[Equest-users] Negative Cooling Load
Montague, Lilah
Lilah.Montague at perkinswill.com
Wed Aug 11 10:30:24 PDT 2010
A few other comments...
There is definitely something wrong when all 100% hours are outside of your throttling zone.
On your PS-F report, in your sim file, your space cooling loads are higher in the winter than in the summer. This is unexpected for the Regina climate. Also, it does not look like your area lights are on in January and December?
I would check your schedules, to ensure your lighting, equipment, occupancy, heating, cooling, and fan profiles are realistic. Also, on your SS-E file, you have a lot of coincidental heating and cooling loads. Might be something going on there.
Best of luck! Lots of systems to juggle in this one, it seems.
Lilah
Lilah Montague, B.Eng. EIT LEED(r) AP
Sustainable Building Energy Advisor
1220 Homer St., Vancouver, BC V6B 2
t: 604.484.2258 f: 604.684.5447 e: Lilah.Montague at perkinswill.com<mailto:Lilah.Montague at perkinswill.com> http://www.busbyperkinswill.ca<http://www.busbyperkinswill.ca/>
Busby Perkins+Will. Ideas + buildings that honor the broader goals of society
[cid:image001.jpg at 01CB3940.3555B290]<http://75.perkinswill.com/>Years of Design Innovation
This email and any files transmitted with it are confidential and intended solely for the addressee.
If you are not the named addressee you should not disseminate, distribute, copy, or alter this email.
Please consider the environment before printing this email.
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Shaun Martin
Sent: Wednesday, August 11, 2010 10:15 AM
To: aazhari at jainconsultants.com; Sami, Vikram; 'John Aulbach'; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Negative Cooling Load
Yes, EE4 does this sort of thing. Specify that a cooling plant exists, but with 0 Btu capacity.
Shaun Martin LEED AP
Principal
Shaun Martin Consulting
Suite 200 - 420 West Hastings Street
Vancouver, BC V6B 1L1
c: 604-789-1095
e:smartin at shaunmartinconsulting.com
member CAGBC, ASHRAE
________________________________
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Ahmed Azhari
Sent: August 11, 2010 9:32 AM
To: 'Sami, Vikram'; 'John Aulbach'; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Negative Cooling Load
I, in fact, don't have a .INP and .PD2 because I am not using equest. I am however using a similar software (EE4-Canadian Based) that uses DOE simulation engine. I have attached the doe-2 .sim file for review if that would help.
Thanks,
Ahmed
From: Sami, Vikram [mailto:Vikram.Sami at perkinswill.com]
Sent: Wednesday, August 11, 2010 12:04 PM
To: John Aulbach; aazhari at jainconsultants.com; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Negative Cooling Load
I'm curious too. The BEPS is not a loads report - its an energy performance report, so the cooling numbers that show up here are really cooling energy numbers.
It would be nice to see the inp file
Vikram Sami, LEED AP
Sustainable Design Analyst
1382 Peachtree St. NE, Atlanta, GA 30309
t: 404-443-7462 f: 404.892.5823 e: vikram.sami at perkinswill.com www.perkinswill.com<http://www.perkinswill.com/>
Perkins+Will. Ideas + buildings that honor the broader goals of society
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John Aulbach
Sent: Wednesday, August 11, 2010 11:59 AM
To: aazhari at jainconsultants.com; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Negative Cooling Load
It would helpt o view your .INP and .PD2 files, sir.. This is a new one on me..
________________________________
From: Ahmed Azhari <aazhari at jainconsultants.com>
To: equest-users at lists.onebuilding.org
Sent: Wed, August 11, 2010 6:17:09 AM
Subject: [Equest-users] Negative Cooling Load
Hi all,
In the DOE file in the BEPS Report (Building Energy Performance Summary Report) the cooling load is negative. Does anyone know what would that possibly mean?
Regards,
__________________________________________________________________________
Ahmed Azhari, B.Eng., LEED(r) AP
Energy Analyst
Jain Sustainability Consultants Inc.
2260 Argentia Road, 2nd Floor
Mississauga, Ontario L5N 6H7, CANADA
Tel: (905) 542 7211 Ext 234
Fax: (905) 542 7622
Email: aazhari at jainconsultants.com<mailto:aazhari at jainconsultants.com>
Web: www.jainassoc.com<http://www.jainassoc.com/>
NOTICE OF CONFIDENTIALITY
This communication, including any attachments, is intended only for the use of the addressees and is confidential.
If you received this communication in error, please permanently delete the entire communication from any computer or other storage medium.
[cid:image002.gif at 01CB3940.3555B290]Please consider your environmental responsibility before printing this e-mail & any documents
__________ Information from ESET Smart Security, version of virus signature database 5357 (20100811) __________
The message was checked by ESET Smart Security.
http://www.eset.com
This email and any files transmitted with it are confidential and intended solely for the addressee. If you are not the named addressee you should not disseminate, distribute, copy, or alter this email.
__________ Information from ESET Smart Security, version of virus signature database 5358 (20100811) __________
The message was checked by ESET Smart Security.
http://www.eset.com
__________ Information from ESET Smart Security, version of virus signature database 5358 (20100811) __________
The message was checked by ESET Smart Security.
http://www.eset.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100811/24bde00d/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 954 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100811/24bde00d/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.gif
Type: image/gif
Size: 1257 bytes
Desc: image002.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100811/24bde00d/attachment.gif>
More information about the Equest-users
mailing list