<html xmlns:v="urn:schemas-microsoft-com:vml" xmlns:o="urn:schemas-microsoft-com:office:office" xmlns:w="urn:schemas-microsoft-com:office:word" xmlns:m="http://schemas.microsoft.com/office/2004/12/omml" xmlns="http://www.w3.org/TR/REC-html40">
<head>
<meta http-equiv="Content-Type" content="text/html; charset=utf-8">
<meta name="Generator" content="Microsoft Word 15 (filtered medium)">
<!--[if !mso]><style>v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style><![endif]--><style><!--
/* Font Definitions */
@font-face
{font-family:"Cambria Math";
panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
{font-family:Calibri;
panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
{font-family:"Segoe UI";
panose-1:2 11 5 2 4 2 4 2 2 3;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{margin:0cm;
margin-bottom:.0001pt;
font-size:12.0pt;
font-family:"Times New Roman",serif;}
a:link, span.MsoHyperlink
{mso-style-priority:99;
color:blue;
text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
{mso-style-priority:99;
color:purple;
text-decoration:underline;}
p.msonormal0, li.msonormal0, div.msonormal0
{mso-style-name:msonormal;
mso-margin-top-alt:auto;
margin-right:0cm;
mso-margin-bottom-alt:auto;
margin-left:0cm;
font-size:12.0pt;
font-family:"Times New Roman",serif;}
span.EmailStyle18
{mso-style-type:personal;
font-family:"Calibri",sans-serif;
color:#1F497D;}
span.EmailStyle20
{mso-style-type:personal-reply;
font-family:"Segoe UI",sans-serif;
color:#44546A;
font-weight:normal;
font-style:normal;}
.MsoChpDefault
{mso-style-type:export-only;
font-size:10.0pt;}
@page WordSection1
{size:612.0pt 792.0pt;
margin:70.85pt 70.85pt 70.85pt 70.85pt;}
div.WordSection1
{page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
</head>
<body lang="EN-GB" link="blue" vlink="purple">
<div class="WordSection1">
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Segoe UI",sans-serif;color:#44546A;mso-fareast-language:EN-US">Hi Karol,<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Segoe UI",sans-serif;color:#44546A;mso-fareast-language:EN-US"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Segoe UI",sans-serif;color:#44546A;mso-fareast-language:EN-US">The trick to getting ApacheHVAC and Macroflo to work together in IES VE is the use of a flow controller set to zero at an appropriate
point in the HVAC network. For your example, the HVAC network would contain a single zone where you want to add mechanical supply. The upstream side of this zone would have a flow controller set to provide the required flowrate and the downstream side would
have a flow controller set to zero volume flow, on continuously. With Macroflo and HVAC both active in ApacheSim, the mechanical supply will be introduced, as defined in the HVAC network, and Macroflo will calculate what subsequently happens to that air (provided
there are sufficient Macroflo openings to prevent the run crashing due to overpressurisation). Hope this helps.<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Segoe UI",sans-serif;color:#44546A;mso-fareast-language:EN-US"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Segoe UI",sans-serif;color:#44546A;mso-fareast-language:EN-US">Regards,<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Segoe UI",sans-serif;color:#44546A;mso-fareast-language:EN-US"><o:p> </o:p></span></p>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Segoe UI",sans-serif;color:#44546A;mso-fareast-language:EN-US">Neil
</span><span style="font-size:10.0pt;font-family:"Segoe UI",sans-serif;color:black"><o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#44546A"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#44546A"><img width="612" height="69" style="width:6.375in;height:.7187in" id="Picture_x0020_1" src="cid:image001.png@01D51249.37ECB530" alt="Leeds 30-E-footer-regional.png"><o:p></o:p></span></p>
</div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Segoe UI",sans-serif;color:#44546A;mso-fareast-language:EN-US"><o:p> </o:p></span></p>
<div>
<div style="border:none;border-top:solid #E1E1E1 1.0pt;padding:3.0pt 0cm 0cm 0cm">
