<div dir="ltr">Good point, should have included section 10 in the must-read list! Thanks!!</div><div class="gmail_extra"><br clear="all"><div><div class="gmail_signature"><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div dir="ltr"><div dir="ltr"><b>Elizabeth Gillmor <font size="1">PE, BEMP, LC, LEED AP</font></b><div><br></div><div><span style="font-size:large;background-color:rgb(255,255,255)"><b><font color="#38761d" face="arial, helvetica, sans-serif">e n e r g e t i c s </font></b></span><b><font color="#38761d" face="arial, helvetica, sans-serif" size="2">consulting engineers, llc</font></b></div><div><font size="2" style="background-color:rgb(255,255,255)" color="#666666"><a href="http://energetics-eng.com" target="_blank">energetics-eng.com</a> |</font><span style="color:rgb(102,102,102);font-size:small"> 303.619.0091</span></div></div></div></div></div></div></div></div></div></div></div></div></div></div>
<br><div class="gmail_quote">On Mon, May 2, 2016 at 12:34 PM, Jones, Christopher <span dir="ltr"><<a href="mailto:Christopher.r.Jones@wspgroup.com" target="_blank">Christopher.r.Jones@wspgroup.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div lang="EN-US" link="blue" vlink="purple">
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1f497d">Elizabeth,<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1f497d">Don’t neglect Section 10 – it also includes mandatory provisions for whole building metering – all fuels. Measurements are to be taken every 60 minutes and reported
hourly, daily, monthly, annually. The system shall be capable of storing the data for 36 months.
<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><img width="108" height="43" src="cid:image001.png@01D1A47F.F731E860" alt="cid:image003.png@01D09C46.E75BA0D0"></span><b><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1c467a"><u></u><u></u></span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1c467a">Christopher Jones,</span></b><b><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1f497d">
</span></b><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1f497d">P.Eng.<i>
<br>
</i></span><span lang="EN-CA" style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1f497d">Senior Engineer<b><u></u><u></u></b></span></p>
<p class="MsoNormal"><b><span lang="EN-CA" style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1f497d"><u></u> <u></u></span></b></p>
<p class="MsoNormal"><b><span lang="EN-CA" style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1f497d">WSP Canada Inc.<u></u><u></u></span></b></p>
<p class="MsoNormal"><span lang="EN-CA" style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1f497d">2300 Yonge Street, Suite 2300<u></u><u></u></span></p>
<p class="MsoNormal"><span lang="EN-CA" style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1f497d">Toronto, ON M4P 1E4</span><span lang="EN-CA" style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#595959"><br>
</span><span lang="EN-CA" style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1f497d">T <a href="tel:%2B1%20416-644-4226" value="+14166444226" target="_blank">+1 416-644-4226</a><u></u><u></u></span></p>
<p class="MsoNormal"><span lang="EN-CA" style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1f497d">F <a href="tel:%2B1%20416-487-9766" value="+14164879766" target="_blank">+1 416-487-9766</a><u></u><u></u></span></p>
<p class="MsoNormal"><span lang="EN-CA" style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1f497d">C <a href="tel:%2B1%20416-697-0056" value="+14166970056" target="_blank">+1 416-697-0056</a><u></u><u></u></span></p>
<p class="MsoNormal"><span lang="EN-CA" style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span lang="EN-CA" style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1f497d"><a href="http://www.wspgroup.com/" target="_blank">www.wspgroup.com</a>
</span><i><span lang="EN-CA" style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#565656"><u></u><u></u></span></i></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">From:</span></b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif""> Bldg-sim [mailto:<a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>Elizabeth Gillmor via Bldg-sim<br>
<b>Sent:</b> Monday, May 02, 2016 1:38 PM<br>
<b>To:</b> Duggin, Cory<br>
<b>Cc:</b> <a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Bldg-sim] 90.1-2013 vs 2015 IECC Performance Path Compliance<u></u><u></u></span></p>
<p class="MsoNormal"><u></u> <u></u></p>
<div>
<p class="MsoNormal">I just did a little seminar on this very topic for our Rocky Mountain ASHRAE tech conference last week. There are a few other key differences in 90.1:<u></u><u></u></p>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
<div>
<p class="MsoNormal">- Mandatory occupancy and daylighting controls in parking garages<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal">- Bi-level occ sensors required in stairwells<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal">- Slightly more stringent cooling efficiency requirements (full load and part load, also slightly lower economizer thresholds). Differences in heat pumps as well I believe.<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal">- More stringent envelope requirements (walls and windows). Also note limits to E/W glazing which may require that you rotate/average the baseline.<u></u><u></u></p>
