I actually helped to develop a method to model thermal bridges in
DOE-2 back in 1986 that has never been widely disseminated, although
I still find it the most practical way to model 2-D heat flows in
whole-building simulations.<br>
<br>
This method uses a two-dimensional finite-element program (WALFERFN)
that calculates one-dimensional equivalent response factors which
are written directly into the DOE-2 layers library (BDLLIB.DAT),
which can then be called by DOE-2 just like any other response
factor in the library.<br>
<br>
I've always used this technique in my residential modeling, with the
added benefit of not needing to input duplicate sets of wall layers
for the stud and non-stud portions, which measurably simplifies the
models and makes them easier to read. The last time I did
significant work on this subject was in 2000-2002, when I created
for the California Energy Commission a library of over 100 wall
layers with metal framing and thus considerable thermal<br>
bridging. I compared the wall assembly U-values to that calculated
by ORNL's Heating-7 program, and they were<br>
right on. Unfortunately, a few years after the project was
completed, the Commission decided to move to EnergyPlus as their
reference program, and so this work was effectively abandoned.<br>
<br>
For more information on this technique, i.e., creating 2-D response
factors, please see this report:<br>
<a class="moz-txt-link-freetext" href="http://www.whiteboxtechnologies.com/PAPERS/96_12_YJH_2Drespfacs_CEC_rpt.pdf">http://www.whiteboxtechnologies.com/PAPERS/96_12_YJH_2Drespfacs_CEC_rpt.pdf</a><br>
<br>
If there's anyone who's still running DOE-2 in batch, rather than
just the eQUEST interface, this procedure should be quite
understandable. Just e-mail me and I'll be happy to give you a copy
of the WALFERFN program and some sample input files. <br>
<br>
Joe <br>
<pre class="moz-signature" cols="72">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a class="moz-txt-link-freetext" href="http://weather.whiteboxtechnologies.com">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data
<a class="moz-txt-link-freetext" href="http://www.whiteboxtechnologies.com">http://www.whiteboxtechnologies.com</a>
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
<div class="moz-cite-prefix">On 1/28/2016 1:22 PM, Jim Dirkes wrote:<br>
</div>
<blockquote
cite="mid:CAFydjmSxPzhKYyti2-9CCu929=G58PkRVJ8UfNi7XvpJth-+FA@mail.gmail.com"
type="cite">
<div dir="ltr">
<div class="gmail_default"
style="font-family:tahoma,sans-serif;font-size:large;color:#b45f06">There
is also a landmark study by Morrison Hershfield in Canada
which I don't have access to at the moment that should provide
guidance.</div>
</div>
<div class="gmail_extra"><br>
<div class="gmail_quote">On Thu, Jan 28, 2016 at 4:11 PM, Marcus
Sheffer <span dir="ltr"><<a moz-do-not-send="true"
href="mailto:sheffer@sevengroup.com" target="_blank">sheffer@sevengroup.com</a>></span>
wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0
.8ex;border-left:1px #ccc solid;padding-left:1ex">Follow the
guidance in ASHRAE 90.1 Appendix A to determine the whole
assembly values.<br>
<br>
Marcus Sheffer<br>
7group<br>
<br>
-----Original Message-----<br>
From: Jones, Christopher [mailto:<a moz-do-not-send="true"
href="mailto:Christopher.r.Jones@wspgroup.com">Christopher.r.Jones@wspgroup.com</a>]<br>
Sent: Thursday, January 28, 2016 8:30 AM<br>
To: Luis Peréz-Lombard; <a moz-do-not-send="true"
href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a><br>
Subject: Re: [Bldg-sim] MODELLING THERMAL BRDIGES IN e-quest
or DOE2<br>
<br>
Hello Sir,<br>
eQuest does not have the capability to directly model
thermal bridges. The typical methodology is to calculate the
effective U-value of the insulation/thermal bridge layer
when building your layers for the construction. BC Hydro
has published significant research on building envelope
thermal bridging. See the lower portion of the webpage:<br>
<a moz-do-not-send="true"
href="https://www.bchydro.com/powersmart/business/programs/new-construction.html#thermal"
rel="noreferrer" target="_blank">https://www.bchydro.com/powersmart/business/programs/new-construction.html#thermal</a><br>
<br>
<br>
<br>
<br>
Christopher Jones, P.Eng.<br>
Senior Engineer<br>
<br>
WSP Canada Inc.<br>
2300 Yonge Street, Suite 2300<br>
Toronto, ON M4P 1E4<br>
T <a moz-do-not-send="true" href="tel:%2B1%20416-644-4226"
value="+14166444226">+1 416-644-4226</a><br>
F <a moz-do-not-send="true" href="tel:%2B1%20416-487-9766"
value="+14164879766">+1 416-487-9766</a><br>
C <a moz-do-not-send="true" href="tel:%2B1%20416-697-0056"
value="+14166970056">+1 416-697-0056</a><br>
<br>
<a moz-do-not-send="true" href="http://www.wspgroup.com"
rel="noreferrer" target="_blank">www.wspgroup.com</a><br>
<div>
<div class="h5"><br>
-----Original Message-----<br>
From: Bldg-sim [mailto:<a moz-do-not-send="true"
href="mailto:bldg-sim-bounces@lists.onebuilding.org">bldg-sim-bounces@lists.onebuilding.org</a>]
