[Equest-users] Converting Interior Walls to Exterior Walls
Nick Caton
ncaton at smithboucher.com
Wed Dec 30 07:50:36 PST 2009
I have a guess as to "how this may have happened."
If the corresponding shell in the wizards was ever set up adjacent to
another, the shared planes may have defaulted to "partially adiabatic,"
which would make part of your model look like it has "interior walls"
that are in fact adiabatic.
Rest assured, the zones behind those white rectangles are not behaving
the way it looks: as though they have your internal wall construction on
the exterior. If you were to delete them, the 3D view would look funny,
but it would be the same as having an adiabatic wall in the same
locations (no heat transfer to/from the outside) - that could be a fast
solution.
The "correct" solution, to model the interaction with the exterior world
in those spaces, is to follow Katie's (well-written!) instructions
below. Don't let her caps lock usage scare ya though - this stuff isn't
too excruciating, as long as you do keep your backups in order =). It
may go without saying, but I'll add that you will potentially save
yourself a lot of time by spending a few minutes in your model noting
the exact name of those "interior" looking walls so that you can ctrl+F
them in the .inp file!
Best of luck!
PS: Happy to see more KC-area contributors, Katie! =) If you're still
having trouble finding the DOE2 files and need a quick fix, you can
download them in PDF here: http://www.doe2.com/Download/DOE-22/ (What
you're looking for is volumes 1-6 and 2r). I'd look at simply
reinstalling myself though, for the convenience ;).
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Katie
Tuttle
Sent: Tuesday, December 29, 2009 1:26 PM
To: Kevin Kelly
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Converting Interior Walls to Exterior Walls
Use the .inp file to modify those - that's the best way I know how. The
file is located with your project - open it with notepad. (See below).
You'll have to go find each wall and change them to = EXTERIOR-WALL and
then add the same fields (construction/height/location/shading-surface).
MAKE SURE YOU LEAVE THE TWO PERIODS AT THE END OF EACH WALL, OTHERWISE
YOU'LL MESS UP YOUR FILE. I WOULD DO A SAVEAS ON THIS FILE BEFORE YOU
MODIFY IT IN CASE YOU MESS SOMETHING UP!!! Save that .inp file and then
open your .PD2 file again. Then you can update the construction types.
Hope this helps!
KATIE L. M. TUTTLE EI, LEED(r) AP
Mechanical Designer
Henderson Engineers, Inc. 8325 Lenexa Drive Lenexa, KS 66214
dir 913 742 5508 tel 913 742 5000 fax 913 742 5001 www.hei-eng.com
<http://www.hei-eng.com>
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Kevin
Kelly
Sent: Tuesday, December 29, 2009 1:19 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Converting Interior Walls to Exterior Walls
Good Afternoon,
I have two (2) of the approximately 50 exterior walls that somehow along
the way were modeled as interior walls. The model is very close to
completion and has a many edits in detailed interface. Is there any way
to convert these walls into exterior walls?
I have never added any spaces or changed any zone layouts outside of the
wizards. I am assuming that is what I will end up doing, but I was just
checking to see if there was a quick fix that I couldn't find.
Anyone have any clue how this could have happened?
I included a screen shot of my 3D model with the specific walls
highlighted.
Thank you everyone, and have a happy new year!
Kevin Kelly. LEED AP
R3 Energy
Energy Systems Analyst
914.909.3940 x115
kkelly at r3energy.com
This email and any files transmitted with it are confidential and
are intended solely for the use of the individual or entity to whom
they are addressed. This communication represents the originator's
personal views and opinions, which do not necessarily reflect those of
Henderson Engineers, Inc. If you are not the original recipient or the
person responsible for delivering the email to the intended recipient,
be advised that you have received this email in error, and that any use,
dissemination, forwarding, printing, or copying of this email is
strictly
prohibited. If you received this email in error, please immediately
notify administrator at hei-eng.com.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091230/88e75e59/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091230/88e75e59/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 92941 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091230/88e75e59/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 5566 bytes
Desc: image005.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091230/88e75e59/attachment.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: interior walls on the exterior.jpg
Type: image/jpeg
Size: 36535 bytes
Desc: interior walls on the exterior.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091230/88e75e59/attachment.jpg>
More information about the Equest-users
mailing list