<div dir="ltr"><font color="#000000" face="Times New Roman" size="3">

</font><span style="font-family:"calibri",sans-serif;font-size:11pt"><font color="#000000"><div style="margin:0in 0in 0pt"><span style="font-family:"calibri",sans-serif;font-size:11pt"><font color="#000000">I agree with David that in-unit electric heaters are often specified due to low first cost, and to shift the burden of paying for water heating to tenants. This also allows lowering the rent (not necessarily by the sufficient margin), making apartments more marketable. Interestingly, the Federal Trade Commission requires EnergyGuide labels for a wide range of appliance (e.g. to show that a given TV may cost $15 a year in electricity bills), but there is no such requirement for apartments, even though difference in annual utility costs paid by renters can be $1,000+. So there is no easy way for tenants to do apples to apples comparison of options when shopping for an apartment, such as Annual$=12*Montly_Rent + Annual_Utility_Costs. I think it is safe to assume that a label like that will not be developed on the federal level in the next four years, but there were some initial discussions about it in NY, and there is a tool used in CA for low income tenants called California Utility Allowance Calculator (CUAC). The technical side does not seem too complicated - it could be an asset-style label showing anticipated energy cost paid by tenants, including typical appliances/lighting, HVAC and DHW. </font></span><span style="font-family:"calibri",sans-serif;font-size:11pt"><br></span></div><div style="margin:0in 0in 0pt"><br></div></font></span><p style="margin:0in 0in 0pt"><span style="font-family:"calibri",sans-serif;font-size:11pt"><font color="#000000">The incentive program in NJ allows either
90.1 2013 Appendix G </font><a href="https://www.ashrae.org/resources--publications/bookstore/standard-90-1-appendix-g-2013-performance-rating-method" target="_blank"><font color="#0000ff">w/addendum
BM package</font></a><font color="#000000">, or ASHRAE </font><a href="http://www.buildingenergyquotient.org/asdesigned.html" target="_blank"><font color="#0000ff">bEQ As-Designed</font></a><font color="#000000">
path, and has no rules against fuel switching. With App G path, a central gas
storage water heater is modeled in the baseline for multifamily projects
irrespective of the DHW fuel in the proposed design (Table G3.1, #11 (</font></span><span style="font-family:"helvetica",sans-serif;font-size:9pt"><font color="#000000">a) and Table
G3.1.1-2). </font></span></p><div style="margin:0in 0in 0pt"><span style="font-family:"helvetica",sans-serif;font-size:9pt"><br></span></div><div style="margin:0in 0in 0pt"><span style="font-family:"helvetica",sans-serif;font-size:9pt"></span><span style="font-family:"calibri",sans-serif;font-size:11pt"><font color="#000000">I
agree with Fred that DHW distribution losses do not seem to be covered in App G, and that
there should be some related savings with in-unit heaters versus
central system. One challenge with using exceptional calculations for that is
to come up with a design for the central baseline distribution – e.g. pipe
length, sizes, location, etc. It seems that the intent of App G was to
prescribe DHW heating fuel and system efficiency, and that G3.1.3.6 should be
expanded to include DHW. There seems to be no logical reason for treating space
conditioning piping losses differently compared to DHW piping losses. </font></span></div><div style="margin:0in 0in 0pt"><span style="font-family:"calibri",sans-serif;font-size:11pt"><font color="#000000"><br></font></span></div><div style="margin:0in 0in 0pt"><span style="font-family:"calibri",sans-serif;font-size:11pt"><font color="#000000">I am not convinced that distribution losses in <u>new</u></font><font color="#000000"> buildings meeting 90.1 2013
are significant given insulation and control requirements in Section 7. Quoting
the NREL’s study in Fred's email, “…the range of distribution loss varied widely (5%–61% due to
loop configuration and operational differences”. So even with the exceptional
calculations, I’d expect a sizable penalty from electric resistance water
