<html><head></head><body><div style="color:#000; background-color:#fff; font-family:HelveticaNeue, Helvetica Neue, Helvetica, Arial, Lucida Grande, sans-serif;font-size:12px"><div id="yui_3_16_0_ym19_1_1488990805244_3755">Hi Energy Modeling Family,<o:p id="yui_3_16_0_ym19_1_1488990805244_3756"></o:p></div><div id="yui_3_16_0_ym19_1_1488990805244_3757"><o:p id="yui_3_16_0_ym19_1_1488990805244_3758"> </o:p></div><div id="yui_3_16_0_ym19_1_1488990805244_3759">I have received a LEED review comment indicating Semi-heated
zones should be modeled identically in the baseline and proposed models. This
is a warehouse with over 1 million square feet of semi-heated space. I have
never been aware of this recommendation. Is this comment based on ASHRAE
90.1-2007?<o:p id="yui_3_16_0_ym19_1_1488990805244_3760"></o:p></div><div id="yui_3_16_0_ym19_1_1488990805244_3761">Any help would be greatly appreciated. <o:p id="yui_3_16_0_ym19_1_1488990805244_3762"></o:p></div><div id="yui_3_16_0_ym19_1_1488990805244_3763"><o:p id="yui_3_16_0_ym19_1_1488990805244_3764"> </o:p></div><div id="yui_3_16_0_ym19_1_1488990805244_3765">Here is the comment:<o:p id="yui_3_16_0_ym19_1_1488990805244_3766"></o:p></div><div id="yui_3_16_0_ym19_1_1488990805244_3767"><i id="yui_3_16_0_ym19_1_1488990805244_3768">“Table 1.4.6 indicates that
the warehouse space is considered as semi-heated space, since the output
heating capacity for the warehouse in this project (10,058 MBH/1,063,827 square
feet) does not meet the heated space criteria (10 Btu/hr-square foot for
climate zone 3) per Table 3.1. <span style="background:yellow;mso-highlight:yellow" id="yui_3_16_0_ym19_1_1488990805244_3769">For semi-heated spaces, the heating equipment (H&V unit) must be
modeled identically in the Baseline and Proposed models between each model
using the actual equipment capacities and efficiencies (i.e. supply fan power,
heating efficiency, and temperature set-points) from the actual design.</span> If
the building envelope in the Proposed model is improved relative to the
Baseline model, the supply fan volume and heating capacity can be autosized in
the Baseline model using the same temperature set points from the Proposed model. Revise the
Proposed and Baseline models so the HVAC equipment capacities and efficiencies
(heating type, supply fan power, heating efficiency, and set point temperatures)
in the warehouse space are modeled identically in each case reflecting the
actual HVAC system parameters. In addition, update Table 1.4.7A and Table
1.4.7B, and provide revised SV-A reports for each model reflecting the changes</i>.”
<o:p id="yui_3_16_0_ym19_1_1488990805244_3770"></o:p></div><div id="yui_3_16_0_ym19_1_1488990805244_3771"><o:p id="yui_3_16_0_ym19_1_1488990805244_3772"> </o:p></div><div id="yui_3_16_0_ym19_1_1488990805244_3773">Thanks<o:p id="yui_3_16_0_ym19_1_1488990805244_3774"></o:p></div><div id="yui_3_16_0_ym19_1_1488990805244_3775"><o:p id="yui_3_16_0_ym19_1_1488990805244_3776"> </o:p></div><div id="yui_3_16_0_ym19_1_1488990805244_3566">
</div><div dir="ltr" id="yui_3_16_0_ym19_1_1488990805244_3777">Mike <o:p id="yui_3_16_0_ym19_1_1488990805244_3778"></o:p></div></div></body></html>