[Equest-users] Under heating
Karen Walkerman
kwalkerman at gmail.com
Thu Dec 4 10:14:46 PST 2008
If you look at your SS-O report, it will show you when your spaces are over
or under-heating. I have found that often I am over or under cooling during
startup periods, i.e. my equipment is sized appropriately for loads at
constant indoor temperatures, but if I'm trying to heat the building 5
degrees in 1 hour, I may have some problems.
Also, in packaged systems, I have found that some of the spaces without a
thermostat often have unmet load hours. I believe this is due to the fact
that eQuest doesn't always accurately model airflow through each zone.
Usually, when I model multiple rooms served by a single system (heat pump,
for example), I model the rooms as one zone together. I feel that this is
appropriate as long as the spaces have similar use type, exposure and
schedules.
One last thing--if you have baseboards and you added them after the wizard,
you will need to specify the thermostat type to "Thermostatic" and give the
baseboards a capacity, otherwise, the spaces will get no heat.
--
Karen
On Thu, Dec 4, 2008 at 1:07 PM, Patrick Darby <pdarby at twfp.com> wrote:
> Hello All,
>
> After Simulation and looking through reports SS-R and SS-O, I have had a
> continuing problem of under heating in my Thermal Zones. I have allowed my
> boiler capacity, all my heating coils, my heating pump parameters to default
> and DOE size, but these actions are of no resolve to the under heating.
>
> Has anyone else ran into this problem, and found a reasonable solution to
> the problem of under heating?
>
> Thank you for any help.
>
> *Patrick Darby, BScE*
> Mechanical Engineering Services
>
>
> * The Walter Fedy Partnership *
> Phone: 519-576-2150 x271
> Fax: 519-576-5499
> Web: *www.twfp.com* <http://www.twfp.com/>
>
> The information contained in this e-mail is intended only for the
> individual or entity to whom it is addressed. Its contents (including any
> attachments) may contain confidential and/or privileged information. If you
> are not an intended recipient you must not use, disclose, disseminate, copy
> or print its contents. If you receive this e-mail in error, please notify
> the sender by reply e-mail and permanently delete the message. Information,
> opinions or conclusions contained in this message that do not relate to the
> official business of "The Walter Fedy Partnership" will be understood as
> neither given nor endorsed by it.
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20081204/b5278336/attachment.htm>
More information about the Equest-users
mailing list