    <p>Roel,</p>
    <p>I have the following concerns about the approach you seem to be
      taking to define terrain-parameters for wind-driven rain:</p>
    <p>(1) you are still basing your investigation on a rather
      simplistic model to derive wind-driven rain from the reported rain
      fall and wind speed, i.e., do you know how reliable is that model?</p>
    <p>(2) for these types of correlations, you might want to use wind
      speeds at a much finer time resolution, since what's reported at
      the standard weather stations are random snapshots at an hourly or
      half-hourly time step.  You could consider using data from
      Personal Weather Stations (PWS), that are typically at the 5
      minute interval and many also have an additional channel for
      gusts.  Such weather data, i.e., 5-minute data in urban or
      suburban areas, are currently available for tens of thousands of
      PWS, especially in North America and the UK, on web sites such as
      Weather Underground (<a class="moz-txt-link-abbreviated"
        href="http://www.wunderground.com">www.wunderground.com</a>). 
      One caveat would be to know the placement of the PWS, which tend
      to be on rooftops (the problem is worse for official weather
      stations that are supposed to be at 10 m above the ground).   If
      you're interested in the WU weather data, let me know via e-mail.</p>
    <p>I would not recommend using New York Central Park, or at least
      you should compare the results to that from some other place
      that's less atypical.   The Central Park  weather station  is
      located at the Belvedere (see attached map), which is an isolated
      building in the middle of a large urban park that is in turn
      surrounded by tall buildings and adjacent to some of the tallest
      buildings in the world.  </p>
    <p><img src="cid:part2.4874A1B6.A6B9D5D8@whiteboxtechnologies.com"
        alt=""></p>
    <p>Yes, I'm aware that the terminal velocity of raindrops varies
      with their size.  However, I ignored that factor because any 
      error due to using a constant value would be small compared to all
      the other assumptions of the model and besides, I don't think
      raindrop size is recorded in any weather data.</p>
    <p>Joe<br>
    </p>
    <div class="moz-cite-prefix">On 7/19/2018 7:30 AM, Roel Tersteeg
      wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:AM0PR04MB4370A95E8765E9BBA681B78186520@AM0PR04MB4370.eurprd04.prod.outlook.com">
      <meta http-equiv="Content-Type" content="text/html; charset=utf-8">
      <meta name="Generator" content="Microsoft Word 15 (filtered
        medium)">
      <style><!--
/* Font Definitions */
@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:Consolas;
        panose-1:2 11 6 9 2 2 4 3 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0cm;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri",sans-serif;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
pre
        {mso-style-priority:99;
        mso-style-link:"HTML Preformatted Char";
        margin:0cm;
        margin-bottom:.0001pt;
        font-size:10.0pt;
        font-family:"Courier New";}
span.HTMLPreformattedChar
        {mso-style-name:"HTML Preformatted Char";
        mso-style-priority:99;
        mso-style-link:"HTML Preformatted";
        font-family:Consolas;
        mso-fareast-language:EN-GB;}
p.msonormal0, li.msonormal0, div.msonormal0
        {mso-style-name:msonormal;
        mso-margin-top-alt:auto;
        margin-right:0cm;
        mso-margin-bottom-alt:auto;
        margin-left:0cm;
        font-size:11.0pt;
        font-family:"Calibri",sans-serif;}
span.EmailStyle20
        {mso-style-type:personal-reply;
        font-family:"Calibri",sans-serif;
        color:windowtext;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-size:10.0pt;
        font-family:"Calibri",sans-serif;
        mso-fareast-language:EN-US;}
@page WordSection1
        {size:612.0pt 792.0pt;
        margin:72.0pt 72.0pt 72.0pt 72.0pt;}
div.WordSection1
        {page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal">Dear Joe, Julien,<o:p></o:p></p>
        <p class="MsoNormal"> <o:p></o:p></p>
        <p class="MsoNormal">Thank you for the extensive replies and
          your suggestions. <o:p> </o:p></p>
        <p class="MsoNormal"> <o:p></o:p></p>
        <p class="MsoNormal">The rainfall above an area is not very
          different between airfield and urban areas, but due to the
          buildings and trees that may shelter locations in build-up
          areas this can cause lower rainfall in those locations. As you
          mentioned the wind will be altered in a more significant way.
          One thing I would like to do is actually (re)define ‘terrain
          parameters’ for wind driven rain. A single number, such as in
          your example, hides the actual uncertainty behind that number.