<p class="MsoNormal"><b><span lang="EN-US" style="font-size:11.0pt;font-family:"Calibri",sans-serif">From:</span></b><span lang="EN-US" style="font-size:11.0pt;font-family:"Calibri",sans-serif"> Bldg-sim <bldg-sim-bounces@lists.onebuilding.org>
<b>On Behalf Of </b>Karol BANDURSKI via Bldg-sim<br>
<b>Sent:</b> 24 May 2019 15:47<br>
<b>To:</b> 'Chris Yates' <chris.malcolm.yates@gmail.com><br>
<b>Cc:</b> bldg-sim@lists.onebuilding.org<br>
<b>Subject:</b> Re: [Bldg-sim] MarcoFlow and ApacheHVAC coupling<o:p></o:p></span></p>
</div>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
<div>
<p class="MsoNormal"><strong><span lang="PL" style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#A80000">** External Email **</span></strong><span lang="PL" style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#A80000"><o:p></o:p></span></p>
</div>
<p class="MsoNormal"><span lang="PL"><o:p> </o:p></span></p>
<div>
<p class="MsoNormal"><span lang="EN-US" style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D;mso-fareast-language:EN-US">Hi Chris,<o:p></o:p></span></p>
<p class="MsoNormal"><span lang="EN-US" style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D;mso-fareast-language:EN-US"><o:p> </o:p></span></p>
<p class="MsoNormal"><span lang="EN-US" style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D;mso-fareast-language:EN-US">Thank you for your advice!<o:p></o:p></span></p>
<p class="MsoNormal"><span lang="EN-US" style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D;mso-fareast-language:EN-US"><o:p> </o:p></span></p>
<p class="MsoNormal"><span lang="EN-US" style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D;mso-fareast-language:EN-US">For now the issue is that we would like to do it as good as possible using IES VE.<o:p></o:p></span></p>
<p class="MsoNormal"><span lang="EN-US" style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D;mso-fareast-language:EN-US"><o:p> </o:p></span></p>
<p class="MsoNormal"><span lang="EN-US" style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D;mso-fareast-language:EN-US">Kind regards,<o:p></o:p></span></p>
<p class="MsoNormal"><span lang="EN-US" style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D;mso-fareast-language:EN-US">Karol<o:p></o:p></span></p>
<p class="MsoNormal"><span lang="EN-US" style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D;mso-fareast-language:EN-US"><o:p> </o:p></span></p>
<p class="MsoNormal"><b><span lang="PL" style="font-size:11.0pt;font-family:"Calibri",sans-serif">From:</span></b><span lang="PL" style="font-size:11.0pt;font-family:"Calibri",sans-serif"> Chris Yates [<a href="mailto:chris.malcolm.yates@gmail.com">mailto:chris.malcolm.yates@gmail.com</a>]
<br>
<b>Sent:</b> Friday, May 24, 2019 4:38 PM<br>
<b>To:</b> Karol Bandurski <<a href="mailto:karol.bandurski@put.poznan.pl">karol.bandurski@put.poznan.pl</a>><br>
<b>Cc:</b> <a href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Bldg-sim] MarcoFlow and ApacheHVAC coupling<o:p></o:p></span></p>
<p class="MsoNormal"><span lang="PL"><o:p> </o:p></span></p>
<div>
<p class="MsoNormal"><span lang="PL">Hi Karol<o:p></o:p></span></p>
<div>
<p class="MsoNormal"><span lang="PL"><o:p> </o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span lang="PL">You could try one of the "RoomAirSettings" models in E+.<o:p></o:p></span></p>
<div>
<p class="MsoNormal"><span lang="PL">There should be an example file in the E+ installation directory that can be run "out of the box". You could mess with this. Rather than coupling network airflow and hvac network these models are typically based on 1d finite
elements or fixed (known) temperature gradients and don't require the zone to be split horizontally.<o:p></o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span lang="PL"><o:p> </o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span lang="PL">Best<o:p></o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span lang="PL"><o:p> </o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span lang="PL">Chris<o:p></o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span lang="PL"> <o:p></o:p></span></p>
