[Equest-users] ASHRAE 62.1 cfm/person
Jeremy Poling
jpoling at epsteinglobal.com
Tue Mar 31 06:50:16 PDT 2009
eQuest also takes a total CFM value instead of the CFM/person value.
This is specified on the Outdoor Air tab of the Zone in the box labeled
"Air Flow". The value of this box overrides all other CFM values
entered. Just remember that eQuest applies an adjustment factor to
account for elevational differences in air density based on the
elevation entered in the Site Data form - this will cause the values in
the reports to be higher than what you entered into the Air Flow box.
Jeremy R. Poling, LEED AP
Senior Sustainability Analyst
Strategic Services
Site Solutions | Operations | Sustainability
EPSTEIN
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090331/fca7c1af/attachment.htm>
More information about the Equest-users
mailing list