<div dir="ltr">Madhav/ David,<div><br></div><div>I am thinking aloud here - </div><div>Climate zones 1-3a are not expected to have very low winter temperatures and most of the heating requirement can be met with a heatpump with some supplemental electric heat. While in Climate zones 4-8, we might need a backup heating source.</div><div><br></div><div>Therefore, I understand why ASHRAE 90.1 would change the baselines based on climate zones, in order to push the boundaries, as far as energy is concerned. I still think a GSHP or a VRF would be competitive when you compare their energy consumption to the 90.1 fossil fuel Baseline for climate zone 4-8. However, if you consider only energy cost, it may be harder to justify GSHP or VRF to your clients depending on the the cost of natural gas in your area. Does an ASHRAE baseline system really dictate the choice of the HVAC system or the fuel type in the proposed building? </div><div><br></div><div>Is the concern more to do with meeting energy cost saving targets ?</div><div><br></div><div>I would be interested to hear more thoughts on this topic.</div><div><br></div><div>Regards</div><div>Ramya Shivkumar<br></div><div class="gmail_quote"><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><br><br>---------- Forwarded message ----------<br>From: David Eldridge <<a href="mailto:DEldridge@grummanbutkus.com" target="_blank">DEldridge@grummanbutkus.com</a>><br>To: "<a href="mailto:bldg-sim@onebuilding.org" target="_blank">bldg-sim@onebuilding.org</a>" <<a href="mailto:bldg-sim@onebuilding.org" target="_blank">bldg-sim@onebuilding.org</a>><br>Cc: <br>Bcc: <br>Date: Tue, 6 Nov 2018 18:26:38 +0000<br>Subject: Re: [Bldg-sim] ASHRAE 90.1-2013 Appendix G - Baseline Fuel Source Mapping<br>





<div lang="EN-US" link="#0563C1" vlink="#954F72">
<div class="m_6641854139863294686m_-6935484298859418053WordSection1">
<p class="MsoNormal"><span style="color:#1f497d">Not sure if I missed a response to this or not…sorry this got lost in my draft folder for a few days.
<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">What you’ve stated as the problem is exactly why the standard takes the other approach – if the baseline system costs less to operate (and may also have lower source energy) then why shouldn’t it be the baseline
 system?<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">The standard is looking to establish the minimum requirements, which shouldn’t be “Best Practice” necessarily but reflect a constantly advancing minimum threshold.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">Choosing to use a system that’s less cost efficient is certainly allowable and, but requires making other improvements in the building to offset what is traded off by using the electric resistance heating system.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">Note that while the requirements of the standard do change based on climate, it isn’t based on geography directly, I have understood in the past that the approach is for national average utility rates to set
 the requirements. I can think of several reasons why NYSERDA specifically would take a different approach, but in general for country-wide adoption I would expect gas heat to be the reasonable baseline in climate zones that need more heating. Is it debatable
 for zones 3b and 3c, perhaps. I’m pretty comfortable with fossil fuel baseline in CZ 4-8.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">Separate topic: you are seeing GSHP and VRF systems use (much) more energy cost than the baselines?<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">David<u></u><u></u></span></p>
<div>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><b><span style="color:#1f497d">David S. Eldridge, Jr.</span></b><b><span style="color:#244061">, P</span></b><b><span style="color:#1f497d">.</span></b><b><span style="color:#244061">E</span></b><b><span style="color:#1f497d">.</span></b><b><span style="color:#244061">,
 LEED AP BD+C, BEMP, BEAP, HBDP</span></b><span style="color:#1f497d"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">Associate</span><span style="color:#1f497d"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:4.0pt;color:#1f497d"> </span><span style="color:#1f497d"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#365f91">Direct: (847) 316-92</span><span style="color:#1f497d">24</span><span style="color:#365f91"> | Mobile: (</span><span style="color:#1f497d">773</span><span style="color:#365f91">)
</span><span style="color:#1f497d">490</span><span style="color:#365f91">-</span><span style="color:#1f497d">5038</span><span style="color:#1f497d"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;color:#1f497d"> </span><span style="color:#1f497d"><u></u><u></u></span></p>
<p class="MsoNormal"><b><span style="color:#244061">Grumman/Butkus Associates</span></b><span style="color:gray">
</span><span style="color:#365f91">| 820 Davis Street, Suite 300 | Evanston, IL 60201</span><span style="color:#1f497d"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:9.0pt;color:gray">Energy Efficiency Consultants and Sustainable Design Engineers</span><span style="color:#1f497d"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><a href="http://grummanbutkus.com/" target="_blank"><span style="font-size:9.0pt;color:gray">grummanbutkus.com</span></a><span style="font-size:9.0pt;color:gray"> |
</span><a href="http://grummanbutkus.com/blog" target="_blank"><span style="font-size:9.0pt;color:gray">Blog</span></a><span style="font-size:9.0pt;color:gray"> |
</span><a href="https://www.facebook.com/pages/GrummanButkus-Associates/1385285015032526" target="_blank"><span style="font-size:9.0pt;color:gray">Facebook</span></a><span style="font-size:9.0pt;color:gray"> |
</span><a href="https://twitter.com/grummanbutkus" target="_blank"><span style="font-size:9.0pt;color:gray">Twitter</span></a><span style="color:gray"><u></u><u></u></span></p>
</div>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<div>
<div style="border:none;border-top:solid #e1e1e1 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b>From:</b> Bldg-sim [mailto:<a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>Madhav Munshi via Bldg-sim<br>
<b>Sent:</b> Thursday, November 01, 2018 4:08 PM<br>
<b>To:</b> <a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a><br>
<b>Subject:</b> [Bldg-sim] ASHRAE 90.1-2013 Appendix G - Baseline Fuel Source Mapping<u></u><u></u></p>
</div>
</div>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial",sans-serif">Hello Everyone,
<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial",sans-serif"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial",sans-serif">Does anyone know why the AHSRAE 90.1-2013 Appendix G Table G3.1.1-3 requires a Baseline HVAC system that is fossil fuel based for climate zones 3b,3c and 4-8? If my Proposed
 Design has an electric GSHP or VRF system, there is very little chance that the energy cost of this Proposed Design is going to be lower than a Baseline with a gas furnace/ boiler. Why does it matter for ASHRAE where the building is located and type of heating
 system selected for a project? <u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial",sans-serif"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial",sans-serif">For folks in the New York, NYSERDA has amended this map to avoid this fuel switch which makes total sense.