          And for that I would like to find measured data, the location
          of which doesn’t matter that much.<o:p></o:p></p>
        <p class="MsoNormal"><span style="color:black"><o:p> </o:p></span></p>
        <p class="MsoNormal">The usage of weather stations for the
          purpose I am looking for is usually not an option as the
          location of weather stations is such that buildings and trees
          around the site don’t have an effect on the measurements
          (typically > 100 m around the site free of obstructions).
          For the model I am trying to build, the (uncertainty in the)
          effect of trees and buildings on rain and wind is exactly what
          I try to model. If you know of weather stations on such sites,
          I would be grateful if you could help me with that. I will
          also have a look at the weather stations in central park and
          see if they can help me.<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">As for the calculation presented, there are
          several methods (e.g. ISO15927, ASHRAE standard 55) and they
          mostly have the form of
          Rainfall*Wind_speed*cos(Wind_direction-Wall_normal), with
          possibly some factors. There is a bit more explanation in
          Climatological note 3 from Met Eireann, from which note 13 is
          an update, how they calculated the map.<o:p></o:p></p>
        <p class="MsoNormal">As a site-note: the velocity of raindrops
          is dependent on the size of the droplet with larger drops
          having a higher speed (terminal velocity) that smaller ones. <o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Roel Tersteeg MSc<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><span style="color:gray">PhD-student <o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:gray">Building Energy
            Research Group<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:gray">School of
            Architecture, Building and Civil Engineering<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:gray">Loughborough
            University<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:gray">T: +44 77 56 10 90
            54<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:gray">E: </span><a
            href="mailto:R.M.Tersteeg@lboro.ac.uk"
            moz-do-not-send="true"><span style="color:gray">R.M.Tersteeg@lboro.ac.uk</span></a><span
            style="color:gray"><o:p></o:p></span></p>
        <p class="MsoNormal"><span style="mso-fareast-language:EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><b><span lang="EN-US">From:</span></b><span
            lang="EN-US"> Julien Marrec <a
              class="moz-txt-link-rfc2396E"
              href="mailto:julien.marrec@gmail.com"><julien.marrec@gmail.com></a>
            <br>
            <b>Sent:</b> 19 July 2018 13:26<br>
            <b>To:</b> Joe Huang <a class="moz-txt-link-rfc2396E"
              href="mailto:yjhuang@whiteboxtechnologies.com"><yjhuang@whiteboxtechnologies.com></a><br>
            <b>Cc:</b> Roel Tersteeg <a class="moz-txt-link-rfc2396E"
              href="mailto:R.M.Tersteeg@lboro.ac.uk"><R.M.Tersteeg@lboro.ac.uk></a>;
            Luis Miguel Blanes Restoy <a class="moz-txt-link-rfc2396E"
              href="mailto:lmblanes@gmail.com"><lmblanes@gmail.com></a>;
            <a class="moz-txt-link-abbreviated"
              href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a><br>
            <b>Subject:</b> Re: [Bldg-sim] Wind driven rain data<o:p></o:p></span></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <div>
          <div>
            <p class="MsoNormal">Hello,<o:p></o:p></p>
          </div>
          <div>
            <p class="MsoNormal"><o:p> </o:p></p>
          </div>
          <div>
            <p class="MsoNormal">FYI, I can think of at least one
              location where you'd find probably good quality weather
              data in a <b><u>big </u>urban center and not at an
                airport: Central Park, New York City, USA</b>, though
              it's in a quite large park but there are tall buildings
              all around it, see <a
href="https://www.google.com/maps/place/40%C2%B046%2744.4%22N+73%C2%B058%2708.4%22W/@40.7787947,-73.9765413,15.5z/data=%214m5%213m4%211s0x0:0x0%218m2%213d40.779%214d-73.969"
                moz-do-not-send="true"> map</a>.<o:p></o:p></p>
          </div>
          <div>
            <p class="MsoNormal"><o:p> </o:p></p>
          </div>
          <div>
            <p class="MsoNormal">Note that in NOAA there's a weird thing
              going on where you have 4 stations with different
              operating dates, one did 1943 to 2010, another 2010 to
              2012 or so, and another started after that (I know I said
              there are four: one did 17 days in august 2010 but
              overlapped another running one). Here are the USAF-WBAN
              codes for the two most interesting:<o:p></o:p></p>
          </div>
          <div>
            <p class="MsoNormal"><o:p> </o:p></p>
          </div>
          <div>
            <p class="MsoNormal">725053-94728 #CENTRAL PARK (2012 to
              today)<o:p></o:p></p>
          </div>
          <div>
            <p class="MsoNormal">725060-94728 #NEW YORK CENTRAL PARK
              (2010 to 2012)<o:p></o:p></p>
          </div>
          <div>
            <p class="MsoNormal"><o:p> </o:p></p>
          </div>
          <div>
            <p class="MsoNormal">This data is free and can be accessed
              at NOAA's ISD (see <a
                href="https://www.ncdc.noaa.gov/isd/data-access"
                moz-do-not-send="true"> here</a>)<o:p></o:p></p>
          </div>
          <div>
            <p class="MsoNormal"><o:p> </o:p></p>
          </div>
          <div>
            <p class="MsoNormal">I looked at France's stations in the
              NOAA database too, since I have a better clue of where
              things actually are, and it seems that there are a bunch
              that aren't at an airport, but there are all in seaside
              towns, so that is probably not what you're looking for...<o:p></o:p></p>
          </div>
          <div>
            <p class="MsoNormal"><o:p> </o:p></p>
          </div>
          <div>
            <p class="MsoNormal">Here are some stations you'll perhaps
              want to look at, I'm including the three airports around
              central park too if you want to compare the data. Don't
              mind the fact that the 'END" date is last year, I just
              haven't refreshed this file since September 2017<o:p></o:p></p>
          </div>
          <div>
            <p class="MsoNormal"><o:p> </o:p></p>
          </div>
          <div>
            <p class="MsoNormal"><o:p> </o:p></p>
          </div>
          <div>
            <table class="MsoNormalTable"
              style="width:692.0pt;border-collapse:collapse"
              cellspacing="0" cellpadding="0" width="923" border="0">
              <tbody>
                <tr style="height:15.0pt">
                  <td style="width:48.0pt;padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom"
                    width="64">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">USAF<o:p></o:p></span></p>
                  </td>
                  <td style="width:48.0pt;padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom"
                    width="64">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">WBAN<o:p></o:p></span></p>
                  </td>
                  <td style="width:164.0pt;padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom"
