[Equest-users] Modeling Dormers
Bishop, Bill
bbishop at PathfinderEngineers.com
Tue Jan 13 12:19:30 PST 2009
Hi Ryan,
I think what you have done will work, but you're not finished yet. The
geometry within geometry is not ignored. You can verify this several
ways. For example, the floor area of the sloped-roof space is probably
identical before and after adding the "brick" dormer. The conduction
loads to the space are probably identical. The solar load, however, may
be reduced due to shading by the dormer shell.
Another thing you should check is whether or not the area "inside" the
sloped roofs is conditioned or not (and that you don't just have a 1'
tall conditioned space). The last project I did with sloped roofs,
eQUEST generated an unconditioned "Under Roof" space with all the roof
surfaces assigned to it. If the conditioned volume checks out, I think
you need to make the following additions/modifications:
1.) Modify the floor polygon of the sloped-roof space to subtract the
area of the dormer.
2.) Modify the roof polygon to subtract the dormer.
3.) Add an interior wall, air-type, for the long
"geometry-within-geometry" wall, NEXT-TO the sloped-roof space.
4.) Delete the exterior wall that the interior wall replaces.
5.) Modify the other two exterior walls. Make them triangles by creating
new polygons.
Hope that helps,
Bill
William Bishop, EIT, LEED(r) AP | Pathfinder Engineers LLP
Mechanical Engineer
3300 Monroe Ave., Suite 306
Rochester, NY 14618
TEL (585) 218-0730 Ext. 114
FAX (585) 218-0737
bbishop at pathfinderengineers.com
www.pathfinderengineers.com
P Please consider the environment before printing this email
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Ryan
Lacey
Sent: Tuesday, January 13, 2009 9:24 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Modeling Dormers
Hello,
I am attempting to model the roof & top floor of my building. It is a
12/12 roof with intersecting dormers and a flat section of roof. There
is no magical way to make this happen from what I can tell. I wish
there was a "easy button" like in those commercials! My best solution
so far has been to create a 1' tall wall & build a 12/12 roof on it.
Rather than build the roof on my 3rd floor, building the 1' wall allows
me to apply my w/sf and occupancy densities for that 1' wall floor area.
To represent the dormers and protruding geometry I plan on modeling
intersecting shells. Is there any issue with this method? See below
the image of the dormer and then the X-ray image showing that the brick
shaped block representing the dormer. The block has geometry extending
into the conditioned space. It this an issue? Is geometry within
geometry ignored in eQUEST? If anybody has any dormer modeling methods,
I would greatly appreciate some tips!
Thanks!
Ryan Lacey
LEED AP
Petersen Engineering, Inc.
PO Box 4774
6 Market Square
Portsmouth, NH 03801
Phone 603.436.4233 x113
Fax 603.436.4294
www.petersenengineering.com
ryan at petersenengineering.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090113/a8d30599/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 15757 bytes
Desc: image004.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090113/a8d30599/attachment.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 22113 bytes
Desc: image003.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090113/a8d30599/attachment-0001.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 6073 bytes
Desc: image002.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090113/a8d30599/attachment-0002.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 18755 bytes
Desc: image001.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090113/a8d30599/attachment-0003.gif>
More information about the Equest-users
mailing list