[Equest-users] CHW Pump differential temperature
Xavier García Casals
xavier.garcia at aiguasol.coop
Fri Oct 31 03:47:01 PDT 2008
Hi,
Probably because the chiller's EIR is reduced due to a more favorable
inlet temperature. Have a look at your chiller performance curves in the
model.
En/na Aulbach, John ha escrit:
> All:
>
> I have run a Base Case and a Parametric run for a Central Plant
> serving an office complex. Everything in both runs is the same, EXCEPT
> that the Base run has a 10°F differential temperature and the
> Parametric run has a 15°F differential temperature. The CHW pump is
> variable speed.
>
> As expected, electric energy is saved (about 40,000 kWh/year for a 600
> ton plant). However, about 15,000 kWh is saved at the Chilled Water
> pump, and 22,000 kWh is saved at the chiller.
>
> I changed the Loop Design DT to 15°F and the CHW Coil Design Delta T
> to 15°F.
>
> Why is my chiller energy reducing?
>
> Thanks.
>
> John R. Aulbach, PE, CEM
> /Project Manager/
> Nexant, Inc.
> 701 West Kimberly Ave., Suite 245
> Placentia, CA 92870-6342 USA
> Phone: 714-524-4402
> Fax: 714-524-4407
> email: jaulbach at nexant.com <mailto:jaulbach at nexant.com>
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
--
* *
*Xavier García Casals*
*Sistemas** Solares, Eficiencia Energética e Ingeniería Bioclimática** *
*AIGUASOL** INGENIERÍA*
* *
Sistemes Avançats d'Energia Solar Tèrmica SCCL
C/ Palermo, 17. Bajos dcha. 28043 Madrid
Tel: (+34) 91 142 27 88
C/ Roger de Llúria, 29 3r 2a 08009 Barcelona
Tel: (+34) 93 342 47 55 Fax: (+34) 93 342 47 56
Mobil: 660 22 94 45
xavier.garcia at aiguasol.coop <mailto:xavier.garcia at aiguasol.coop>
http://www.aiguasol.coop <http://www.aiguasol.coop/>
* *
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20081031/7ce8bd9a/attachment.htm>
More information about the Equest-users
mailing list