                    width="219">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">STATION
                        NAME<o:p></o:p></span></p>
                  </td>
                  <td style="width:48.0pt;padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom"
                    width="64">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">CTRY<o:p></o:p></span></p>
                  </td>
                  <td style="width:48.0pt;padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom"
                    width="64">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">STATE<o:p></o:p></span></p>
                  </td>
                  <td style="width:48.0pt;padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom"
                    width="64">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">ICAO<o:p></o:p></span></p>
                  </td>
                  <td style="width:48.0pt;padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom"
                    width="64">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">LAT<o:p></o:p></span></p>
                  </td>
                  <td style="width:48.0pt;padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom"
                    width="64">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">LON<o:p></o:p></span></p>
                  </td>
                  <td style="width:48.0pt;padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom"
                    width="64">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">ELEV(M)<o:p></o:p></span></p>
                  </td>
                  <td style="width:48.0pt;padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom"
                    width="64">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">BEGIN<o:p></o:p></span></p>
                  </td>
                  <td style="width:48.0pt;padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom"
                    width="64">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">END<o:p></o:p></span></p>
                  </td>
                  <td style="width:48.0pt;padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom"
                    width="64">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">KEEP<o:p></o:p></span></p>
                  </td>
                </tr>
                <tr style="height:15.0pt">
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">70020<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">99999<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">BOULOGNE<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">FR<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <br>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <br>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">50.733<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">1.6<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">74<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">19730101<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">20170902<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">YES<o:p></o:p></span></p>
                  </td>
                </tr>
                <tr style="height:15.0pt">
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">72000<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">99999<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">PENMARCH<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">FR<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <br>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <br>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">47.8<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">-4.367<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">19<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">19360102<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">20170902<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">YES<o:p></o:p></span></p>
                  </td>
                </tr>
                <tr style="height:15.0pt">
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">73150<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">99999<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">LA
                        ROCHELLE<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">FR<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <br>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <br>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">46.15<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">-1.15<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">10<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">19290801<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">20170902<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">YES<o:p></o:p></span></p>
                  </td>
                </tr>
                <tr style="height:15.0pt">
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">76410<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">99999<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">SETE<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">FR<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <br>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <br>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">43.4<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">3.7<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">81<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">19360615<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">20170902<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">YES<o:p></o:p></span></p>
                  </td>
                </tr>
                <tr style="height:15.0pt">
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">76950<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">99999<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">CAP
                        FERRAT<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">FR<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <br>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <br>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">43.683<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">7.333<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">144<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">19730101<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">20100412<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">YES<o:p></o:p></span></p>
                  </td>
                </tr>
                <tr style="height:15.0pt">
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">725030<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">14732<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">LA
                        GUARDIA AIRPORT<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">US<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">NY<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">KLGA<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">40.779<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">-73.88<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">3.4<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">19730101<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">20170904<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">YES<o:p></o:p></span></p>
                  </td>
                </tr>
                <tr style="height:15.0pt">
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">725033<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">94728<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">NYC
