<div dir="ltr"><div>Christopher,<br><br>In terms of geometry, the input methodology has some good points, even if it appears a bit clunky. The latest version 4.8 has some improvements. Ida also has very good IFC import capability. I can usually re-use about 70% from unaudited Revit models, more if the model is well constructed. Sketchup can be input as well.<br><br>The user interface for generating building models is friendly and uncluttered. IDA rarely get's a "facelift". This is a good thing - it's evolving. It still uses the floppy disk icon! It handles data predictably and robustly without any "volatile" relationships between data inputs. The underlying component models can be accessed if using the expert version (i.e. the maths that describe objects such as zones, coil's, boreholes, etc). There's a schematic modelling interface enabling the user to build sub-system models and hack into details in larger building models. It has an ice rink and swimming pool module. I understand this was used for calculations on the ice making facility at the new Stadium in Stockholm (they can ice the whole pitch!). There is a 90.1 tool available.<br><br>The thing that really is unique to IDA is that it simulates plant, controls and network airflow in a very integrated way. In fact, these three aspects are permanently coupled. They cannot be uncoupled. This makes for a very robust analysis. The nearest example I can think of that compares is simulating IES with ApacheHVAC and Macroflo activated. This can quantify air movement under both natural and mechanical ventilation combined. A direct comparison with other software cannot be made though. Some quite arbitarily complex systems can be made. For example, mixed mode systems with lockout's between the VAV boxes and actuated louvres, unusual SAT reset strategies, dual duct systems. These all simulate the coupled controls + network aiflow + plant in a very stable manner. You don't need to make the timestep very small to make the simulation very stable, because the timestep varies dynamically during runtime seeking the most stable computational solution. Waterside modelling is a bit harder but can be done with a bit of practice.<br><br>I could go on, but it's getting late.<br><br></div>Chris<br><div><br><div class="gmail_extra"><div class="gmail_quote">On Fri, Feb 23, 2018 at 8:29 PM, Jones, Christopher via Bldg-sim <span dir="ltr"><<a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
<div lang="EN-US">
<div class="gmail-m_-4380258441131036955WordSection1">
<p class="MsoNormal"><span style="font-size:11pt;font-family:"Calibri",sans-serif;color:rgb(31,73,125)">Thank you Javed,<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:"Calibri",sans-serif;color:rgb(31,73,125)">I am interested in what you say about modeling the geometry. I am a big fan of SketchUp for doing the geometry – works for Sefaira, OpenStudio and IES VE. Are
you indicating that IDA ICE has a more cumbersome geometry modeling interface?<u></u><u></u></span></p><span class="gmail-">
<p class="MsoNormal"><span style="font-size:11pt;font-family:"Calibri",sans-serif;color:rgb(31,73,125)"><u></u> <u></u></span></p>
<p class="MsoNormal"><b><span style="font-size:6pt;font-family:"Calibri",sans-serif;color:rgb(31,73,125)"><u></u> <u></u></span></b></p>
<p class="MsoNormal"><b><span style="font-size:10pt;font-family:"Arial",sans-serif;color:rgb(31,73,125)" lang="EN-GB">Christopher R. Jones</span></b><span style="font-size:10pt;font-family:"Arial",sans-serif;color:rgb(31,73,125)" lang="EN-GB">,
