[Equest-users] Modelling boiler lock out

John Carpenter jcarpenter at genesysengineering.net
Thu Apr 16 12:12:32 PDT 2009


Angelina,

 

If you are in the detailed edit mode and double click on the hot water loop,
you should see a tab called "operation."

 

If you then change the "Loop operation" to "Snap," the model will allow you
to shut off the boilers at any temperature you wish.  Just make sure you
change the snap location to "outside" instead of a zone.

 

Regards,

 

John Carpenter
Mechanical Engineer
Genesys Engineering
Pelham, NY
(T) 914-633-6490 x128
(F) 914-633-6951
www.genesysengineering.net

  _____  

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Kalianda,
Angelina
Sent: Thursday, April 16, 2009 3:03 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Modelling boiler lock out

 

Hi all,

 

How do you model a boiler lock out?  The boiler will shut off when outside
air temp is 76 degree.

 

Thanks,

 

Angelina 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090416/2c063f9b/attachment.htm>


More information about the Equest-users mailing list