Christopher, <br>
<br>
I took a brief scroll through the link that you provided, and yes,
there's a lot of information there. I haven't yet found a technical
description of the methodology, but I did get to the tables with
pretty colored pictures of wall sections and their computed
U-values. I hope there's more information on the dynamic
characteristics of these wall sections, i.e., thermal mass,
diffusivity, etc., since those would be needed to model them
correctly in a simulation program. <br>
<br>
In terms of comparing the methodologies, as you've suggested, one
place to start would be simply comparing the steady-state U-values
derived for the same wall constructions. I've done some digging on
my end and found an old 1997 User News newsletter with a brief
description of the 2-D response factor work I did with Fred
Winkelmann and Vladimir Bazjanac and a table listing the R-values
for the 76 steel-frame wall sections modeled. Since the whole
newsletter is only 657K, I've attached it with this e-mail. The
newsletter is interesting in other ways, as well, including the
announcement of the 5th IBPSA conference to be held in the Czech
Republic :-) .<br>
<br>
Joe<br>
<br>
<pre class="moz-signature" cols="72">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a class="moz-txt-link-freetext" href="http://weather.whiteboxtechnologies.com">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data
<a class="moz-txt-link-freetext" href="http://www.whiteboxtechnologies.com">http://www.whiteboxtechnologies.com</a>
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
<div class="moz-cite-prefix">On 1/29/2016 5:18 AM, Jones,
Christopher wrote:<br>
</div>
<blockquote
cite="mid:25F861E695EA99478F9790869A57C7D4A8B0635F@catormsx02"
type="cite">
<meta http-equiv="Content-Type" content="text/html; charset=utf-8">
<meta name="Generator" content="Microsoft Word 14 (filtered
medium)">
<!--[if !mso]><style>v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style><![endif]-->
<style><!--
/* Font Definitions */
@font-face
{font-family:Calibri;
panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
{font-family:Tahoma;
panose-1:2 11 6 4 3 5 4 4 2 4;}
@font-face
{font-family:Consolas;
panose-1:2 11 6 9 2 2 4 3 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{margin:0in;
margin-bottom:.0001pt;
font-size:12.0pt;
font-family:"Times New Roman","serif";
color:black;}
a:link, span.MsoHyperlink
{mso-style-priority:99;
color:blue;
text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
{mso-style-priority:99;
color:purple;
text-decoration:underline;}
p
{mso-style-priority:99;
mso-margin-top-alt:auto;
margin-right:0in;
mso-margin-bottom-alt:auto;
margin-left:0in;
font-size:12.0pt;
font-family:"Times New Roman","serif";
color:black;}
pre
{mso-style-priority:99;
mso-style-link:"HTML Preformatted Char";
margin:0in;
margin-bottom:.0001pt;
font-size:10.0pt;
font-family:"Courier New";
color:black;}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
{mso-style-priority:99;
mso-style-link:"Balloon Text Char";
margin:0in;
margin-bottom:.0001pt;
font-size:8.0pt;
font-family:"Tahoma","sans-serif";
color:black;}
span.HTMLPreformattedChar
{mso-style-name:"HTML Preformatted Char";
mso-style-priority:99;
mso-style-link:"HTML Preformatted";
font-family:Consolas;
color:black;}
span.EmailStyle20
{mso-style-type:personal-reply;
font-family:"Arial","sans-serif";
color:#1F497D;}
span.BalloonTextChar
{mso-style-name:"Balloon Text Char";
mso-style-priority:99;
mso-style-link:"Balloon Text";
font-family:"Tahoma","sans-serif";
color:black;}
.MsoChpDefault
{mso-style-type:export-only;
font-size:10.0pt;}
@page WordSection1
{size:8.5in 11.0in;
margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
{page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