heaters. As David pointed out, this penalty may be reduced by specifying low flow fixtures, and also <span style="color:black"><a href="http://energy.gov/energysaver/drain-water-heat-recovery"><font color="#0563c1">drain water heat
recovery</font></a></span><font face="Times New Roman" size="3">, so</font>lar DHW pre-heat, etc. The program in NJ has incentives up to $1.7/SF, which is hopefully enough to get developers interested in looking at measures that affect tenant bills.</font><p style="margin:0in 0in 8pt"><br></p></span><p style="margin:0in 0in 8pt"><span style="font-family:"calibri",sans-serif;font-size:11pt"><font color="#000000">Maria</font></span></p></div><font color="#000000" face="Times New Roman" size="3">

</font><div class="gmail_extra"><div><div class="gmail-m_-4668099752303710656gmail_signature"><div dir="ltr"><div><div dir="ltr"><p><b><span style="color:rgb(102,102,102);font-family:"verdana","sans-serif";font-size:11pt">Maria Karpman </span></b><span style="color:rgb(102,102,102);font-family:"verdana","sans-serif";font-size:11pt">LEED AP, BEMP, CEM</span><span style="color:rgb(31,73,125);font-family:"calibri","sans-serif";font-size:11pt"><u></u><u></u></span></p><p><span style="color:rgb(102,102,102);font-family:"verdana","sans-serif";font-size:11pt">________________</span><span style="color:rgb(31,73,125);font-family:"calibri","sans-serif";font-size:11pt"><u></u><u></u></span></p><p><span style="color:rgb(102,102,102);font-family:"verdana","sans-serif";font-size:11pt">Karpman Consulting<u></u><u></u></span></p><p><span style="color:rgb(102,102,102);font-family:"verdana","sans-serif";font-size:10pt"><a href="http://www.karpmanconsulting.net/" target="_blank"><font color="#1155cc">www.karpmanconsulting.net</font></a> </span><span style="color:rgb(31,73,125);font-family:"calibri","sans-serif";font-size:10pt"><u></u><u></u></span></p><p><span style="color:rgb(102,102,102);font-family:"verdana","sans-serif";font-size:7.5pt">Phone </span><span style="background:white;color:rgb(102,102,102);font-family:"helvetica","sans-serif";font-size:7.5pt"><a href="tel:860.430.1909" target="_blank" value="+18604301909"><font color="#1155cc">860.430.1909</font></a> </span><span style="color:rgb(31,73,125);font-family:"calibri","sans-serif";font-size:11pt"><u></u><u></u></span></p><p><span style="color:rgb(102,102,102);font-family:"arial","sans-serif";font-size:7.5pt">41C New London Turnpike</span><span style="color:rgb(31,73,125);font-family:"calibri","sans-serif";font-size:11pt"><u></u><u></u></span></p><p><span style="color:rgb(102,102,102);font-family:"arial","sans-serif";font-size:7.5pt">Glastonbury, CT 06033</span></p></div></div></div></div></div>
<br><div class="gmail_quote">On Fri, Dec 9, 2016 at 3:11 PM, Porter, Frederick         NOR via Bldg-sim <span dir="ltr"><<a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.<wbr>org</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;padding-left:1ex;border-left-color:rgb(204,204,204);border-left-width:1px;border-left-style:solid">





<div lang="EN-US">
<div class="gmail-m_-4668099752303710656m_1874221948657670253WordSection1">
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"calibri","sans-serif";font-size:11pt">Interesting! First, Sunayana, are you sure you should be using
<i>2013</i> App G/PRM? Even if the local energy code specifies ASHRAE 2013, LEED v4 uses ASHRAE 90.1-2010. And if utility programs are involved, there is usually some restriction on fuel switching. But that’s just bureaucratic detail.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"calibri","sans-serif";font-size:11pt"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"calibri","sans-serif";font-size:11pt">For the purposes of actually determining operating costs of
<i>realistic</i> alternative systems, it’s not clear the standard (or most BEM software) is addressing this adequately. In larger multi-unit buildings, it is probably
<i>not</i> practical to duplicate your proposed electric DHW system (in-unit, tank or instant), using gas, because all these heaters would require multiple flues, etc.  So a REAL alternative is a central DHW heater with recirculation.  That recirculation typically
 has considerable loop losses, which the PRM <i>seems</i> to have directed us to ignore. However if you read the text carefully, this restriction (G3.1.3.6) targets circulating fluids used for space conditioning.
