<p>Hi,</p>
<p>This has been bogging us for a while, as we cannot figure out how
to interpret the various issues in ASHRAE 90.1.</p>
<p>If in a multifamily building the residential units are only
heated but not cooled in the actual design (climate is North
Europe), how does the baseline get modeled? I suppose Systems #9
and #10 (Heating Only) would be out of the question as these are
intended for ancillary spaces. So it would have to be System #1 or
#2, but with cooling as well?<br>
</p>
<p>More importantly, would the Proposed residential units be modeled
with additional cooling using identical systems as in Baseline?</p>
<p>Thank you in advance,</p>