<div class="WordSection1">
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1F497D">Joe,<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1F497D">It
would be very interesting to compare the methodologies in
your paper with the results of the Morrison Herschfield
research. BC Hydro published that detailed research. <o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<div>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><a
moz-do-not-send="true"
href="https://www.bchydro.com/powersmart/business/programs/new-construction.html?WT.mc_id=rd_thermalguide#thermal"><a class="moz-txt-link-freetext" href="https://www.bchydro.com/powersmart/business/programs/new-construction.html?WT.mc_id=rd_thermalguide#thermal">https://www.bchydro.com/powersmart/business/programs/new-construction.html?WT.mc_id=rd_thermalguide#thermal</a></a><o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><img
id="Picture_x0020_2"
src="cid:part2.05040506.07020407@whiteboxtechnologies.com"
alt="cid:image003.png@01D09C46.E75BA0D0" border="0"
height="43" width="108"></span><b><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1C467A"><o:p></o:p></span></b></p>
<p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1C467A">Christopher
Jones,</span></b><b><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1F497D"></span></b><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1F497D">P.Eng.<i>
<br>
</i></span><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1F497D"
lang="EN-CA">Senior Engineer<b><o:p></o:p></b></span></p>
<p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1F497D"
lang="EN-CA"><o:p> </o:p></span></b></p>
<p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1F497D"
lang="EN-CA">WSP Canada Inc.<o:p></o:p></span></b></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1F497D"
lang="EN-CA">2300 Yonge Street, Suite 2300<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1F497D"
lang="EN-CA">Toronto, ON M4P 1E4</span><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#595959"
lang="EN-CA"><br>
</span><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1F497D"
lang="EN-CA">T +1 416-644-4226<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1F497D"
lang="EN-CA">F +1 416-487-9766<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1F497D"
lang="EN-CA">C +1 416-697-0056<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1F497D"
lang="EN-CA"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1F497D"
lang="EN-CA"><a moz-do-not-send="true"
href="http://www.wspgroup.com/">www.wspgroup.com</a>
</span><i><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#565656"
lang="EN-CA"><o:p></o:p></span></i></p>
</div>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<div>
<div style="border:none;border-top:solid #B5C4DF
1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext">From:</span></b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext">
Bldg-sim [<a class="moz-txt-link-freetext" href="mailto:bldg-sim-bounces@lists.onebuilding.org">mailto:bldg-sim-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>Joe Huang<br>
<b>Sent:</b> Friday, January 29, 2016 5:44 AM<br>
<b>To:</b> <a class="moz-txt-link-abbreviated" href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Bldg-sim] MODELLING THERMAL BRDIGES
IN e-quest or DOE2 (minor correction on dates).<o:p></o:p></span></p>
</div>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">The work I did for the CEC was done in 1996
(as indicated in the report title), not 2000-2002, which was a
follow-on effort to do 2-D foundation heat flows.<br>
<br>
Joe<br>
<br>
<o:p></o:p></p>
<pre>Joe Huang <o:p></o:p></pre>
<pre>White Box Technologies, Inc.<o:p></o:p></pre>
<pre>346 Rheem Blvd., Suite 205A<o:p></o:p></pre>