P.Eng.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10pt;font-family:"Arial",sans-serif;color:rgb(31,73,125)" lang="EN-GB">Technical Specialist<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10pt;font-family:"Arial",sans-serif;color:rgb(31,73,125)" lang="EN-GB">Sustainability & Energy<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:8pt;font-family:"Arial",sans-serif;color:rgb(31,73,125)"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:"Calibri",sans-serif;color:rgb(31,73,125)"><img id="gmail-m_-4380258441131036955Picture_x0020_15" src="cid:image001.png@01D3ACBB.1200A3D0" width="78" height="37"></span><span style="font-size:10pt;font-family:"Arial",sans-serif;color:rgb(31,73,125)"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10pt;font-family:"Arial",sans-serif;color:rgb(31,73,125)">T <a href="tel:%28416%29%20644-0252" value="+14166440252" target="_blank">+1 416-644-0252</a><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10pt;font-family:"Arial",sans-serif;color:rgb(31,73,125)"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:10pt;font-family:"Arial",sans-serif;color:rgb(31,73,125)">2300 Yonge Street, Suite 2300<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10pt;font-family:"Arial",sans-serif;color:rgb(31,73,125)">Toronto, ON M4P 1E4 Canada</span><span style="font-size:10pt;font-family:"Arial",sans-serif;color:rgb(31,73,125)" lang="EN-GB"><br>
<br>
</span><span style="font-size:10pt;font-family:"Arial",sans-serif;color:rgb(31,73,125)"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10pt;font-family:"Arial",sans-serif;color:rgb(31,73,125)"><a href="http://wsp.com" target="_blank"><span style="color:rgb(5,99,193)">wsp.com</span></a><u></u><u></u></span></p>
<p class="MsoNormal"><u><span style="font-size:11pt;font-family:"Calibri",sans-serif;color:blue" lang="EN-CA"><u></u><span style="text-decoration:none"> </span><u></u></span></u></p>
<p class="MsoNormal"><b><span style="font-size:11pt;font-family:"Calibri",sans-serif;color:rgb(127,127,127)"><u></u> <u></u></span></b></p>
<p class="MsoNormal"><i><span style="font-size:10pt;font-family:"Arial",sans-serif;color:rgb(110,169,0)">Please consider the environment before printing...<u></u><u></u></span></i></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:"Calibri",sans-serif;color:rgb(31,73,125)" lang="EN-CA"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:"Calibri",sans-serif;color:rgb(31,73,125)"><u></u> <u></u></span></p>
</span><p class="MsoNormal"><b><span style="font-size:11pt;font-family:"Calibri",sans-serif">From:</span></b><span style="font-size:11pt;font-family:"Calibri",sans-serif"> Javed Iqbal [mailto:<a href="mailto:javedvit@gmail.com" target="_blank">javedvit@gmail.com</a>]
<br>
<b>Sent:</b> Friday, February 23, 2018 1:16 PM<br>
<b>To:</b> Jones, Christopher <<a href="mailto:Christopher.r.Jones@wsp.com" target="_blank">Christopher.r.Jones@wsp.com</a>><br>
<b>Cc:</b> <a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Bldg-sim] IDA ICE experience<u></u><u></u></span></p><div><div class="gmail-h5">
<p class="MsoNormal"><u></u> <u></u></p>
<div>
<div>
<p class="MsoNormal"><span style="font-size:18pt;font-family:"Arial",sans-serif;color:rgb(7,55,99)">Hello,<u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:18pt;font-family:"Arial",sans-serif;color:rgb(7,55,99)"><u></u> <u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:18pt;font-family:"Arial",sans-serif;color:rgb(7,55,99)">I have used IDA ICE sometime ago. The main advantage of IDA ICE over other simulation programs is implementing control sequences which is pretty powerful. I believe,
It gives greater flexibility in modeling and implementing controls for <span style="background:white none repeat scroll 0% 0%">
passive strategies </span>such as natural ventilation, double facade compared etc. 3D modeling is heck, however, due to very particular about own geometrical interface unlike E+ which gives various means to import stable geometry.<u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:18pt;font-family:"Arial",sans-serif;color:rgb(7,55,99)"><u></u> <u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:18pt;font-family:"Arial",sans-serif;color:rgb(7,55,99)">This is my perception, developed while used it for short time and might vary compared to someone who is expert user of IDA ICE.<u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:18pt;font-family:"Arial",sans-serif;color:rgb(7,55,99)"><u></u> <u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:18pt;font-family:"Arial",sans-serif;color:rgb(7,55,99)">Hope this helps!!<u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:18pt;font-family:"Arial",sans-serif;color:rgb(7,55,99)"><u></u> <u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:18pt;font-family:"Arial",sans-serif;color:rgb(7,55,99)"> <u></u><u></u></span></p>
