I think you need to combine PS-E for the end-use breakdown by time-of-use blocks, with the ES-F which will give you average rates for each block.

I'm not sure how this would work if you also had a mid-peak period, PS-E may only report a peak and non-peak breakdown.  If you have that, hopefully you can lump them together on the LEED forms.

David



From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Josh Greenfield
Sent: Monday, October 06, 2008 1:13 PM
To: Karen Walkerman
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] eQuest $$ Reports and LEED

Karen...thanks for the response...ES-D and ES-E are still overall costs and do not break the costs out into sub-categories (lights, task lights, space cooling, etc.) like BEPS and BEPU do...do you know of any reports that do a sub-categorized cost break-out?


Josh Greenfield, PE, LEED AP
Senior Associate
Primera Engineers, Ltd.
100 S. Wacker Drive, Suite 700
Chicago, IL 60606
312.606.0910 Main
312.242.6392 Direct
312.606.0415 Fax
jgreenfield at primerachicago.com<blocked::mailto:jgreenfield at primerachicago.com>
http://www.primerachicago.com
Be Green...please consider the environment before printing this email.
From: Karen Walkerman [mailto:kwalkerman at gmail.com]
Sent: Monday, October 06, 2008 12:06 PM
To: Josh Greenfield
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] eQuest $$ Reports and LEED

ES-D and ES-E

--
Karen
On Mon, Oct 6, 2008 at 1:02 PM, Josh Greenfield <JGreenfield at primerachicago.com<mailto:JGreenfield at primerachicago.com>> wrote:

I know that the BEPS and BEPU .sim file reports will give me consumption data, but is there a standardized report, or even a way to create a customized report that will make eQuest output a simulation into a format similar to Tables 5 or 6 in the EAc1 section of LEED-NC, with respect to cost values?  This particular project I am having issues with is using an On-Peak/Off-Peak rate structure, so I cannot simply multiply the consumption data by a fixed utility rate.  Am I missing a report that already exists with this information?  Thanks for the help.



Josh Greenfield, PE, LEED AP
Senior Associate
Primera Engineers, Ltd.
100 S. Wacker Drive, Suite 700
Chicago, IL 60606
312.606.0910 Main
312.242.6392 Direct
312.606.0415 Fax
jgreenfield at primerachicago.com
http://www.primerachicago.com

Be Green...please consider the environment before printing this email.

_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>


-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20081006/438441c3/attachment.htm>


More information about the Equest-users mailing list