Since eQUEST doesn't model airflow or natural convection, you can model
radiant cooling with no ventilation by using a fan coil or VAV system
with no heating or economizer installed and set the fan efficiency at 0
kW/CFM.

We design a lot of radiant systems with separate ventilation (based on
DOE-2 and Title 24, one would think this was a physically impossible
concept) and I usually end up modeling it as an induction system with
100% outside air if I can get away with constant fan control, zones not
too different from each other, and no operable windows. Otherwise, I
have to use one of those nasty old VAV w/reheat systems and fudge the
efficiencies. The arbitrary restrictions in eQUEST can be rather
maddening.

Christopher Wark
Project Engineer
___________________________
RUMSEY 
E N G I N E E R S
Energy Efficient Design 
99 Linden Street
Oakland CA 94607
510 663 2070 x 239
fax 510 663 2080
cwark at rumseyengineers.com <mailto:eswalley at rumseyengineers.com>  
www.rumseyengineers.com <http://www.rumseyengineers.com/> 
___________________________

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Josh
Doherty
Sent: Wednesday, February 25, 2009 12:06 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Radiant Floor Cooling

 

Hello wise ones,

Has anyone ever modeled radiant floor cooling in eQUEST?  I am trying to
determine how difficult it will be to model such a system.  Any input
would be appreciated.  Thanks.

 

Josh Doherty

DC Engineering

123 W. Spruce Street

Missoula, MT 59802

Phone: (406) 829-8828   Ext. 121

Fax:  (406) 829-8829

jdoherty at dcengineering.net

 

 

 

 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090225/a2cea7c7/attachment.htm>


More information about the Equest-users mailing list