Indeed it looks like a very high heating power installed. Did you have a 
look to check that your system is not simultaniously cooling and heating 
(Cold deck reset --> constant)?

En/na Cyrus Grimes ha escrit:
>
> I'm trying to create my baseline model for a school on Gallipolis OH. 
> I have the school broken into 5 zones and am using  PSZ units.  The 
> space loads seem to be modeling fine, I'm just having a problem 
> getting  the heating and cooling loads under control.  Using the 90.1 
> prescribed supply-air-to-room temperature difference of 20° and a dead 
> band of 5°, I end up with a heating
>
> design capacity of 80 btu/hr/sqft.
>
>  
>
> I was wondering if other people have run into that same problem and 
> how it may be resolved.  I'll seen more information if it will help I 
> just don't want to take too much space.
>
>  
>
>                          Cyrus Grimes                          .    
>
>                     Mechanical Engineer
>
>  
>
> *Corporate Office*
>
> 1108 City Park Avenue, 3^rd Floor
>
> Columbus, Ohio 43206
>
>  
>
> Phone (614) 443-1178 ext. 274
>
> Fax: (614) 443-1594
>
> /e-mail: cgrimes at dynamix-ltd.com <mailto:cgrimes at dynamix-ltd.com>/
>
>  
>
>  www.dynamix-ltd.com <http://www.dynamix-ltd.com/>
>
> P Please consider the environment before printing this e-mail note
>
>  
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>   

-- 

* *

*Xavier García Casals*

 

*Sistemas** Solares, Eficiencia Energética e Ingeniería Bioclimática** *

*AIGUASOL** INGENIERÍA*

* *

Sistemes Avançats d'Energia Solar Tèrmica SCCL

C/ Palermo, 17. Bajos dcha. 28043 Madrid

Tel: (+34) 91 142 27 88

 

C/ Roger de Llúria,  29 3r 2a 08009 Barcelona

Tel: (+34) 93 342 47 55  Fax: (+34) 93 342 47 56

 

Mobil: 660 22 94 45

xavier.garcia at aiguasol.coop <mailto:xavier.garcia at aiguasol.coop>

http://www.aiguasol.coop <http://www.aiguasol.coop/>

* *

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20081008/a425cebb/attachment.htm>


More information about the Equest-users mailing list