James Hess
JHess at tmecorp.com
Fri Apr 25 05:54:21 PDT 2008
Susan,
I believe that only the "Powered Induction Unit" system type in eQuest allows
you to model a VAV system with fan powered boxes (series or parallel). With
the PIU system type, you can model all FPT boxes, or a combination of FPT
boxes and standard boxes. Select the specific box type in the zone airflow
tab à "Zone Terminal and Fans" à "Terminal Type" à Standard VAV, Series PIU,
Parallel PIU ...
Regards,
James Hess
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Susan F
Sent: Friday, April 25, 2008 6:49 AM
To: equest-users at lists.onebuilding.org
Subject: Spam:[Equest-users] Packaged RTU
Hi,
I am trying to model a packaged rooftop VAV unit. I have selected the type
PVAV but this does not allow me to add terminal units. I want my perimeter
zones to have fan powered VAV boxes while my interior zones will have
standard VAV boxes. Any idea how to add the VAV boxes?
Thanks in advance!