<pre>Moraga CA 94556<o:p></o:p></pre>
<pre><a moz-do-not-send="true" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a><o:p></o:p></pre>
<pre><a moz-do-not-send="true" href="http://weather.whiteboxtechnologies.com">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data<o:p></o:p></pre>
<pre><a moz-do-not-send="true" href="http://www.whiteboxtechnologies.com">http://www.whiteboxtechnologies.com</a><o:p></o:p></pre>
<pre>(o) (925)388-0265<o:p></o:p></pre>
<pre>(c) (510)928-2683<o:p></o:p></pre>
<pre>"building energy simulations at your fingertips"<o:p></o:p></pre>
<div>
<p class="MsoNormal">On 1/29/2016 2:41 AM, Joe Huang wrote:<o:p></o:p></p>
</div>
<blockquote style="margin-top:5.0pt;margin-bottom:5.0pt">
<p class="MsoNormal">I actually helped to develop a method to
model thermal bridges in DOE-2 back in 1986 that has never
been widely disseminated, although I still find it the most
practical way to model 2-D heat flows in whole-building
simulations.<br>
<br>
This method uses a two-dimensional finite-element program
(WALFERFN) that calculates one-dimensional equivalent
response factors which are written directly into the DOE-2
layers library (BDLLIB.DAT), which can then be called by
DOE-2 just like any other response factor in the library.<br>
<br>
I've always used this technique in my residential modeling,
with the added benefit of not needing to input duplicate
sets of wall layers for the stud and non-stud portions,
which measurably simplifies the models and makes them
easier to read. The last time I did significant work on
this subject was in 2000-2002, when I created for the
California Energy Commission a library of over 100 wall
layers with metal framing and thus considerable thermal
bridging. I compared the wall assembly U-values to that
calculated by ORNL's Heating-7 program, and they were right
on. Unfortunately, a few years after the project was
completed, the Commission decided to move to EnergyPlus as
their reference program, and so this work was effectively
abandoned.<br>
<br>
For more information on this technique, i.e., creating 2-D
response factors, please see this report:<br>
<a moz-do-not-send="true"
href="http://www.whiteboxtechnologies.com/PAPERS/96_12_YJH_2Drespfacs_CEC_rpt.pdf">http://www.whiteboxtechnologies.com/PAPERS/96_12_YJH_2Drespfacs_CEC_rpt.pdf</a><br>
<br>
If there's anyone who's still running DOE-2 in batch, rather
than just the eQUEST interface, this procedure should be
quite understandable. Just e-mail me and I'll be happy to
give you a copy of the WALFERFN program and some sample
input files.
<br>
<br>
Joe <br>
<br>
<o:p></o:p></p>
<pre>Joe Huang <o:p></o:p></pre>
<pre>White Box Technologies, Inc.<o:p></o:p></pre>
<pre>346 Rheem Blvd., Suite 205A<o:p></o:p></pre>
<pre>Moraga CA 94556<o:p></o:p></pre>
<pre><a moz-do-not-send="true" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a><o:p></o:p></pre>
<pre><a moz-do-not-send="true" href="http://weather.whiteboxtechnologies.com">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data<o:p></o:p></pre>
<pre><a moz-do-not-send="true" href="http://www.whiteboxtechnologies.com">http://www.whiteboxtechnologies.com</a><o:p></o:p></pre>
<pre>(o) (925)388-0265<o:p></o:p></pre>
<pre>(c) (510)928-2683<o:p></o:p></pre>
<pre>"building energy simulations at your fingertips"<o:p></o:p></pre>
<div>
<p class="MsoNormal">On 1/28/2016 1:22 PM, Jim Dirkes wrote:<o:p></o:p></p>
</div>
<blockquote style="margin-top:5.0pt;margin-bottom:5.0pt">
<div>
<div>
<p class="MsoNormal">There is also a landmark study by
Morrison Hershfield in Canada which I don't have
access to at the moment that should provide guidance.<o:p></o:p></p>
</div>
</div>
<div>
<p class="MsoNormal"><o:p> </o:p></p>
<div>
<p class="MsoNormal">On Thu, Jan 28, 2016 at 4:11 PM,
