[Equest-users] Multizone heating question
James Hansen
JHANSEN at ghtltd.com
Thu Dec 11 11:01:36 PST 2008
I looked at your .inp file - with a multizone system, you have the
heating coil of the dual duct scenario running all the time - it doesn't
look like you can set the minimum flow rate thru this coil to 0, which
means theoretically there is always a heating load, and perhaps the
boiler is running constantly during FAN ON conditions. Just a guess.
Also, you have the heating and cooling setpoints at the same temp (68
degrees). From my experience, you don't want to do this...it may cause
unexpected problems, especially when you are talking about multiple
thermostats controlling a complicated dual duct system.
GHT Limited
James Hansen, PE, LEED AP
Senior Associate
1010 N. Glebe Rd, Suite 200
Arlington, VA 22201-4749
703-338-5754 (Cell)
703-243-1200 (Office)
703-276-1376 (Fax)
www.ghtltd.com <http://www.ghtltd.com/>
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Daly,
Matt
Sent: Thursday, December 11, 2008 1:57 PM
To: Marcus Eliason
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Multizone heating question
Yes, where is your weather file?
My guess is, your chilled air stream needs to be mixed with heated air
to raise it to a proper zone temperature.
Matt Daly * Project Manager * Willamette ESD
2611 Pringle Road SE * Salem, OR 97302
503-385-4693 * fax 503-540-2959
matt.daly at wesd.org <mailto:matt.daly at wesd.org>
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Karen
Walkerman
Sent: Thursday, December 11, 2008 10:37 AM
To: Marcus Eliason
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Multizone heating question
I'm happy to look at your inp file, but I can't open it with eQuest. My
initial guess is that you have a pilot on all summer, or that your
boiler is cycling at an inefficient part load ratio in response to small
demands.
--
Karen
On Thu, Dec 11, 2008 at 1:25 PM, Marcus Eliason <meliason at essexco.com>
wrote:
Hello,
I am modeling an existing building with multizone air handlers with
chilled
water coils for cooling and hot water coils for heating. The hot water
is
generated by a gas furnace. I am seeing some discrepancies in my gas
usage
from actual to the simulation. In the actual building, the gas usage is
only high in the winter months (the building is in the south) and is
next
to nothing in summer months. I have tried all the various methods of
coil
control under the "heating" tab and cannot get the simulation to reflect
the
real life usage. Does anybody have any ideas on how to control the
heating
better? Representative files are attached.
Marcus Eliason
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
The information contained in this communication is confidential, may be privileged, and is intended only for the use of the addressee. It is the property of GHT Limited. Unauthorized use, disclosure or copying of this communication or any part thereof is strictly prohibited and may be unlawful. If you have received this communication in error, please notify me immediately by return e-mail or by e-mail to ght at ghtltd.com, and destroy this communication and all copies thereof, including all attachments. Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20081211/80b8e419/attachment.htm>
More information about the Equest-users
mailing list