                        CENTRAL PARK<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">US<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">NY<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">KNYC<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">40.779<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">-73.969<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">47.5<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">19431201<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">20100731<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">YES<o:p></o:p></span></p>
                  </td>
                </tr>
                <tr style="height:15.0pt">
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">725033<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">99999<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">NEW
                        YORK CITY  CENTRAL PARK<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">US<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">NY<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <br>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">40.767<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">-73.983<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">27<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">20100801<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">20100817<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">YES<o:p></o:p></span></p>
                  </td>
                </tr>
                <tr style="height:15.0pt">
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">725053<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">94728<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><b><span
                          style="color:black;mso-fareast-language:EN-US">CENTRAL
                          PARK<o:p></o:p></span></b></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">US<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">NY<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">KNYC<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">40.779<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">-73.969<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">42.7<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">20120801<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">20170904<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">YES<o:p></o:p></span></p>
                  </td>
                </tr>
                <tr style="height:15.0pt">
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">725060<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">94728<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><b><span
                          style="color:black;mso-fareast-language:EN-US">NEW
                          YORK CENTRAL PARK<o:p></o:p></span></b></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">US<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">NY<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">KNYC<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">40.779<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">-73.969<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">47.5<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">20100801<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">20120801<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">YES<o:p></o:p></span></p>
                  </td>
                </tr>
                <tr style="height:15.0pt">
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">744860<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">94789<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">JOHN
                        F KENNEDY INTERNATIONAL AIRPORT<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">US<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">NY<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">KJFK<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">40.639<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">-73.762<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">3.4<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">19730101<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal" style="text-align:right"
                      align="right"><span
                        style="color:black;mso-fareast-language:EN-US">20170904<o:p></o:p></span></p>
                  </td>
                  <td style="padding:.75pt .75pt 0cm
                    .75pt;height:15.0pt" nowrap="nowrap" valign="bottom">
                    <p class="MsoNormal"><span
                        style="color:black;mso-fareast-language:EN-US">YES<o:p></o:p></span></p>
                  </td>
                </tr>
              </tbody>
            </table>
            <p class="MsoNormal"><o:p> </o:p></p>
          </div>
          <div>
            <p class="MsoNormal"><o:p> </o:p></p>
          </div>
          <div>
            <p class="MsoNormal">Best,<o:p></o:p></p>
          </div>
          <div>
            <p class="MsoNormal">Julien<o:p></o:p></p>
          </div>
          <div>
            <p class="MsoNormal"><o:p> </o:p></p>
          </div>
          <div>
            <p class="MsoNormal"><o:p> </o:p></p>
          </div>
          <div>
            <p class="MsoNormal" style="margin-bottom:12.0pt"><o:p> </o:p></p>
          </div>
        </div>
        <div>
          <p class="MsoNormal"><br clear="all">
            <o:p></o:p></p>
          <div>
            <div>
              <div>
                <div>
                  <div>
                    <div>
                      <div>
                        <div>
                          <p class="MsoNormal">--<br>
                            Julien Marrec, EBCP, BPI MFBA<br>
                            Owner at <a href="http://www.effibem.com"
                              target="_blank" moz-do-not-send="true">EffiBEM</a><br>
                            T: +33 6 95 14 42 13<br>
                            <span style="color:black"><br>
                              LinkedIn (</span><a
                              href="https://www.linkedin.com/in/julienmarrec"
                              target="_blank" moz-do-not-send="true">en</a><span
                              style="color:black">) <i>| </i>(</span><a
href="https://fr.linkedin.com/in/julienmarrec/fr" target="_blank"
                              moz-do-not-send="true">fr</a><span
                              style="color:black">) : </span><o:p></o:p></p>
                        </div>
                      </div>
                    </div>
                  </div>
                </div>
              </div>
            </div>
          </div>
          <p class="MsoNormal"><o:p> </o:p></p>
          <div>
            <p class="MsoNormal"><span lang="NL">2018-07-19 3:55
                GMT+02:00 Joe Huang via Bldg-sim <</span><a
                href="mailto:bldg-sim@lists.onebuilding.org"
                target="_blank" moz-do-not-send="true"><span lang="NL">bldg-sim@lists.onebuilding.org</span></a><span
                lang="NL">>:<o:p></o:p></span></p>
            <blockquote style="border:none;border-left:solid #CCCCCC
              1.0pt;padding:0cm 0cm 0cm
6.0pt;margin-left:4.8pt;margin-top:5.0pt;margin-right:0cm;margin-bottom:5.0pt">
              <div>
                <p>Roel,<o:p></o:p></p>
                <p>I'm not an expert in this field of liquid
                  precipitation, but here are my thoughts in response to
                  your comments:<o:p></o:p></p>
                <p>1) I'm not aware of drastic differences in rainfall
                  between the airport and more urban areas of a city. 