Marcus Sheffer <<a moz-do-not-send="true"
href="mailto:sheffer@sevengroup.com">sheffer@sevengroup.com</a>>
wrote:<o:p></o:p></p>
<p class="MsoNormal">Follow the guidance in ASHRAE 90.1
Appendix A to determine the whole assembly values.<br>
<br>
Marcus Sheffer<br>
7group<br>
<br>
-----Original Message-----<br>
From: Jones, Christopher [mailto:<a
moz-do-not-send="true"
href="mailto:Christopher.r.Jones@wspgroup.com"><a class="moz-txt-link-abbreviated" href="mailto:Christopher.r.Jones@wspgroup.com">Christopher.r.Jones@wspgroup.com</a></a>]<br>
Sent: Thursday, January 28, 2016 8:30 AM<br>
To: Luis Peréz-Lombard; <a moz-do-not-send="true"
href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a><br>
Subject: Re: [Bldg-sim] MODELLING THERMAL BRDIGES IN
e-quest or DOE2<br>
<br>
Hello Sir,<br>
eQuest does not have the capability to directly model
thermal bridges. The typical methodology is to
calculate the effective U-value of the
insulation/thermal bridge layer when building your
layers for the construction. BC Hydro has published
significant research on building envelope thermal
bridging. See the lower portion of the webpage:<br>
<a moz-do-not-send="true"
href="https://www.bchydro.com/powersmart/business/programs/new-construction.html#thermal"
target="_blank">https://www.bchydro.com/powersmart/business/programs/new-construction.html#thermal</a><br>
<br>
<br>
<br>
<br>
Christopher Jones, P.Eng.<br>
Senior Engineer<br>
<br>
WSP Canada Inc.<br>
2300 Yonge Street, Suite 2300<br>
Toronto, ON M4P 1E4<br>
T <a moz-do-not-send="true"
href="tel:%2B1%20416-644-4226">+1 416-644-4226</a><br>
F <a moz-do-not-send="true"
href="tel:%2B1%20416-487-9766">+1 416-487-9766</a><br>
C <a moz-do-not-send="true"
href="tel:%2B1%20416-697-0056">+1 416-697-0056</a><br>
<br>
<a moz-do-not-send="true"
href="http://www.wspgroup.com" target="_blank">www.wspgroup.com</a><o:p></o:p></p>
<div>
<div>
<p class="MsoNormal"><br>
-----Original Message-----<br>
From: Bldg-sim [mailto:<a moz-do-not-send="true"
href="mailto:bldg-sim-bounces@lists.onebuilding.org">bldg-sim-bounces@lists.onebuilding.org</a>]
On Behalf Of Luis Peréz-Lombard<br>
Sent: Thursday, January 28, 2016 4:08 AM<br>
To: <a moz-do-not-send="true"
href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a><br>
Subject: [Bldg-sim] MODELLING THERMAL BRDIGES IN
e-quest or DOE2<br>
<br>
Dear building simulation colleagues,<br>
I would very much appreciate any insights or work
around to simulate envelope thermal bridges in
e-quest.<br>
Sincerely,<br>
LPL<br>
-------------------------------------------------------------<br>
Luis Pérez-Lombard<br>
Dr. Ingeniero Industrial<br>
Profesor Contratado Doctor<br>
Departamento de Ingeniería Energética<br>
Escuela Superior de Ingenieros<br>
Universidad de Sevilla<br>
Camino de los Descubrimientos s/n<br>
41092 SEVILLA<br>
Tfno.: 95.448.72.56<br>
Fax: 95.446.31.53<br>
e-mail: <a moz-do-not-send="true"
href="mailto:lpl@us.es">lpl@us.es</a><br>
-------------------------------------------------------------<br>
<br>
_______________________________________________<br>
Bldg-sim mailing list<br>
<a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org"
target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send a
blank message to <a moz-do-not-send="true"
href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">
BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><o:p></o:p></p>
</div>
</div>
<p class="MsoNormal">________________________________<br>
<br>
<br>
You are receiving this communication because you are
listed as a current WSP contact. Should you have any
questions regarding WSP’s electronic communications
policy, please consult our Anti-Spam Commitment
<a moz-do-not-send="true"
href="http://www.wspgroup.com/casl">www.wspgroup.com/casl</a>.