</div>
</div>
</div>
<p class="MsoNormal"><span lang="PL"><o:p> </o:p></span></p>
<div>
<div>
<p class="MsoNormal"><span lang="PL">On Fri, May 24, 2019 at 11:27 AM Karol Bandurski via Bldg-sim <<a href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a>> wrote:<o:p></o:p></span></p>
</div>
<blockquote style="border:none;border-left:solid #CCCCCC 1.0pt;padding:0cm 0cm 0cm 6.0pt;margin-left:4.8pt;margin-top:5.0pt;margin-right:0cm;margin-bottom:5.0pt">
<p class="MsoNormal"><span lang="PL">Dear All<br>
<br>
My question refer to IES VE.<br>
<br>
Do you know some description how couple Atrium MacroFlow calculation, based<br>
on temperature stratification with flow forced by fans defined in<br>
ApacheHVAC?<br>
<br>
We prepare some model with students. Atrium is divided on three air zones<br>
and MacroFlow calculate flows caused by temperature differences, but we<br>
would like to add there also flow caused by mechanical system, e.g. inlet in<br>
the lowest part and outlets in windows in the highest part of Atrium.<br>
<br>
Kind regards,<br>
Karol<br>
--------------------------------------------------------------------<br>
Karol BANDURSKI M. Sc.<br>
Faculty of Civil and Environemntal Engeneering<br>
Division of Heating, Air Conditioning and Air Protection<br>
Poznan University of Technology<br>
<a href="https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.researchgate.net%2Fprofile%2FKarol_Bandurski&data=02%7C01%7CNeil.Shankland%40burohappold.com%7Cbe09fc72911441eb5e1408d6e056c88c%7C50ee6418869e48f5a9823607fcee1e1d%7C0%7C0%7C636943060671447761&sdata=%2FU1IlAAOcYwgKju%2F9XX%2BiUyEZZoVL2lhlIlq%2Bmxj4Mk%3D&reserved=0" target="_blank">https://www.researchgate.net/profile/Karol_Bandurski</a><br>
<a href="https://eur02.safelinks.protection.outlook.com/?url=http:%2F%2Fwww.put.poznan.pl%2F~karol.bandurski&data=02%7C01%7CNeil.Shankland%40burohappold.com%7Cbe09fc72911441eb5e1408d6e056c88c%7C50ee6418869e48f5a9823607fcee1e1d%7C0%7C0%7C636943060671457750&sdata=TS3F7YijB67VPDkW0exTnX2aTfN0qI55BxPr0Nx4Wbs%3D&reserved=0" target="_blank">www.put.poznan.pl/~karol.bandurski</a><br>
<br>
<br>
<br>
<br>
_______________________________________________<br>
Bldg-sim mailing list<br>
<a href="https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.onebuilding.org%2Flistinfo.cgi%2Fbldg-sim-onebuilding.org&data=02%7C01%7CNeil.Shankland%40burohappold.com%7Cbe09fc72911441eb5e1408d6e056c88c%7C50ee6418869e48f5a9823607fcee1e1d%7C0%7C0%7C636943060671457750&sdata=Xniz7rF13dHwn8NA1XTH5A0ujaTVtpAUidLhIa9W%2Fq0%3D&reserved=0" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">
BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><o:p></o:p></span></p>
</blockquote>
</div>
</div>
</div>
<p style="font-family:arial; font-size:11px; color:#808080;">This transmission is confidential and intended solely for the person or organisation to whom it is correctly addressed. If you are not the intended recipient of this transmission, you should not take
any action in reliance on it. Further, this transmission may contain confidential design and other information owned by Buro Happold Ltd. You should not copy, distribute, use, offer for sale or hire such information or in any way infringe the design and intellectual
property rights of Buro Happold Ltd. It is intended that communication by email from Buro Happold Ltd or its employees is limited to communications connected to the services provided by Buro Happold Ltd. Buro Happold Ltd accepts no liability for any communications
not connected to the services it provides. Computer viruses may be transmitted or downloaded onto your computer system via email communication. It is the recipient’s responsibility to take any action necessary to prevent computer viruses being transmitted
in this way. Accordingly, Buro Happold Ltd disclaims all responsibility which arises directly or indirectly from such transmission of computer viruses. Buro Happold Ltd. Registered in England: 2049511.</p>
</body>
</html>