[Equest-users] IPLV in Heat Pumps
Jonathan Curtin
jcurtin at WylieAssociates.com
Mon Dec 21 06:52:56 PST 2009
All,
The ASHRAE Journal December 2009 Issue has a fitting article "A Closer
Look at Chiller Ratings" highlighting the problems of over-reliance on
IPLV/NPLV for use with chillers, and specifically what type of impact
climate has on these ratings. Lesson: be wary of these broadly applied
simplified ratings.
eQUEST won't allow you to input IPLV to describe a system, but you can
calculate it for the part-load and off-design performance curves that
eQUEST will use as defaults, and determine if the curves are suitable to
use in your case. Just don't be surprised though if the actual
performance based on your specific building and location ends up nowhere
near the IPLV performance.
Regards,
Jonathan M. Curtin, EIT, LEED(r) AP
Mechanical Engineer
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Paul
Diglio
Sent: Monday, December 21, 2009 04:15 AM
To: Amandeep Singh; equest-users at lists.onebuilding.org; John Aulbach
Subject: Re: [Equest-users] IPLV in Heat Pumps
Amandeep:
I agree with John. Actually, I believe IPLV is a somewhat new rating
that applies to larger systems. EER or COP are much more accurate
ratings.
I am confused about the SEER and IPLV ratings. What temperature bin do
they use to calculate these numbers? It would seem to me that an AC
system in the south would operate at a higher load throughout the
cooling season than one in the northeast. Of course, it would depend on
how the system was sized. An oversized system will operate at a much
lower load ratio than a tightly sized system.
Does anyone know the formula?
Paul Diglio, CEM
--- On Sun, 12/20/09, John Aulbach <jra_sac at yahoo.com> wrote:
From: John Aulbach <jra_sac at yahoo.com>
Subject: Re: [Equest-users] IPLV in Heat Pumps
To: "Amandeep Singh" <amandeep.singh at energycenter.org>,
equest-users at lists.onebuilding.org
Date: Sunday, December 20, 2009, 9:02 PM
Amandeeph:
As far as I am concerned, IPLV is a mythical number, like SEER.
It is based on assumed levels of usage for a pumed annual usage. If your
truly need part load curves, ask the manufacturer for the 75%, 50% and
25% points. You cannot evolve these four numbers out of a single mnumber
(IPLV).
________________________________
From: Amandeep Singh <amandeep.singh at energycenter.org>
To: equest-users at lists.onebuilding.org
Sent: Thu, December 17, 2009 1:03:45 PM
Subject: [Equest-users] IPLV in Heat Pumps
Hello everyone,
I was working on a school model located in Lakeside, San Diego
county. The school has Bard wall mount heat pumps (capacity - 2 to 4
tons), really old one. I got manufacture data of the old and new units
for replacement. The new units data has EER, IPLV and COP ratings. I
would prefer to use IPLV instead of EER rating in case of cooling to
calculate savings. The eQuest does have options for EER and SEER but
not for IPLV in the schematic design wizard. What should I do here?
Does it make sense to use IPLV instead of EER to calculate
savings for the Lakeside?
Thanks,
Aman
Amandeep Singh
Energy Engineer
8690 Balboa Ave, Suite 100
San Diego, CA 92123-1502
858.634.4729 phone
858.244.1178 fax
www.energycenter.org <http://www.energycenter.org/> web
Submit your SANDEE Award nomination today.
Visit www.energycenter.org
<http://www.energycenter.org/signature> .
-----Inline Attachment Follows-----
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
<http://us.mc833.mail.yahoo.com/mc/compose?to=EQUEST-USERS-UNSUBSCRIBE@O
NEBUILDING.ORG>
------------------------------------------------------------------------------
Legal Disclaimer: The information contained in this communication is confidential and is covered by the Electronic Communications Privacy Act, 18 U.S.C. §§ 2510-2521; it may be privileged and is intended for the exclusive use of the above named addressee(s). If you are not the intended recipient(s), you are expressly prohibited from copying, distributing, disseminating, or in any other way using any of the information contained within this communication. If you have received this communication in error, please contact the sender by telephone at (713) 781-2526 or by response via email and permanently delete the original email (including attachments) and any copies.
Please consider the environment before printing this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091221/79df41b7/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 8634 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091221/79df41b7/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 5651 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091221/79df41b7/attachment-0001.jpeg>
More information about the Equest-users
mailing list