<u></u><u></u></span></p>
<p class="MsoNormal" style="text-indent:0.5in"><span style="color:rgb(31,73,125);font-family:"calibri","sans-serif";font-size:11pt">(“G3.1.3.6 Piping Losses (<i>Systems 1, 5, 7, 8, and 11</i>). Piping losses shall not be modeled in either the proposed or baseline
 building designs for hot-water, chilled-water, or steam piping.”) <u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"calibri","sans-serif";font-size:11pt"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"calibri","sans-serif";font-size:11pt">However, the DHW language seems ambiguous on this point. In any case, central DHW loop losses are sometimes close to the actual DHW use energy. So the real
 cost penalty of gas vs. electric may not be as large as it appears from a simple ratio of utility cost/Btu. California’s T24 compliance software, though based on E+, has developed a much more rigorous approach to DHW calculations that at least considers piping
 losses in multi-family residential applications, along with researched draw profiles. The program passes off the DHW energy calculations to CSE (California Simulation Engine) for multi-family residential DHW.  Perhaps more accessible, a recent paper “Strategy
 Guideline: Proper Water Heater Selection” (<a href="http://www.nrel.gov/docs/fy15osti/63880.pdf" target="_blank">http://www.nrel.gov/docs/fy15<wbr>osti/63880.pdf</a>) includes a broken link to
</span><span style="font-size:11.5pt">MultiFamily_Central_DHW_Evalua<wbr>tionTool_v1.0.xlsx.
</span><span style="color:rgb(31,73,125);font-family:"calibri","sans-serif";font-size:11pt">You might try contacting the authors or Bldg America to see if you could get a copy. Output illustrated in the report is pasted below.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"calibri","sans-serif";font-size:11pt"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"calibri","sans-serif";font-size:11pt">If the project really can’t take the energy cost penalty caused by electric vs. gas DHW, and if the space heating uses HW boilers, there are systems that combine
 the DHW and HW piping; essentially the HW coils are supplied with potable water. This reduces the cost of piping and boilers in the building compared with separate DHW and HW. It does seem to penalize the efficiency of the heating side a bit, as the “HW” return
 temperature is often not as low as it would be for HW only. <u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"calibri","sans-serif";font-size:11pt"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"calibri","sans-serif";font-size:11pt">A related item for all to consider is that new gas tank type condensing DHW heaters are being rated at efficiencies of up to 99%. However, this is at a test
 condition which is rarely duplicated in reality (large flows of 60F inlet water). In any recirculating DHW system, the inlet T is usually much warmer, and in other cases, the draws are smaller and intermittent. Particularly the former reduces efficiency. That
 effect is considered in eQ and E+ models of HEATING condensing boilers, but not in the eQ DHW heater representation. So just plopping 1.01 into the “HIR” field of an eQ DHW heater is not realistic. (I’m not sure if E+ could be set up to represent this correctly
 or not.)<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"calibri","sans-serif";font-size:11pt"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"calibri","sans-serif";font-size:11pt">I think there is some fodder here for LEED CIRs, ASHRAE Interpretations, proposed changes to the PRM, or direct questions to a code official or utility program
 manager. In addition to the never-ending battle to have simulation software that provides reasonable representations of building components and operation!<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"calibri","sans-serif";font-size:11pt"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"calibri","sans-serif";font-size:11pt">Good Luck,<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"calibri","sans-serif";font-size:11pt">Fred<u></u><u></u></span></p>