<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial",sans-serif"><u></u> <u></u></span></p>
<p class="MsoNormal"><img border="0" width="706" height="894" id="m_6641854139863294686m_-6935484298859418053Picture_x0020_7" alt="cid:image006.jpg@01D471FF.EBC60790"><span style="font-size:10.0pt;font-family:"Arial",sans-serif"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial",sans-serif"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial",sans-serif">Thank you<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial",sans-serif"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial",sans-serif">Madhav<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial",sans-serif"><u></u> <u></u></span></p>
<p class="MsoNormal" style="margin-left:1.5in"><b><span style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#66869e">MADHAV MUNSHI
</span></b><span style="font-size:10.0pt;font-family:"Arial",sans-serif;color:black">| LEED AP BD+C | BEMP
<b><u></u><u></u></b></span></p>
<p class="MsoNormal" style="margin-left:1.5in"><span style="font-size:8.0pt;font-family:"Arial",sans-serif;color:black">Associate – Senior Energy Analyst<u></u><u></u></span></p>
<p class="MsoNormal" style="margin-left:1.5in"><a href="mailto:mmunshi@kohlerronan.com" target="_blank"><span style="font-size:8.0pt;font-family:"Arial",sans-serif;color:black">mmunshi@kohlerronan.com</span></a><u><span style="color:black"><u></u><u></u></span></u></p>
<p class="MsoNormal" style="margin-left:1.5in"><u></u> <u></u></p>
<p class="MsoNormal" style="margin-left:1.5in"><b><span style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#66869e">KOHLER RONAN
</span></b><span style="font-size:10.0pt;font-family:"Arial",sans-serif;color:black">| Consulting Engineers<b><u></u><u></u></b></span></p>
<p class="MsoNormal" style="margin-left:1.5in"><span style="font-size:8.0pt;font-family:"Arial",sans-serif;color:black">171 Madison Avenue, New York, NY 10016<u></u><u></u></span></p>
<p class="MsoNormal" style="margin-left:1.5in"><span style="font-size:8.0pt;font-family:"Arial",sans-serif;color:black">212.695.2422 F 212.695.2423<u></u><u></u></span></p>
<p class="MsoNormal" style="margin-left:1.5in"><span style="font-size:8.0pt;font-family:"Arial",sans-serif;color:black"><u></u> <u></u></span></p>
<p class="MsoNormal" style="margin-left:1.5in"><span style="font-size:8.0pt;font-family:"Arial",sans-serif;color:black">93 Lake Avenue, Danbury, CT 06810<u></u><u></u></span></p>
<p class="MsoNormal" style="margin-left:1.5in"><span style="font-size:8.0pt;font-family:"Arial",sans-serif;color:black">203.778.1017 F 203.778.1018<u></u><u></u></span></p>
<p class="MsoNormal" style="margin-left:1.5in"><span style="font-size:8.0pt;font-family:"Arial",sans-serif"><u></u> <u></u></span></p>
<p class="MsoNormal" style="margin-left:1.5in"><a href="http://kohlerronan.com/" target="_blank"><span style="color:#1f497d;text-decoration:none"><img border="0" width="29" height="29" id="m_6641854139863294686m_-6935484298859418053Picture_x0020_1" alt="cid:image006.jpg@01D4385F.038E8F30"></span></a><a href="https://www.facebook.com/Kohler-Ronan-LLC-Consulting-Engineers-146070618769600/" target="_blank"><span style="color:blue;text-decoration:none"><img border="0" width="29" height="29" id="m_6641854139863294686m_-6935484298859418053Picture_x0020_2" alt="cid:image007.png@01D4385F.038E8F30"></span></a> <a href="https://twitter.com/KohlerRonan" target="_blank"><span style="color:blue;text-decoration:none"><img border="0" width="29" height="29" id="m_6641854139863294686m_-6935484298859418053Picture_x0020_3" alt="cid:image008.png@01D4385F.038E8F30"></span></a> <a href="https://www.linkedin.com/company/1672806?trk=hp-feed-company-name" target="_blank"><span style="text-decoration:none"><img border="0" width="29" height="29" id="m_6641854139863294686m_-6935484298859418053Picture_x0020_4" alt="cid:image009.png@01D4385F.038E8F30"></span></a> <a href="https://www.instagram.com/kohler_ronan/" target="_blank"><span style="text-decoration:none"><img border="0" width="29" height="29" id="m_6641854139863294686m_-6935484298859418053Picture_x0020_5" alt="cid:image010.png@01D4385F.038E8F30"></span></a><span style="font-size:9.0pt;font-family:"Arial",sans-serif"><u></u><u></u></span></p>
<p class="MsoNormal"><u></u> <u></u></p>