                  However, there are noticeable differences in wind
                  speeds for which, in the absence of measured data, are
                  accounted for in building energy modeling by
                  TERRAIN-PARAMETERs dependent on the general site
                  description, e.g., 1.00 for flat terrain such as an
                  airport, 0.85 for rural,  0.67 for urban or forest,
                  and 0.47 for urban centers with tall building, and the
                  height difference between the measured data and the
                  site.  if you're having difficulty in finding either
                  measured wind speed or driving rain data (good luck!),
                  I would suggest you just use the airport data and
                  adjust that with a Terrain Parameter.<o:p></o:p></p>
                <p>2) If you insist on getting rain and wind speed data
                  for a suburban location, I'm sure those can be found
                  among the 8,000+ weather stations for which I have
                  hourly weather data, but the locations would be
                  anywhere in the world.  Do you care where is the
                  location?  <o:p></o:p></p>
                <p>3) The Met Eirerann paper describes a driving rain
                  index, but does not provide the equation.  In thinking
                  about it again (note that I've only thought about this
                  after reading your original query), I think a
                  plausible approach would be:<o:p></o:p></p>
                <p>   a. find the approximate downward velocity of
                  falling rain (a quick web search for "How fast do
                  raindrops fall" gave the answer of 10 m/sec)<o:p></o:p></p>
                <p>   b. divide that by the (adjusted) wind speed to get
                  the fraction that would fall on a vertical surface,
                  i.e., driving rain.<o:p></o:p></p>
                <p>   c. multiply the "driving rain fraction" by the
                  reported rain fall to get the amount of driving rain.<o:p></o:p></p>
                <p>   c. use the wind direction to apportion the driving
                  rain by the wall orientation. <o:p></o:p></p>
                <p>It's still not clear to me what is the primary
                  motivation for your investigation.  Is it to determine
                  the amount of driving rain at a particular location or
                  weather file?  to validate the method to calculate
                  driving rain?  Or to just get a handle on how much
                  driving rain is there ?<o:p></o:p></p>
                <p>Joe<o:p></o:p></p>
                <pre>Joe Huang<o:p></o:p></pre>
                <pre>White Box Technologies, Inc.<o:p></o:p></pre>
                <pre>346 Rheem Blvd., Suite 205A<o:p></o:p></pre>
                <pre>Moraga CA 94556<o:p></o:p></pre>
                <pre><a href="mailto:yjhuang@whiteboxtechnologies.com" target="_blank" moz-do-not-send="true">yjhuang@whiteboxtechnologies.com</a><o:p></o:p></pre>
                <pre><a href="http://weather.whiteboxtechnologies.com" target="_blank" moz-do-not-send="true">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data<o:p></o:p></pre>
                <pre>(o) (925)388-0265<o:p></o:p></pre>
                <pre>(c) (510)928-2683<o:p></o:p></pre>
                <pre>"building energy simulations at your fingertips"<o:p></o:p></pre>
                <div>
                  <div>
                    <div>
                      <p class="MsoNormal">On 7/18/2018 5:43 AM, Roel
                        Tersteeg wrote:<o:p></o:p></p>
                    </div>
                    <blockquote
                      style="margin-top:5.0pt;margin-bottom:5.0pt">
                      <div>
                        <p class="MsoNormal"
                          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">Dear
                          Joe and Luis,<o:p></o:p></p>
                        <p class="MsoNormal"
                          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"> <o:p></o:p></p>
                        <p class="MsoNormal"
                          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">Thank
                          you for your replies to my question and
                          apologies for my very late reply to you both.
