[Equest-users] Number of heating hours not met

David Dowling David.Dowling at WestPlainsEngineering.com
Wed May 13 07:12:08 PDT 2009


I think I might have figured it out and thank you Charles for directing
me to the system type.  

 

I originally had the system set up as system per site.  I just now
changed it to system per zone and it seemed to remove the error.  It
also dropped the percentage any system zone is out side the throttling
range from 100 to 3.5.

 

 

David Dowling

Mechanical Designer

WEST PLAINS ENGINEERING, INC.

1750 Rand Road

Rapid City, SD  57702

Phone: (605) 348-7455  Fax: (605) 348-9445

david.dowling at westplainsengineering.com

www.westplainsengineering.com <http://www.westplainsengineering.com/> 

 

 

________________________________

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of David
Dowling
Sent: Wednesday, May 13, 2009 7:46 AM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Number of heating hours not met

 

I am using the ASHRAE 90.1-2004 compliant system number 3 which happens
to be DX Coils with Furnace.  

 



David Dowling

Mechanical Designer

WEST PLAINS ENGINEERING, INC.

1750 Rand Road

Rapid City, SD  57702

Phone: (605) 348-7455  Fax: (605) 348-9445

david.dowling at westplainsengineering.com

www.westplainsengineering.com <http://www.westplainsengineering.com/> 

 

 

________________________________

From: Charles Land [mailto:cland at geo-marine.com] 
Sent: Wednesday, May 13, 2009 6:12 AM
To: David Dowling; equest-users at lists.onebuilding.org
Subject: RE: Number of heating hours not met

 

What type of systems are you using?

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of David
Dowling
Sent: Tuesday, May 12, 2009 6:32 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Number of heating hours not met

 

I have a question concerning a warning related to the number of heating
hours not met and apologize in advance if this topic has been covered
before.  The warning I am getting is:

 

"Zone might have insufficient heating capability.  Check that the system
or zone HEATING-CAPACITY plus this zones BASEBOARD-RATING is adequate to
maintain the zone specified DESIGN-HEAT-T for the calculated peek zone
load (see LS-A or LS-B for the zone peak load)."

 

I am using the auto sizing function within eQuest so I am not
understanding why the spaces are not satisfied.  Dose anyone know how to
make the auto size function work to satisfy each zone?

 



David Dowling

Mechanical Designer

WEST PLAINS ENGINEERING, INC.

1750 Rand Road

Rapid City, SD  57702

Phone: (605) 348-7455  Fax: (605) 348-9445

david.dowling at westplainsengineering.com

www.westplainsengineering.com <http://www.westplainsengineering.com/> 

 

 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090513/991c07a7/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 4427 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090513/991c07a7/attachment.jpeg>


More information about the Equest-users mailing list