[Equest-users] Sizing of equipment
Sam Mason
sam.mason at atelierten.com
Tue Jan 13 08:26:46 PST 2009
Janne,
Without information on HW loop temp, cooling system type and control,
and heating control, it's tough to figure out what is going on with your
model. That being said, I will provide what help I can. The sizing
ratios on the coils only increase the coil size and do not increase
airflow which is generally why zones will have hours out of range.
Check the minimum flow ratio and airflow to your zones and make sure
they are appropriate for the loads in the space. With regards to your
system setup, make sure your reheat setpoints and supply air setpoints
are consistent.
For future reference, if you provide the input file, myself or others on
the list serve will be able to better respond to future questions.
Sam
--
Sam Mason
Atelier Ten
sam.mason at atelierten.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Kairento, Janne
Sent: Tuesday, January 13, 2009 11:03 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Sizing of equipment
Hey All,
I am running a load with many zones on 5 floors totaling over 300 zones.
There are some zones with many unmet hours, some of the core, some
perimeter. I went in and changed the sizing ratio of these zone to
reduce the unmet heating hours. I am modeling this building with 9
AHU's, all VAV w/ reheat. Does anyone have any insight or suggestions on
why or how these unmet hrs. exist. I have changed the hot water loop
flow GPM but it had no effect on the unmet heating hrs. so I deduced
this is not the cause.
Janne Kairento, E.I.T., LEED AP
Cosentini Associates
One Broadway
Cambridge, MA 02142
Phone: 617.494.9090
Fax: 617.494.9292
Please consider the environment before printing this e-mail
NOTICE OF CONFIDENTIALITY This E-mail message and its attachments (if
any) are intended solely for the use of the addressees hereof. In
addition, this message and the attachments (if any) may contain
information that is confidential, privileged and exempt from disclosure
under applicable law. If you are not the intended recipient of this
message, you are prohibited from reading, disclosing, reproducing,
distributing, disseminating or otherwise using this transmission.
Delivery of this message to any person other than the intended recipient
is not intended to waive any right or privilege. If you have received
this message in error, please promptly notify the sender by reply E-mail
and immediately delete this message from your system.
________________________________________________________________________
This e-mail has been scanned for all viruses by Star. The
service is powered by MessageLabs. For more information on a proactive
anti-virus service working around the clock, around the globe, visit:
http://www.star.net.uk
________________________________________________________________________
______________________________________________________________________
This email has been scanned by the MessageLabs Email Security System.
For more information please visit http://www.messagelabs.com/email
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090113/524da395/attachment.htm>
More information about the Equest-users
mailing list