[Equest-users] Hours outside of throttling range -VAV system
James Geers
jgeers at sfa-architects.com
Tue Jan 20 12:47:15 PST 2009
Using "Cycle on Any" does the trick. Thank you. Will this affect my DCV?
James F. Geers
Registered Architect
LEED Accredited Professional
SFA Architects
300 West Fourth Street
Cincinnati, Ohio 45202
513.721.0600
513.721.0611 (fax)
_____
From: Howe, Timothy [mailto:Timothy.Howe at stantec.com]
Sent: Tuesday, January 20, 2009 3:28 PM
To: James Geers; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Hours outside of throttling range -VAV system
Go to: Air-side HVAC System Parameters -> Fans -> Night Cycle Control ->
Select: Cycle on any.
Timothy Howe, MS, LEEDR AP
Mechanical Engineer
_____
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of James Geers
Sent: Tuesday, January 20, 2009 3:13 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Hours outside of throttling range -VAV system
I likewise have been having enormous trouble reducing the hours outside of
the throttling range for my design case building. In the winter months in
the morning I will have multiple hours outside of the throttling range for
multiple zones and this exceeds 300 hours.
Things I have varied but did not solve the problem include:
1. Occupancy schedule
2. Heating Design Day Schedule
3. Night Setback Temperature
4. Boiler Size
5. Loop Capacity
6. Pump Size
7. Delta T for heating and Pre-heating coils
8. Minimum Outside Air
9. Throttling Range
10. Design temperature
At this point I am randomly changing settings to reduce the amount of hours
outside of throttle range, but I would like to have a more deductive
process.
I have a suspicion that there was a setting in the wizard that is overriding
my inputs, but that is conjecture.
My engineer designed the system in Trane Trace and oversized it by 25% so
the designed heating equipment should be adequate.
Thank you,
James F. Geers
Registered Architect
LEED Accredited Professional
SFA Architects
300 West Fourth Street
Cincinnati, Ohio 45202
513.721.0600
513.721.0611 (fax)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090120/b4e4862b/attachment.htm>
More information about the Equest-users
mailing list