</div>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal">Other important items to note:<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal">- A90.1 has MANDATORY electrical submetering requirements (separate monitoring for lighting, receptacles, and HVAC, plus some whole-building requirements) -- this is a biggie. Read section 8-Power thoroughly!<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal">- You CAN take credit for renewable energy (up to 5%)<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal">- A90.1 does not have the same commissioning requirements<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal">- A90.1 allows extra lighting credit for room geometry adjustments and some extra lighting controls (see control factor table), whereas IECC does not<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal">This is not a comprehensive list but those are the big ones that jump out. Whichever method you choose, make sure you are using the space-by-space method for lighting (it will almost always come out better than whole-building).<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal">Cheers,<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal">Elizabeth<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
</div>
<div>
<p class="MsoNormal"><br clear="all">
<u></u><u></u></p>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<p class="MsoNormal"><b>Elizabeth Gillmor </b><b><span style="font-size:7.5pt">PE, BEMP, LC, LEED AP</span></b><u></u><u></u></p>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal"><b><span style="font-size:18.0pt;font-family:"Arial","sans-serif";color:#38761d;background:white">e n e r g e t i c s </span></b><b><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#38761d">consulting engineers, llc</span></b><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;color:#666666;background:white"><a href="http://energetics-eng.com" target="_blank">energetics-eng.com</a> |</span><span style="color:#666666"> <a href="tel:303.619.0091" value="+13036190091" target="_blank">303.619.0091</a></span><u></u><u></u></p>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
<p class="MsoNormal"><u></u> <u></u></p>
<div>
<p class="MsoNormal">On Mon, May 2, 2016 at 11:08 AM, Duggin, Cory via Bldg-sim <<a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a>> wrote:<u></u><u></u></p>
<div>
<div>
<p class="MsoNormal">Does anyone have experience showing code compliance via the performance path in 90.1-2013 vs 2015 IECC? I have a project that isn’t meeting the 15% threshold against the 2015 IECC
standard reference design (per C401.2(3)). I have always thought the 15% was to level the compliance paths, but the main difference I am finding between the 2015 IECC SRD and 90.1-2013 budget building is the mandatory plug load control requirement. What
am I missing to account for the 15% difference?<u></u><u></u></p>
<p class="MsoNormal"> <u></u><u></u></p>
<p class="MsoNormal">Thanks,<u></u><u></u></p>
<p class="MsoNormal"> <u></u><u></u></p>
<p class="MsoNormal"><b>Cory Duggin, PE, LEED AP BD+C, BEMP</b><u></u><u></u></p>
<p class="MsoNormal"><i><span style="font-size:10.0pt">Principal/Energy Modeling Wizard</span></i><u></u><u></u></p>
<p class="MsoNormal"><b><span style="color:#006363">TLC Engineering for Architecture</span></b><u></u><u></u></p>
<p class="MsoNormal"><span style="font-size:10.0pt">6 Cadillac Drive, Suite 200</span><u></u><u></u></p>
<p class="MsoNormal"><span style="font-size:10.0pt">Brentwood, TN 37027-5080</span><u></u><u></u></p>
<p class="MsoNormal"><span style="font-size:10.0pt"> </span><u></u><u></u></p>
<table border="0" cellspacing="0" cellpadding="0">
<tbody>
<tr>
<td valign="bottom" style="padding:0in 0in 0in 0in">
<p class="MsoNormal" align="right" style="text-align:right">
<span style="font-size:9.0pt;color:#333333">direct: </span><u></u><u></u></p>
</td>
<td valign="bottom" style="padding:0in 0in 0in 0in">
<p class="MsoNormal"><span style="font-size:10.0pt"><a href="tel:615-346-1939" target="_blank">615-346-1939</a></span><u></u><u></u></p>
</td>
</tr>
<tr>
<td valign="bottom" style="padding:0in 0in 0in 0in">
<p class="MsoNormal" align="right" style="text-align:right">
<span style="font-size:9.0pt;color:#333333">website: </span><u></u><u></u></p>
</td>
<td valign="bottom" style="padding:0in 0in 0in 0in">
<p class="MsoNormal"><span style="font-size:10.0pt"><a href="http://www.tlc-engineers.com/" target="_blank">www.tlc-engineers.com</a></span><u></u><u></u></p>
</td>
</tr>
</tbody>
</table>
<p class="MsoNormal"> <u></u><u></u></p>
<p class="MsoNormal"> <u></u><u></u></p>
</div>
</div>
<p class="MsoNormal" style="margin-bottom:12.0pt"><br>
_______________________________________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">
BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><u></u><u></u></p>
</div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
</div>
<hr>
<div style="font-size:9pt;color:gray;font-family:Arial,sans-serif"><br>
You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment
<a href="http://www.wspgroup.com/casl" target="_blank">www.wspgroup.com/casl</a>. For any concern or if you believe you should not be receiving this message, please forward this message to us at
<a href="mailto:caslcompliance@wspgroup.com" target="_blank">caslcompliance@wspgroup.com</a> so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged,
confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying
or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.
<br>
<br>
</div>
</div>
</blockquote></div><br></div>