</div>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
<div>
<p class="MsoNormal">On Fri, Feb 23, 2018 at 6:54 PM, Jones, Christopher via Bldg-sim <<a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.<wbr>org</a>> wrote:<u></u><u></u></p>
<blockquote style="border-width:medium medium medium 1pt;border-style:none none none solid;border-color:currentcolor currentcolor currentcolor rgb(204,204,204);padding:0in 0in 0in 6pt;margin-left:4.8pt;margin-right:0in">
<div>
<div>
<p class="MsoNormal">I am wondering about experience with IDA ICE. Some are claiming it is the greatest thing since sliced bread. The blurb on their website sounds encouraging but I am always nervous
when the cost of software isn’t readily apparent. <u></u><u></u></p>
<p class="MsoNormal"> <u></u><u></u></p>
<p class="MsoNormal">We are using eQuest, IES VE and OpenStudio. Are there things IDA ICE can to that these other tools cannot? If IDA ICE has good ice rink capabilities then it might be worth investigating.<u></u><u></u></p>
<p class="MsoNormal"> <u></u><u></u></p>
<p class="MsoNormal"><b><span style="font-size:6pt"> </span></b><u></u><u></u></p>
<p class="MsoNormal"><b><span style="font-size:10pt;font-family:"Arial",sans-serif" lang="EN-GB">Christopher R. Jones</span></b><span style="font-size:10pt;font-family:"Arial",sans-serif" lang="EN-GB">,
P.Eng.</span><u></u><u></u></p>
<p class="MsoNormal"><span style="font-size:10pt;font-family:"Arial",sans-serif" lang="EN-GB">Technical Specialist</span><u></u><u></u></p>
<p class="MsoNormal"><span style="font-size:10pt;font-family:"Arial",sans-serif" lang="EN-GB">Sustainability & Energy</span><u></u><u></u></p>
<p class="MsoNormal"><span style="font-size:8pt;font-family:"Arial",sans-serif"> </span><u></u><u></u></p>
<p class="MsoNormal"><img id="gmail-m_-4380258441131036955m_-3337302117521781239Picture_x0020_15" src="cid:image001.png@01D3ACBB.1200A3D0" width="78" border="0" height="37"><u></u><u></u></p>
<p class="MsoNormal"><span style="font-size:10pt;font-family:"Arial",sans-serif">T <a href="tel:%28416%29%20644-0252" value="+14166440252" target="_blank">+1 416-644-0252</a></span><u></u><u></u></p>
<p class="MsoNormal"><span style="font-size:10pt;font-family:"Arial",sans-serif"> </span><u></u><u></u></p>
<p class="MsoNormal"><span style="font-size:10pt;font-family:"Arial",sans-serif">2300 Yonge Street, Suite 2300</span><u></u><u></u></p>
<p class="MsoNormal" style="margin-bottom:12pt"><span style="font-size:10pt;font-family:"Arial",sans-serif">Toronto, ON M4P 1E4 Canada</span><u></u><u></u></p>
<p class="MsoNormal"><span style="font-size:10pt;font-family:"Arial",sans-serif"><a href="http://wsp.com" target="_blank"><span style="color:rgb(5,99,193)">wsp.com</span></a></span><u></u><u></u></p>
<p class="MsoNormal"><span style="color:blue" lang="EN-CA"> </span><u></u><u></u></p>
<p class="MsoNormal">
<b><span style="color:rgb(127,127,127)"> </span></b><u></u><u></u></p>
<p class="MsoNormal">
<i><span style="font-size:10pt;font-family:"Arial",sans-serif;color:rgb(110,169,0)">Please consider the environment before printing...</span></i><u></u><u></u></p>
<p class="MsoNormal"><span lang="EN-CA"> </span><u></u><u></u></p>
<p class="MsoNormal"> <u></u><u></u></p>
</div>
<p class="MsoNormal"><u></u> <u></u></p>
<div class="MsoNormal" style="text-align:center" align="center">
<hr width="100%" size="2" align="center">
</div>
<p class="MsoNormal"><span style="font-size:7.5pt;font-family:"Arial",sans-serif;color:gray"><br>
<br>
NOTICE: This communication and any attachments ("this message") may contain information which is privileged, confidential, proprietary or otherwise subject to restricted disclosure under applicable law. This message is for the sole use of the intended recipient(s).
Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on, this message is strictly prohibited. If you have received this message in error, or you are not an authorized or intended recipient, please notify
the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies. You are receiving this communication because you are listed as a current WSP contact. Should you have any questions
regarding WSP's electronic communications policy, please consult our Anti-Spam Commitment at
<a href="http://www.wsp.com/casl" target="_blank">www.wsp.com/casl</a>. For any concern or if you believe you should not be receiving this message, please forward this message to
<a href="mailto:caslcompliance@wsp.com" target="_blank">caslcompliance@wsp.com</a> so that we can promptly address your request. Note that not all messages sent by WSP qualify as commercial electronic messages.
<br>
<br>
AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »), peut contenir des renseignements ou de l'information privilégiés, confidentiels, propriétaires ou à divulgation restreinte en vertu de la loi. Ce message est destiné à l'usage exclusif
du/des destinataire(s) voulu(s). Toute utilisation non permise, divulgation, lecture, reproduction, modification, diffusion ou distribution est interdite. Si vous avez reçu ce message par erreur, ou que vous n'êtes pas un destinataire autorisé ou voulu, veuillez
en aviser l'expéditeur immédiatement et détruire le message et toute copie électronique ou imprimée. Vous recevez cette communication car vous faites partie des contacts de WSP. Si vous avez des questions concernant la politique de communications électroniques
de WSP, veuillez consulter notre Engagement anti-pourriel au <a href="http://www.wsp.com/lcap" target="_blank">
www.wsp.com/lcap</a>. Pour toute question ou si vous croyez que vous ne devriez pas recevoir ce message, prière de le transférer au
<a href="mailto:conformitelcap@wsp.com" target="_blank">conformitelcap@wsp.com</a> afin que nous puissions rapidement traiter votre demande. Notez que ce ne sont pas tous les messages transmis par WSP qui constituent des messages electroniques commerciaux.
<br>
</span><br>
<span style="font-size:7.5pt;font-family:"Arial",sans-serif;color:whitesmoke"><br>
<br>
-LAEmHhHzdJzBlTWfa4Hgs7pbKl </span><u></u><u></u></p>
</div>
<p class="MsoNormal" style="margin-bottom:12pt"><br>
______________________________<wbr>_________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/<wbr>listinfo.cgi/bldg-sim-<wbr>onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">
BLDG-SIM-UNSUBSCRIBE@<wbr>ONEBUILDING.ORG</a><u></u><u></u></p>
</blockquote>
</div>
<p class="MsoNormal"><br>
<br clear="all">
<u></u><u></u></p>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<p class="MsoNormal">-- <u></u><u></u></p>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<p class="MsoNormal"><i><span style="font-size:13.5pt;font-family:"Arial",sans-serif"><u></u> <u></u></span></i></p>
</div>
<p class="MsoNormal"><span style="font-size:13.5pt;font-family:"Arial",sans-serif;color:rgb(7,55,99)">Javed Iqbal, LEED AP, CEA<br>
Sr. Energy Analyst</span><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div></div></div>
</div>
<br>______________________________<wbr>_________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" rel="noreferrer" target="_blank">http://lists.onebuilding.org/<wbr>listinfo.cgi/bldg-sim-<wbr>onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@<wbr>ONEBUILDING.ORG</a><br>
<br></blockquote></div><br></div></div></div>