[Equest-users] Modeling Window changes
Matutinovic, Luka
LMatutinovic at halsall.com
Fri May 29 07:29:09 PDT 2009
John,
It's difficult to diagnose your issue without having the .inp and .pd2
files to review.
What do you mean by "more energy efficient"? If you are referring to
U-value, the result does seem counter-intuitive (unless the negative
result is actually a reduction in energy shown as a "negative"). If
however, you consider a reduction in the SHGC to be more energy
efficient, this may in fact lead to increased energy use in heating
dominated climates since less solar gain is available in the winter. As
I said, seeing the simulation would be helpful.
Cheers,
Luka Matutinovic, B.A.Sc., LEED(r) AP
Green Building Consultant
T. 416.487.5257 ext. 317
F. 416.487.9766
Toll Free 1.888.425.7255
www.halsall.com
HALSALL ASSOCIATES LTD.
Toronto Richmond Hill Ottawa Sudbury
Burlington Calgary Vancouver Dubai
'Best Workplaces in Canada'
2009 Globe and Mail
P Please consider the environment before printing this e-mail
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
jklikape at aol.com
Sent: Friday, May 29, 2009 10:23 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Modeling Window changes
Good Morning,
My associate and I are beginners on the E-Quest program and are feeling
our way around the program. Among many other questions that we may have
we are in a quandry as to why, when we use a more energy efficient
window in the EEM module, the results show a negative effect in our
simulation. Is there some basic fundimental we,re missing here?
John Klika
KGZ Consulting Engineers, Ltd.
Joliet, Illinois
815-714-2818
________________________________
Wanna slim down for summer? Go to America Takes it Off
<http://www.aolhealth.com/diet/weight-loss-program/?ncid=emlcntusheal000
00001> to learn how.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090529/bdfce3f8/attachment.htm>
More information about the Equest-users
mailing list