> How we can model a Variable Speed "Air Cooled" Screw Chillers in
> eQUEST? The
> available variable speed chillers curves in eQUEST are only for the
> centrifugal .
>
> Thanks,
>
> Mohammad Al-Masri
> Simulation Engineer
> LEED AP BD+C, CAPM
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
> <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
>
>
> --
> Carol Gardner PE
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
> No virus found in this incoming message.
> Checked by AVG - www.avg.com
> Version: 9.0.851 / Virus Database: 271.1.1/3079 - Release Date: 08/18/10 02:35:00
>
--
Brian Fountain, Principal
GreenSim
voice - 519-489-0112
email - bfountain at greensim.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100818/446912cb/attachment.htm>
More information about the Equest-users
mailing list