                          Unfortunately the data from official, synoptic
                          weather stations is airfield data and thus not
                          applicable to my situation as there is no
                          difference in microclimate (no changes in wind
                          or rainfall due to surrounding building). The
                          same goes for the Met Eireann information (if
                          of interest, the Climatological notes 13 and 3
                          about wind driven rain can also be found and
                          downloaded here as well: <a
                            href="https://www.met.ie/education/publications/climatological-notes"
                            target="_blank" moz-do-not-send="true">
https://www.met.ie/education/publications/climatological-notes</a>)<o:p></o:p></p>
                        <p class="MsoNormal"
                          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"> <o:p></o:p></p>
                        <p class="MsoNormal"
                          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">I
                          am looking specific for wind driven rain data,
                          or indeed combined wind and precipitation data
                          that can be converted to wind driven rain, for
                          different (sub)urban settings. The suggestion
                          for looking at ‘personal weather stations’ is
                          very interesting, although this has the issue
                          of uncertainty about the quality of the
                          measurements.<o:p></o:p></p>
                        <p class="MsoNormal"
                          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"> <o:p></o:p></p>
                        <p class="MsoNormal"
                          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">Kind
                          regards,<o:p></o:p></p>
                        <p class="MsoNormal"
                          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"> <o:p></o:p></p>
                        <p class="MsoNormal"
                          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">Roel
                          <o:p></o:p></p>
                        <p class="MsoNormal"
                          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"> <o:p></o:p></p>
                        <p class="MsoNormal"
                          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><b><span
                              lang="EN-US">From:</span></b><span
                            lang="EN-US"> Luis Miguel Blanes Restoy </span><a
                            href="mailto:lmblanes@gmail.com"
                            target="_blank" moz-do-not-send="true"><span
                              lang="EN-US"><lmblanes@gmail.com></span></a><span
                            lang="EN-US"> <br>
                            <b>Sent:</b> 06 July 2018 14:34<br>
                            <b>To:</b> Joe Huang </span><a
                            href="mailto:yjhuang@whiteboxtechnologies.com"
                            target="_blank" moz-do-not-send="true"><span
                              lang="EN-US"><yjhuang@whiteboxtechnologies.com></span></a><span
                            lang="EN-US"><br>
                            <b>Cc:</b> </span><a
                            href="mailto:bldg-sim@lists.onebuilding.org"
                            target="_blank" moz-do-not-send="true"><span
                              lang="EN-US">bldg-sim@lists.onebuilding.org</span></a><span
                            lang="EN-US"><br>
                            <b>Subject:</b> Re: [Bldg-sim] Wind driven
                            rain data</span><o:p></o:p></p>
                        <p class="MsoNormal"
                          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"> <o:p></o:p></p>
                        <div>
                          <p class="MsoNormal"
                            style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">Joe<o:p></o:p></p>
                          <div>
                            <p class="MsoNormal"
                              style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">Try
                              this link<o:p></o:p></p>
                          </div>
                          <div>
                            <p class="MsoNormal"
                              style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><a
href="https://es.scribd.com/document/346851908/MET-Driving-Rain-Index-IRELAND#close_user_settings_menu"
                                target="_blank" moz-do-not-send="true">https://es.scribd.com/document/346851908/MET-Driving-Rain-Index-IRELAND#close_user_settings_menu</a><o:p></o:p></p>
                          </div>
                          <div>
                            <p class="MsoNormal"
                              style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">Regards<o:p></o:p></p>
                          </div>
                          <div>
                            <p class="MsoNormal"
                              style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">Luis<o:p></o:p></p>
                          </div>
                        </div>
                        <p class="MsoNormal"
                          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"> <o:p></o:p></p>
                        <div>
                          <div>
                            <p class="MsoNormal"
                              style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">On
                              Thu 5 Jul 2018, 04:28 Joe Huang, <<a
                                href="mailto:yjhuang@whiteboxtechnologies.com"
                                target="_blank" moz-do-not-send="true">yjhuang@whiteboxtechnologies.com</a>>
                              wrote:<o:p></o:p></p>
                          </div>
                          <blockquote
                            style="border:none;border-left:solid #CCCCCC
                            1.0pt;padding:0cm 0cm 0cm
6.0pt;margin-left:4.8pt;margin-top:5.0pt;margin-right:0cm;margin-bottom:5.0pt">
                            <div>
                              <p>Luis,<o:p></o:p></p>
                              <p>Thanks for the tip.  I went to the
                                link, which by the way is for the Irish
                                Meteorological Service,  and read that
                                it said, "<span
style="font-size:12.0pt;font-family:"Arial",sans-serif;color:#434343;background:white">The
                                  amount of rain received by a wall
                                  correlates fairly well with the
                                  product of rainfall and the component
                                  of the wind speed normal to the wall.
