Mickey Bush mbush at dmiinc.com
Fri Apr 18 14:35:01 PDT 2008


Hi,

I would like to be the first to pose a question on the eQuest mailing list! 

I am having a problem modeling a dedicated outside air handling unit in
Equest.
 
I have specified a constant OAcfm/person in each zone to calculate the
ventilation rates, and the air handling units served by the OAHU link
to it with the OA-From command. But there appears to be a problem in
that the OAHU will fail to recognize the zone OA requirements from zones
defined by floor multipliers, and therefore it is not sized properly.
For example, my 23 story building (Ground, Mid (*21), Top) will have the
OAHU sized for 3 floors only (Ground, Mid, Top).
 
I attempted to force the size of the dedicated outside air unit, but since
it is VAV, it runs continuously at minimum flow.

If anybody has any experience with this issue, your ideas and insight are
appreciated.
 
Thanks,
Mickey

Mickey Bush
DMI
35 Walnut Street
Wellesley, MA 02481
Phone: 781-431-1100 x13
Fax: 781-431-1109

-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Vikram Sami
Sent: Friday, April 18, 2008 5:22 PM
To: Jason Glazer; eQUEST-users at onebuilding.org
Subject: Re: [Equest-users] Testing

Thanks for all the responses - I was getting nervous without my
surrogate friends :-) 


Vikram Sami, LEED AP
Direct Phone 404-253-1466 | Direct Fax 404-253-1366

LORD, AECK & SARGENT ARCHITECTURE
1201 Peachtree Street NE, Suite 300, Atlanta, GA 30361
Responsive Design * Technological Expertise * Exceptional Service
www.lordaecksargent.com

Please don't print this email unless you really have to.
In the United States, we use enough office paper each year to build a
10-foot high wall that's 6,815 miles long or two and a half times the
distance from New York to Los Angeles. 
~ Wisconsin Department of Natural Resources, "Recycling Facts and
Figures," PUBL CE-163, 2002.


-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jason
Glazer
Sent: Friday, April 18, 2008 5:21 PM
To: eQUEST-users at onebuilding.org
Subject: Re: [Equest-users] Testing

So far 67 people have signed up for the eQUEST-users mailing list. I
would not be surprised if that ends up being a few hundred by next week.

Jason

On 4/18/2008 4:17 PM, Steven Savich wrote:
> Also here.  Working away on a simulation.
> 
>  
> 
> Steven Savich
> 
> Systems West Engineers
> 
> 411 High Street
> 
> Eugene, OR  97401-2427
> 
> (541) 342-7210
> 
> (541) 342-7220 (fax)
> 
> ----------------------------------------------------------------------
> --
> 
> *From:* equest-users-bounces at lists.onebuilding.org
> [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of 
> *Aulbach, John
> *Sent:* Friday, April 18, 2008 2:12 PM
> *To:* Vikram Sami; equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] Testing
> 
>  
> 
> I'm here. Guess this is specific for eQuest questions. May of the 
> other questions seem to ASHRAE-90.1 based, or comparative queries to 
> which program can run what.
> 
>  
> 
> Needless to say, I am in sunny Southern California. Birthplace of 
> eQuest. And know Jeff Hirsch well.
> 
>  
> 
> John R. Aulbach, PE, CEM
> 
> //Project Manager//
> 
> Nexant, Inc.
> 
> 701 West Kimberly Ave., Suite 245
> 
> Placentia, CA 92870-6342 USA
> 
> Phone: 714-524-4402
> 
> Fax: 714-524-4407
> 
> email: jaulbach at nexant.com <mailto:jaulbach at nexant.com>
> 
>  
> 
>  
> 
> ----------------------------------------------------------------------
> --
> 
> *From:* equest-users-bounces at lists.onebuilding.org
> [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of 
> *Vikram Sami
> *Sent:* Friday, April 18, 2008 2:08 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Testing
> 
> Not sure if this works, but so far I haven't received an email from 
> this list, so I was wondering if anyone has signed up yet.
> 
>  
> 
> *Vikram Sami,* LEED AP
> Direct Phone 404-253-1466 | Direct Fax 404-253-1366
> 
> *L**ORD**, A**ECK** & S**ARGENT** A**RCHITECTURE
> *1201 Peachtree Street NE, Suite 300, Atlanta, GA 30361 Responsive 
> Design * Technological Expertise * Exceptional Service 
> www.lordaecksargent.com <file:///\\www.lordaecksargent.com>
> 
> *Please don't print this email unless you really have to*/./ /One tree

> makes 16.67 reams of copy paper or 8,333.3 sheets ~Conservatree, 
> September 2002/
> 
>  
> 
> 
> ----------------------------------------------------------------------
> --
> 
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to 
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG

--
Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair Admin of BLDG-SIM
list for building simulation users

_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG


__________ Information from ESET NOD32 Antivirus, version of virus signature
database 3039 (20080418) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com




More information about the Equest-users mailing list