<p class="MsoNormal"><b><span style="color:black;font-family:"calibri","sans-serif";font-size:11pt">Fred Porter, BEMP, LEED</span></b><b><span style="color:rgb(31,73,125);font-family:"calibri","sans-serif";font-size:11pt">©</span></b><b><span style="color:black;font-family:"calibri","sans-serif";font-size:11pt">
 AP<u></u><u></u></span></b></p>
<p class="MsoNormal" style="margin-bottom:2pt"><span style="color:rgb(127,127,127);font-family:"calibri","sans-serif";font-size:11pt">Principal Engineer<u></u><u></u></span></p>
<p class="MsoNormal" style="margin-bottom:2pt"><span style="color:rgb(127,127,127);font-family:"calibri","sans-serif";font-size:11pt">Sustainability Services<u></u><u></u></span></p>
<p class="MsoNormal"><b><span style="color:rgb(0,93,170);font-family:"calibri","sans-serif";font-size:11pt">NORESCO<u></u><u></u></span></b></p>
<p class="MsoNormal"><span style="color:rgb(128,127,131);font-family:"calibri","sans-serif";font-size:10pt"><a href="http://www.noresco.com/" target="_blank"><span style="color:blue">www.noresco.com</span></a></span><span style="color:rgb(128,127,131);font-family:"calibri","sans-serif";font-size:9pt"><u></u><u></u></span></p>
<p class="MsoNormal"><b><span style="color:rgb(127,127,127);font-family:"calibri","sans-serif";font-size:8pt"><u></u> <u></u></span></b></p>
<p class="MsoNormal"><img width="770" height="233" id="gmail-m_-4668099752303710656m_1874221948657670253Picture_x0020_1" src="cid:image002.jpg@01D2521D.BA6D4C20" border="0"><span style="color:rgb(31,73,125);font-family:"calibri","sans-serif";font-size:11pt"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"calibri","sans-serif";font-size:11pt"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"calibri","sans-serif";font-size:11pt"><u></u> <u></u></span></p>
<p class="MsoNormal"><b><span style="font-family:"tahoma","sans-serif";font-size:10pt">From:</span></b><span style="font-family:"tahoma","sans-serif";font-size:10pt"> Bldg-sim [mailto:<a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists<wbr>.onebuilding.org</a>]
<b>On Behalf Of </b>Sunayana Jain via Bldg-sim<br>
<b>Sent:</b> Friday, December 09, 2016 10:36 AM<br>
<b>To:</b> Angelica Walsh via Bldg-sim<br>
<b>Subject:</b> [External] [Bldg-sim] Multi-Family DHW<u></u><u></u></span></p>
<p class="MsoNormal"><u></u> <u></u></p>
<div>
<div>
<p class="MsoNormal">All,<u></u><u></u></p>
<p class="MsoNormal"> <u></u><u></u></p>
<p class="MsoNormal">We are working on an energy model of a high-rise multi-family building in the New Jersey climate zone. This project will be using high efficiency in-unit electric water heaters
 (0.95 EF) for DHW requirements.<u></u><u></u></p>
<p class="MsoNormal"> <u></u><u></u></p>
<p class="MsoNormal">As per the latest code (ASHRAE 90.1-2013 Appendix G), baseline DHW system for a multi-family building has to be a gas storage water heater. As I understand, there will be a significant
 energy cost penalty for using electric fuel versus natural gas in the design for DHW.<u></u><u></u></p>
<p class="MsoNormal"> <u></u><u></u></p>
<p class="MsoNormal">Has anyone encountered similar situation?<u></u><u></u></p>
<p class="MsoNormal"> <u></u><u></u></p>
<p class="MsoNormal">Thanks,<u></u><u></u></p>
<p class="MsoNormal"> <u></u><u></u></p>
<p class="MsoNormal"><b><span style="color:rgb(23,16,156)">Sunayana Jain CEM, LEED AP BD+C<br>
Sustainable Buildings & Operations Project Manager </span></b><u></u><u></u></p>
<p class="MsoNormal"><b><span style="color:rgb(79,98,40)">Sustainable Solutions Corporation</span></b><u></u><u></u></p>
</div>
<p class="MsoNormal"><br clear="all">
<u></u><u></u></p>
<div>
<div>
<div>
<div>
<div>
<p style="margin:0in 0in 0pt"><span style="font-family:"calibri","sans-serif";font-size:11pt"><u></u> <u></u></span></p>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>

<br>______________________________<wbr>_________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank" rel="noreferrer">http://lists.onebuilding.org/l<wbr>istinfo.cgi/bldg-sim-onebuildi<wbr>ng.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">BLDG-SIM-UNSUBSCRIBE@ONEBUILDI<wbr>NG.ORG</a><br>
<br></blockquote></div><br></div></div>