                                  This led Lacy and Shellard to propose
                                  the product of the mean annual
                                  rainfall and the mean annual wind
                                  speed as a driving rain index which is
                                  proportional to the total rainfall
                                  driven in one year on to a vertical
                                  surface always facing the wind", 
                                  which is functionally quite close to
                                  what I was envisioning, i.e., WDR = LP
                                  * f(wspd, wdir),  where LP is Liquid
                                  Precipitation or Rainfall. However,
                                  when I clicked on the link to the
                                  actual paper cited,  the Meteireann
                                  web site responded that  "404: Page
                                  not found".  Therefore, I still don't
                                  know the function that converts LP or
                                  rainfall to WDR.</span><o:p></o:p></p>
                              <p><span
style="font-size:12.0pt;font-family:"Arial",sans-serif;color:#434343;background:white">Joe</span><o:p></o:p></p>
                              <pre>Joe Huang<o:p></o:p></pre>
                              <pre>White Box Technologies, Inc.<o:p></o:p></pre>
                              <pre>346 Rheem Blvd., Suite 205A<o:p></o:p></pre>
                              <pre>Moraga CA 94556<o:p></o:p></pre>
                              <pre><a href="mailto:yjhuang@whiteboxtechnologies.com" target="_blank" moz-do-not-send="true">yjhuang@whiteboxtechnologies.com</a><o:p></o:p></pre>
                              <pre><a href="http://weather.whiteboxtechnologies.com" target="_blank" moz-do-not-send="true">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data<o:p></o:p></pre>
                              <pre>(o) (925)388-0265<o:p></o:p></pre>
                              <pre>(c) (510)928-2683<o:p></o:p></pre>
                              <pre>"building energy simulations at your fingertips"<o:p></o:p></pre>
                              <div>
                                <p class="MsoNormal"
                                  style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">On
                                  7/4/2018 2:30 PM, Luis Miguel Blanes
                                  Restoy wrote:<o:p></o:p></p>
                              </div>
                              <blockquote
                                style="margin-top:5.0pt;margin-bottom:5.0pt">
                                <div>
                                  <div>
                                    <p class="MsoNormal"
                                      style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">Hi
                                      Roel and Joe<o:p></o:p></p>
                                  </div>
                                  <div>
                                    <p class="MsoNormal"
                                      style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"> <o:p></o:p></p>
                                  </div>
                                  <div>
                                    <p class="MsoNormal"
                                      style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">Did
                                      you look at available data from
                                      Met Eireann? There is a paper
                                      regarding WDR index calculation
                                      method that may be of your
                                      interest. See below link.<o:p></o:p></p>
                                  </div>
                                  <div>
                                    <p class="MsoNormal"
                                      style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"> <o:p></o:p></p>
                                  </div>
                                  <div>
                                    <p class="MsoNormal"
                                      style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><a
href="https://www.met.ie/climate/what-we-measure/rainfall"
                                        target="_blank"
                                        moz-do-not-send="true">https://www.met.ie/climate/what-we-measure/rainfall#</a><o:p></o:p></p>
                                  </div>
                                  <div>
                                    <p class="MsoNormal"
                                      style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"> <o:p></o:p></p>
                                  </div>
                                  <div>
                                    <p class="MsoNormal"
                                      style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">Regards<o:p></o:p></p>
                                  </div>
                                  <div>
                                    <p class="MsoNormal"
                                      style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">Luis<o:p></o:p></p>
                                  </div>
                                  <div>
                                    <p class="MsoNormal"
                                      style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"> <o:p></o:p></p>
                                    <p> <o:p></o:p></p>
                                    <div>
                                      <div>
                                        <p class="MsoNormal"
                                          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">On
                                          Wed 4 Jul 2018, 22:12 Joe
                                          Huang via Bldg-sim, <<a
                                            href="mailto:bldg-sim@lists.onebuilding.org"
                                            target="_blank"
                                            moz-do-not-send="true">bldg-sim@lists.onebuilding.org</a>>
                                          wrote:<o:p></o:p></p>
                                      </div>
                                      <blockquote
                                        style="border:none;border-left:solid
                                        #CCCCCC 1.0pt;padding:0cm 0cm
                                        0cm
6.0pt;margin-left:4.8pt;margin-top:5.0pt;margin-right:0cm;margin-bottom:5.0pt">
                                        <div>
                                          <p>What is your definition for
                                            Wind-driven Rain? 
                                            Practically all weather
                                            station reports, including
                                            official stations available
                                            in NOAA's ISD as well as
                                            unofficial "Personal Weather
                                            Stations" hosted on
                                            WeatherUnderground, contain
                                            information on liquid
                                            precipitation (LP), wind
                                            speed, and wind direction. 
