<html>
  <head>
    <meta http-equiv="Content-Type" content="text/html; charset=utf-8">
  </head>
  <body text="#000000" bgcolor="#FFFFFF">
    <p>From my experience, such kinds of counter-intuitive results,
      e.g., cooling energies going up with lower U-values,  are due to
      overlooked systems/loads interactions rather than arcane loads
      considerations such as spectral properties of window glazings. <br>
    </p>
    <p>The three interactions that I would look are:</p>
    <p>(1) does the system have an economizer that vents the cooling
      loads when the indoor temperature or enthalpy exceed that outdoor
      ?</p>
    <p>(2) is the system sizing the same for both runs? If not, fix the
      system size to the larger from the two autosized runs.</p>
    <p>(3) (this gets rather arcane but explained the anomaly for
      increased heating in mild cooling climates like the Pacific
      Northwest) change Cooling Control from CONSTANT to WARMEST, i.e.,
      control cooling control for the warmest zone rather than all
      zones.<br>
    </p>
    <p>Joe<br>
    </p>
    <pre class="moz-signature" cols="72">Joe Huang    
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a class="moz-txt-link-freetext" href="http://weather.whiteboxtechnologies.com">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data
<a class="moz-txt-link-freetext" href="http://www.whiteboxtechnologies.com">http://www.whiteboxtechnologies.com</a>
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
    <div class="moz-cite-prefix">On 11/3/2017 7:15 AM, Javed Iqbal via
      Bldg-sim wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CAEF2+-n2LsMx45STmu7vt47rfkjucfbkG6FNiKdVWHJN9=2daw@mail.gmail.com">
      <div dir="auto">In my past experiences, such problems were
        resolved by using detailed spectral properties      (LBNL window
        output) in eQuest for an Indian composite climate case.
        <div dir="auto">
          <div dir="auto"> </div>
          <div dir="auto"><br>
          </div>
          <div dir="auto"><br>
            <div data-smartmail="gmail_signature" dir="auto">Sent from
              mobile, pls excuse typos</div>
          </div>
        </div>
      </div>
      <div class="gmail_extra"><br>
        <div class="gmail_quote">On Nov 3, 2017 2:47 PM, "akshay gupta"
          <<a href="mailto:akshaykg@gmail.com" target="_blank"
            moz-do-not-send="true">akshaykg@gmail.com</a>> wrote:<br
            type="attribution">
          <blockquote class="gmail_quote" style="margin:0 0 0
            .8ex;border-left:1px #ccc solid;padding-left:1ex">
            <div dir="ltr">Hi Javed
              <div><br>
              </div>
              <div>Thanks for helping. We were actually modelling using
                simplified glass inputs. But I can try with detailed
                glass model as well.</div>
              <div><br>
              </div>
              <div>Regards</div>
              <div> </div>
            </div>
            <div class="gmail_extra"><br>
              <div class="gmail_quote">On 3 November 2017 at 18:51,
                Javed Iqbal <span dir="ltr"><<a
                    href="mailto:javedvit@gmail.com" target="_blank"
                    moz-do-not-send="true">javedvit@gmail.com</a>></span>
                wrote:<br>
                <blockquote class="gmail_quote" style="margin:0 0 0
                  .8ex;border-left:1px #ccc solid;padding-left:1ex">
                  <div dir="auto">Thank you, Mr. Jim. 
                    <div dir="auto"><br>
                    </div>
                    <div dir="auto">Apart from internal loads, it's
                      worth looking into window spectral properties.
                      Sometime simple inputs like U value, SHGC and Tvis
                      is not enough and recommended to use whole
                      assembly window properties generated through LBNL
                      window software which could be imported directly
                      into the eQuest.</div>
                    <div dir="auto"><br>
                    </div>
                    <div dir="auto">It might help!!</div>
                    <div dir="auto"><br>
                    </div>
                    <div dir="auto">Regards,<br>
                      <br>
                      <div data-smartmail="gmail_signature" dir="auto">Sent
                        from mobile, pls excuse typos</div>
                    </div>
                  </div>
                  <div class="gmail_extra"><br>
                    <div class="gmail_quote">
                      <div>
                        <div class="m_-1960156932950890873h5">On Nov 3,
                          2017 1:37 PM, "akshay gupta via Bldg-sim" <<a
                            href="mailto:bldg-sim@lists.onebuilding.org"
                            target="_blank" moz-do-not-send="true">bldg-sim@lists.onebuilding.or<wbr>g</a>>
                          wrote:<br type="attribution">
                        </div>
                      </div>
                      <blockquote
                        class="m_-1960156932950890873m_-9026500415791253507quote"
                        style="margin:0 0 0 .8ex;border-left:1px #ccc
                        solid;padding-left:1ex">
                        <div>
                          <div class="m_-1960156932950890873h5">
                            <div dir="ltr">Hi There
                              <div><br>
                              </div>
                              <div>I am facing an issue in eQuest in
                                almost all simulation models for most
                                hot and composite indian climates.
                                Whenever we reduce U-value of glass in
                                model, from Single Glazing U-Value of 1
                                Btu/hr Sqft F to 0.32 Btu/hr Sqft F (or
                                any other U-value lower than 1), we see
                                an increase in energy consumption.</div>
                              <div><br>
                              </div>
                              <div>Can someone point out principal
                                mistake that may be making in the model.</div>
                              <div><br>
                              </div>
                              <div>Thanks in advance.</div>
                              <div><br>
                              </div>
                              <div>Regards</div>
                              <font color="#888888">
                                <div><br>
                                </div>
                                <div>Akshay Gupta </div>
                              </font></div>
                            <br>
                          </div>
                        </div>
                        <span>______________________________<wbr>_________________<br>
                          Bldg-sim mailing list<br>
                          <a
href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org"
                            rel="noreferrer" target="_blank"
                            moz-do-not-send="true">http://lists.onebuilding.org/l<wbr>istinfo.cgi/bldg-sim-onebuildi<wbr>ng.org</a><br>
                          To unsubscribe from this mailing list send  a
                          blank message to <a
                            href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG"
                            target="_blank" moz-do-not-send="true">BLDG-SIM-UNSUBSCRIBE@ONEBUILDI<wbr>NG.ORG</a><br>
                          <br>
                        </span></blockquote>
                    </div>
                    <br>
                  </div>
                </blockquote>
              </div>
              <br>
            </div>
          </blockquote>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Bldg-sim mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
  </body>
</html>