On Behalf Of Luis Peréz-Lombard<br>
Sent: Thursday, January 28, 2016 4:08 AM<br>
To: <a moz-do-not-send="true"
href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a><br>
Subject: [Bldg-sim] MODELLING THERMAL BRDIGES IN e-quest
or DOE2<br>
<br>
Dear building simulation colleagues,<br>
I would very much appreciate any insights or work around
to simulate envelope thermal bridges in e-quest.<br>
Sincerely,<br>
LPL<br>
-------------------------------------------------------------<br>
Luis Pérez-Lombard<br>
Dr. Ingeniero Industrial<br>
Profesor Contratado Doctor<br>
Departamento de Ingeniería Energética<br>
Escuela Superior de Ingenieros<br>
Universidad de Sevilla<br>
Camino de los Descubrimientos s/n<br>
41092 SEVILLA<br>
Tfno.: 95.448.72.56<br>
Fax: 95.446.31.53<br>
e-mail: <a moz-do-not-send="true"
href="mailto:lpl@us.es">lpl@us.es</a><br>
-------------------------------------------------------------<br>
<br>
_______________________________________________<br>
Bldg-sim mailing list<br>
<a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org"
rel="noreferrer" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank
message to <a moz-do-not-send="true"
href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
</div>
</div>
________________________________<br>
<br>
<br>
You are receiving this communication because you are listed
as a current WSP contact. Should you have any questions
regarding WSP’s electronic communications policy, please
consult our Anti-Spam Commitment <a moz-do-not-send="true"
href="http://www.wspgroup.com/casl" rel="noreferrer"
target="_blank">www.wspgroup.com/casl</a>. For any concern
or if you believe you should not be receiving this message,
please forward this message to us at <a
moz-do-not-send="true"
href="mailto:caslcompliance@wspgroup.com"><a class="moz-txt-link-abbreviated" href="mailto:caslcompliance@wspgroup.com">caslcompliance@wspgroup.com</a></a><mailto:<a
moz-do-not-send="true"
href="mailto:caslcompliance@wspgroup.com"><a class="moz-txt-link-abbreviated" href="mailto:caslcompliance@wspgroup.com">caslcompliance@wspgroup.com</a></a>>
so that we can promptly address your request. This message
is intended only for the use of the individual or entity to
which it is addressed, and may contain information which is
privileged, confidential, proprietary or exempt from
disclosure under applicable law. If you are not the intended
recipient or the person responsible for delivering the
message to the intended recipient, you are strictly
prohibited from disclosing, distributing, copying or in any
way using this message. If you have received this
communication in error, please notify the sender, and
destroy and delete any copies you may have received.<br>
<br>
WSP provides professional land surveying services through
the following entities: WSP Surveys (AB) Limited Partnership
and WSP Surveys (BC) Limited Partnership<br>
<div class="HOEnZb">
<div class="h5"><br>
_______________________________________________<br>
Bldg-sim mailing list<br>
<a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org"
rel="noreferrer" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank
message to <a moz-do-not-send="true"
href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
</div>
</div>
</blockquote>
</div>
<br>
<br clear="all">
<div><br>
</div>
-- <br>
<div class="gmail_signature">
<div dir="ltr">
<div>
<div dir="ltr">
<div>
<div dir="ltr">
<div>
<div dir="ltr">
<div>
<div dir="ltr">
<div>
<div dir="ltr">
<div>
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<p><span
style="font-size:10pt;font-family:Arial,sans-serif;color:black;background-image:initial;background-repeat:initial"></span></p>
James V Dirkes
II, PE, BEMP,
LEED AP<br>
CEO/President<br>
The Building
Performance
Team Inc.<br>
1631 Acacia
Dr, GR, Mi
49504<br>
<br>
Direct:
616.450.8653<br>
<a
moz-do-not-send="true"
href="mailto:jim@buildingperformanceteam.com" target="_blank"><a class="moz-txt-link-abbreviated" href="mailto:jim@buildingperformanceteam.com">jim@buildingperformanceteam.com</a></a><br>
<br>
<a
moz-do-not-send="true"
href="http://buildingperformanceteamcom" target="_blank">Website </a>l
<a
moz-do-not-send="true"
href="https://www.linkedin.com/pub/jim-dirkes/7/444/413" target="_blank">LinkedIn</a>
<p
style="margin-bottom:0in;margin-bottom:.0001pt;text-align:center"
align="center"><b><i><span
style="font-size:14.0pt;line-height:115%;font-family:"MS
Reference Sans
Serif","sans-serif""> </span></i></b><span
style="font-family:"MS
Reference Sans
Serif","sans-serif""></span></p>
<p
style="vertical-align:middle">
</p>
<p
style="margin-bottom:6.0pt;text-autospace:none"><span
style="font-family:Calibri,sans-serif"><font size="4">Fail
faster!</font></span><br>
</p>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
Bldg-sim mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a class="moz-txt-link-abbreviated" href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
</blockquote>
<br>
</body>
</html>