[Equest-users] Min OA schedule

Brahme, Rohini UTRC BrahmeR at utrc.utc.com
Tue Jan 13 07:15:23 PST 2009


To answer my own question -

 

The hourly reports match the min OA-schedule when the min OA control
method is set at Fraction of Hourly Flow. Did not realize that he
Min-Air-Sch does not override the Min-OA control method.

 

-Rohini

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Brahme,
Rohini UTRC
Sent: Monday, January 12, 2009 4:30 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Min OA schedule

 

I have been struggling with this for a while without much success.

I have a schedule for the Min-Air-Schedule under the outdoor air tab for
systems. No other outdoor air keyword anywhere (no cfm/person in zones
or economizer, or min outside air). When I look at the hourly report,
the OA to supply ratio does not match the schedule. Also, OA cfm as a
ratio of design supply cfm, or design OA cfm - does not match the
schedule. What does this keyword do? The system is a dual duct variable
speed.

Any pointers appreciated.

-Rohini

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090113/6e1be7c8/attachment.htm>


More information about the Equest-users mailing list