[Equest-users] Changing window types with parametric simulation
eric wang
shaojieworld2006 at yahoo.com
Thu Mar 26 12:32:04 PDT 2009
Josh,
I guess you created a new glass code in the project. However, there is no glass type that uses this glass code as library selection under glass types. So, eQUEST removes the new glass code automatically. What you can do is to create a new glass type with the glass code you want to keep for the parametric runs even though that glass type is not used anywhere in the building.
Hpe this helps
Shaojie
--- On Thu, 3/26/09, Josh Doherty <jdoherty at dcengineering.net> wrote:
From: Josh Doherty <jdoherty at dcengineering.net>
Subject: [Equest-users] Changing window types with parametric simulation
To: "equest-users at lists.onebuilding.org" <equest-users at lists.onebuilding.org>
Date: Thursday, March 26, 2009, 2:00 PM
I am having problems changing window types via a parametric run. The following error keeps popping up when I run the simulation:
Here is a screen shot of the parametric run that I specify.
Does anyone see a problem with this or have an idea of what I am doing wrong? Thanks so much.
Josh Doherty
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090326/0324b547/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 21828 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090326/0324b547/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 59519 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090326/0324b547/attachment-0001.jpg>
More information about the Equest-users
mailing list