<html><head><meta http-equiv="content-type" content="text/html; charset=utf-8"></head><body dir="auto"><div>Same here, unless you have efficient fans, in which case you could call it a local exhaust, and use a baseline system fan power for that (can't remember the value)</div><div><br><br>Envoyé de mon iPhone</div><div><br>Le 3 nov. 2016 à 17:31, Jim Dirkes via Bldg-sim <<a href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a>> a écrit :<br><br></div><blockquote type="cite"><div>I vote for process load<br><br>On Thursday, November 3, 2016, Chris Jones via Bldg-sim <<a href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a>> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div lang="EN-US" link="blue" vlink="purple">
<div>
<p class="MsoNormal"><span style="color:#1f497d">I am working on a school model. The Food Classroom has a number of stoves with range hoods. These exhaust fans are hand on/off – not interlocked with the HVAC system. I estimate 2 hours a day operation.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">Would the fan power of these range hoods be included in the HVAC system fan power allowance? Or would you call it a process load – same in both proposed and baseline?<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">90.1-2007 App G. is the referenced standard.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<div>
<p class="MsoNormal"><b><span style="font-size:8.0pt;font-family:"Arial","sans-serif";color:#1f497d"><u></u> <u></u></span></b></p>
<p class="MsoNormal"><b><span style="font-size:8.0pt;font-family:"Arial","sans-serif";color:#1f497d">Christopher Jones, P. Eng.<u></u><u></u></span></b></p>
<p class="MsoNormal"><b><span style="font-size:8.0pt;font-family:"Arial","sans-serif";color:#1f497d">Rowan Williams Davies & Irwin Inc.</span></b><span style="font-size:8.0pt;font-family:"Arial","sans-serif";color:#1f497d"><br>
<i>Consulting Engineers & Scientists</i><br>
901 King Street West, Suite 400, Toronto, Ontario, M5V 3H5<br>
<b>T:</b> (519) 823-1311 ext 2052 <u></u><u></u></span></p>
<p class="MsoNormal"><b><span style="font-size:8.0pt;font-family:"Arial","sans-serif";color:#1f497d">M:</span></b><span style="font-size:8.0pt;font-family:"Arial","sans-serif";color:#1f497d"> (416) 697-0056
<u></u><u></u></span></p>
</div>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
</div>
<div style="font-size:7pt">
<hr>
RWDI - One of Canada's 50 Best Managed Companies - This communication is intended for the sole use of the party to whom it was addressed and may contain information that is privileged and/or confidential. Any other distribution, copying or disclosure is strictly
prohibited. If you received this email in error, please notify us immediately by replying to this email and delete the message without retaining any hard or electronic copies of same. Outgoing emails are scanned for viruses, but no warranty is made to their
absence in this email or attachments. If you require any information supplied by RWDI in a different format to facilitate accessibility, contact the sender of the email, email <a href="javascript:_e(%7B%7D,'cvml','solutions@rwdi.com');" target="_blank">solutions@rwdi.com</a> or call +1.519.823.1311.
<hr>
</div>
</div>
</blockquote><br><br>-- <br><div dir="ltr"><div><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><p><span style="font-size:10pt;font-family:Arial,sans-serif;color:black;background-image:initial;background-repeat:initial"></span></p>James V Dirkes II, PE, BEMP, LEED AP<br>CEO/President<br>The Building Performance Team Inc.<br>1631 Acacia Dr, GR, Mi 49504<br><br>Direct: 616.450.8653<br><a href="mailto:jim@buildingperformanceteam.com" target="_blank">jim@buildingperformanceteam.com</a><br><br><a href="http://buildingperformanceteam.com" target="_blank">Website </a>l <a href="https://www.linkedin.com/pub/jim-dirkes/7/444/413" target="_blank">LinkedIn</a> | <a href="http://buildingperformanceteam.com/bpt-insights-blog/item/73-modeled-performance-isn-t-actual-performance" target="_blank">May 2016 ASHRAE Journal article on energy modeling</a><p align="center" style="margin-bottom:0in;margin-bottom:.0001pt;text-align:center"><b><i><span style="font-size:14.0pt;line-height:115%;font-family:"MS Reference Sans Serif","sans-serif""> </span></i></b><span style="font-family:"MS Reference Sans Serif","sans-serif""></span></p><p style="vertical-align:middle">
</p><p style="margin-bottom:6.0pt;text-autospace:none"><span style="font-family:Calibri,sans-serif"><font size="4" color="#0000ff"></font></span></p><pre style="white-space:pre-wrap"><p style="margin-bottom:6.0pt;text-autospace:none"><span style="font-family:Calibri,sans-serif;font-size:10pt">…an open mind is not an end in itself </span><span style="font-family:Calibri,sans-serif;font-size:10pt">but rather is like an open mouth, designed to bite down on something solid and </span><span style="font-size:10pt;font-family:Calibri,sans-serif">nourishing</span><span style="font-family:arial,sans-serif;font-size:12.8px">.</span></p><p style="margin-bottom:6.0pt;text-autospace:none">
</p></pre></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div><br>
</div></blockquote><blockquote type="cite"><div><span>_______________________________________________</span><br><span>Bldg-sim mailing list</span><br><span><a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a></span><br><span>To unsubscribe from this mailing list send a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a></span><br></div></blockquote></body></html>