                                            Can the WDR be calculated
                                            from these standard
                                            parameters, maybe as the LP
                                            * f(wspd, wdir) ?<o:p></o:p></p>
                                          <p>Joe<o:p></o:p></p>
                                          <div>
                                            <p class="MsoNormal"
                                              style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">On
                                              7/4/2018 3:52 AM, Roel
                                              Tersteeg via Bldg-sim
                                              wrote:<o:p></o:p></p>
                                          </div>
                                          <blockquote
                                            style="margin-top:5.0pt;margin-bottom:5.0pt">
                                            <div>
                                              <p class="MsoNormal"
                                                style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">Dear
                                                all,<o:p></o:p></p>
                                              <p class="MsoNormal"
                                                style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"> <o:p></o:p></p>
                                              <p class="MsoNormal"
                                                style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">For
                                                the verification of a
                                                model to estimate wind
                                                driven rain (WDR) I
                                                would like to use WDR
                                                data from different
                                                microclimates (rural,
                                                (sub)urban). I have
                                                access to several data
                                                sets of free field or
                                                airfield WDR
                                                measurements from
                                                different locations and
                                                the results from a
                                                measurement campaign in
                                                Vancouver. To better
                                                evaluate the model I
                                                would like to use
                                                measured data from one
                                                or more locations with
                                                different microclimates,
                                                not being free field or
                                                airfield sites.<o:p></o:p></p>
                                              <p class="MsoNormal"
                                                style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"> <o:p></o:p></p>
                                              <p class="MsoNormal"
                                                style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">My
                                                question is if someone
                                                knows if measurements
                                                are available of wind
                                                driven rain in one or
                                                more microclimates?<o:p></o:p></p>
                                              <p class="MsoNormal"
                                                style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"> <o:p></o:p></p>
                                              <p class="MsoNormal"
                                                style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">Kind
                                                regards,<o:p></o:p></p>
                                              <p class="MsoNormal"
                                                style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"> <o:p></o:p></p>
                                              <p class="MsoNormal"
                                                style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">Roel
                                                Tersteeg MSc<o:p></o:p></p>
                                              <p class="MsoNormal"
                                                style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"> <o:p></o:p></p>
                                              <p class="MsoNormal"
                                                style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
                                                  style="color:gray">PhD-student
                                                </span><o:p></o:p></p>
                                              <p class="MsoNormal"
                                                style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
                                                  style="color:gray">Building
                                                  Energy Research Group</span><o:p></o:p></p>
                                              <p class="MsoNormal"
                                                style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
                                                  style="color:gray">School
                                                  of Architecture,
                                                  Building and Civil
                                                  Engineering</span><o:p></o:p></p>
                                              <p class="MsoNormal"
                                                style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
                                                  style="color:gray">Loughborough
                                                  University</span><o:p></o:p></p>
                                              <p class="MsoNormal"
                                                style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
                                                  style="color:gray">T:
                                                  +44 77 56 10 90 54</span><o:p></o:p></p>
                                              <p class="MsoNormal"
                                                style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
                                                  style="color:gray">E:
                                                </span><a
                                                  href="mailto:R.M.Tersteeg@lboro.ac.uk"
                                                  target="_blank"
                                                  moz-do-not-send="true"><span
                                                    style="color:gray">R.M.Tersteeg@lboro.ac.uk</span></a><o:p></o:p></p>
                                              <p class="MsoNormal"
                                                style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"> <o:p></o:p></p>
                                            </div>
                                          </blockquote>
                                          <p class="MsoNormal"
                                            style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"> <o:p></o:p></p>
                                        </div>
                                        <p class="MsoNormal"
                                          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">_______________________________________________<br>
                                          Bldg-sim mailing list<br>
                                          <a
href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org"
                                            target="_blank"
                                            moz-do-not-send="true">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
                                          To unsubscribe from this
                                          mailing list send  a blank
                                          message to <a
                                            href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG"
                                            target="_blank"
                                            moz-do-not-send="true">
BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><o:p></o:p></p>
                                      </blockquote>
                                    </div>
                                  </div>
                                </div>
                              </blockquote>
                              <p class="MsoNormal"
                                style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"> <o:p></o:p></p>
                            </div>
                          </blockquote>
                        </div>
                      </div>
                    </blockquote>
                    <p class="MsoNormal"><o:p> </o:p></p>
                  </div>
                </div>
              </div>
              <p class="MsoNormal" style="margin-bottom:12.0pt"><br>
                _______________________________________________<br>
                Bldg-sim mailing list<br>
                <a
href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org"
                  target="_blank" moz-do-not-send="true">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
                To unsubscribe from this mailing list send  a blank
                message to <a
                  href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG"
                  moz-do-not-send="true">
                  BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><o:p></o:p></p>
            </blockquote>
          </div>
          <p class="MsoNormal"><o:p> </o:p></p>
        </div>
      </div>
    </blockquote>
    <br>
  </body>
</html>