[Equest-users] eQuest refrigeration and hourly reports
Brian Davis
BDavis at dwyer.com
Fri Dec 5 05:38:49 PST 2008
Karen,
I have found that you can, however those options do not show up at first. When you go to create a new hourly block, select "GLOBAL" as the variable type then use the default "CLEARNESS NUMBER" as the variable list. These really don't matter as you will be changing them later. Once done, go back into the block, now under viable type, there are many more options, all of which you are looking for below.
Not sure why you cannot select them from the start, but they are there.
Brian
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Karen Walkerman
Sent: Thursday, December 04, 2008 6:42 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] eQuest refrigeration and hourly reports
one more question...
why can't I get any hourly info on compressors, condensers, refrigeration systems, refrigeration circuits, etc??? How am I going to trouble-shoot?
Thanks again,
--
Karen