[Equest-users] Heat recovery issues
Doy S
dsan2525 at yahoo.com
Mon May 18 17:57:33 PDT 2009
Hi,
I have the same situation, My basline is using DX coils with furnace for warm up heat and VAV with electric coils for re heat. The addition of a dual enthalpy wheel heat recovery system caused the energy consumption to increase. I changed the default control to "Mixed Air Reset" and the consumption dropped significantly but is still slightly higher than the baseline run. Any other thoughts?
Thanks,
Doy Sanguyu
--- On Thu, 5/14/09, B. Fountain <bfountain at greensim.com> wrote:
From: B. Fountain <bfountain at greensim.com>
Subject: Re: [Equest-users] Heat recovery issues
To: "Grove, Rebecca" <RGrove at ThorntonTomasetti.com>
Cc: equest-users at lists.onebuilding.org
Date: Thursday, May 14, 2009, 9:28 AM
Note that the eQUEST default control for heat recovery is "Float" which
maximizes heat recovery at all times. Consider changing this to "Mixed
Air Reset" where heat recovery will be modulated, allowing economizer free
cooling when applicable.
> I seem to be running into a slight problem getting the heat recovery
> system to work. Right now I have it set as a sensible wheel with an
> airflow of 35315 cfm and an efficiency of 60% (all according to the
> specifications given to me). Unfortunately, using the heat exchanger
> actually causes my energy consumption to increase. Do you have any idea
> why this might be happening and what I can do to fix it?
>
>
> Rebecca Grove, LEED AP
> Senior Engineer
> Thornton Tomasetti
> One Audubon Street, Fourth Floor
> New Haven, CT 06511
> T 203.672.1390 F 203.672.1391
> D 203.672.1436
> RGrove at ThorntonTomasetti.com
> www.ThorntonTomasetti.com
>
> <><><><><><><><><><><><><><><><><><><><><><><><><><><><><><><>
> The information in this email and any attachments may contain
> confidential information that is intended solely for the
> attention and use of the named addressee(s). This message or
> any part thereof must not be disclosed, copied, distributed
> or retained by any person without authorization from the
> addressee. If you are not the intended addressee, please
> notify the sender immediately, and delete this message.
> <><><><><><><><><><><><><><><><><><><><><><><><><><><><><><><>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090518/7eb4ac90/attachment.htm>
More information about the Equest-users
mailing list