For any concern or if you believe you should not be
receiving this message, please forward this message to
us at
<a moz-do-not-send="true"
href="mailto:caslcompliance@wspgroup.com">caslcompliance@wspgroup.com</a><mailto:<a
moz-do-not-send="true"
href="mailto:caslcompliance@wspgroup.com"><a class="moz-txt-link-abbreviated" href="mailto:caslcompliance@wspgroup.com">caslcompliance@wspgroup.com</a></a>>
so that we can promptly address your request. This
message is intended only for the use of the individual
or entity to which it is addressed, and may contain
information which is privileged, confidential,
proprietary or exempt from disclosure under applicable
law. If you are not the intended recipient or the
person responsible for delivering the message to the
intended recipient, you are strictly prohibited from
disclosing, distributing, copying or in any way using
this message. If you have received this communication
in error, please notify the sender, and destroy and
delete any copies you may have received.<br>
<br>
WSP provides professional land surveying services
through the following entities: WSP Surveys (AB)
Limited Partnership and WSP Surveys (BC) Limited
Partnership<o:p></o:p></p>
<div>
<div>
<p class="MsoNormal"><br>
_______________________________________________<br>
Bldg-sim mailing list<br>
<a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org"
target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send a
blank message to <a moz-do-not-send="true"
href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">
BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><o:p></o:p></p>
</div>
</div>
</div>
<p class="MsoNormal" style="margin-bottom:12.0pt"><o:p> </o:p></p>
<div>
<p class="MsoNormal"><o:p> </o:p></p>
</div>
<p class="MsoNormal">-- <o:p></o:p></p>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<p
class="MsoNormal">James
V Dirkes II,
PE, BEMP, LEED
AP<br>
CEO/President<br>
The Building
Performance
Team Inc.<br>
1631 Acacia
Dr, GR, Mi
49504<br>
<br>
Direct:
616.450.8653<br>
<a
moz-do-not-send="true"
href="mailto:jim@buildingperformanceteam.com"><a class="moz-txt-link-abbreviated" href="mailto:jim@buildingperformanceteam.com">jim@buildingperformanceteam.com</a></a><br>
<br>
<a
moz-do-not-send="true"
href="http://buildingperformanceteamcom" target="_blank">Website </a>l
<a
moz-do-not-send="true"
href="https://www.linkedin.com/pub/jim-dirkes/7/444/413" target="_blank">LinkedIn</a>
<o:p></o:p></p>
<p>Fail
faster!<o:p></o:p></p>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
<p class="MsoNormal"><br>
<br>
<br>
<o:p></o:p></p>
<pre>_______________________________________________<o:p></o:p></pre>
<pre>Bldg-sim mailing list<o:p></o:p></pre>
<pre><a moz-do-not-send="true" href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><o:p></o:p></pre>
<pre>To unsubscribe from this mailing list send a blank message to <a moz-do-not-send="true" href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><o:p></o:p></pre>
</blockquote>
<p class="MsoNormal"><o:p> </o:p></p>
</blockquote>
<p class="MsoNormal"><o:p> </o:p></p>
</div>
<hr>
<div style="font-size:9pt; color:gray; font-family:Arial,
sans-serif;"><br>
You are receiving this communication because you are listed as a
current WSP contact. Should you have any questions regarding
WSP’s electronic communications policy, please consult our
Anti-Spam Commitment
<a moz-do-not-send="true" href="www.wspgroup.com/casl">www.wspgroup.com/casl</a>.
For any concern or if you believe you should not be receiving
this message, please forward this message to us at
<a moz-do-not-send="true"
href="mailto:caslcompliance@wspgroup.com">caslcompliance@wspgroup.com</a>
so that we can promptly address your request. This message is
intended only for the use of the individual or entity to which
it is addressed, and may contain information which is
privileged, confidential, proprietary or exempt from disclosure
under applicable law. If you are not the intended recipient or
the person responsible for delivering the message to the
intended recipient, you are strictly prohibited from disclosing,
distributing, copying or in any way using this message. If you
have received this communication in error, please notify the
sender, and destroy and delete any copies you may have received.
<br>
<br>
WSP provides professional land surveying services through the
following entities: WSP Surveys (AB) Limited Partnership and WSP
Surveys (BC) Limited Partnership
</div>
</blockquote>
<br>
</body>
</html>