[Equest-users] Location of HVAC Equipment
Bishop, Bill
bbishop at PathfinderEngineers.com
Tue Jan 27 11:54:02 PST 2009
Niko,
See the descriptions below from the DOE-2 help menu. Looks like the
boiler sees the zone, but the zone doesn't see the boiler.
Bill
LOCATION
Accepts a code-word that specifies the location of the boiler:
OUTDOOR The boiler is located outdoors.
ZONE The boiler is located within a zone.
Note that the program does not model any zonal heat gain from the
boiler. See ZONE-NAME keyword.
ZONE-NAME
Takes the U-name of the zone containing the heater when LOCATION = ZONE.
You must specify the zone; if not, LOCATION will default to OUTDOOR.
(Partially implemented; the program will use the zone temperature when
calculating the tank losses or the performance of a HEAT-PUMP water
heater, however these interactions do not have any effect on the zone
temperature. For heat-pump water heaters, this can result in serious
errors.)
William Bishop, EIT, LEED(r) AP | Pathfinder Engineers LLP
Mechanical Engineer
3300 Monroe Ave., Suite 306
Rochester, NY 14618
TEL (585) 218-0730 Ext. 114
FAX (585) 218-0737
bbishop at pathfinderengineers.com
www.pathfinderengineers.com
P Please consider the environment before printing this email
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Niko
Michael Kalinic
Sent: Tuesday, January 27, 2009 2:36 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Location of HVAC Equipment
Hello All,
Can anyone explain why after placing HVAC equipment such as a boiler in
a particular thermal zone that is unconditioned there are no visible
changes in space temperature while the equipment is operating. Does
eQUEST not see the boiler as an internal gain?
Thank You,
Niko
--
Niko Michael Kalinic
University of Colorado
Building Systems Program
kalinic at colorado.edu
cell: (303)887-5685