<p>Joe,</p>
<p><br>
</p>
<p>In addition to what you noted, RP-1404 does show the user how the utility bills could be transformed to the hourly time scale, regressed, and used for hourly prediction for the whole year (or any shorter time frame). This is shown in the final report with
a lot of success (acceptable levels of uncertainty) to predict whole building electric use, and also thermal loads (hot water, and chilled water).</p>
<p><br>
</p>
<p>Thanks.</p>
<p><br>
</p>
<p>Bass</p>
<br>
<br>
<div style="color: rgb(0, 0, 0);">
<hr tabindex="-1" style="display:inline-block; width:98%">
<div id="divRplyFwdMsg" dir="ltr"><font face="Calibri, sans-serif" color="#000000" style="font-size:11pt"><b>From:</b> Bldg-sim <bldg-sim-bounces@lists.onebuilding.org> on behalf of Joe Huang <yjhuang@whiteboxtechnologies.com><br>
<b>Sent:</b> Sunday, August 30, 2015 11:33 PM<br>
<b>To:</b> bldg-sim@lists.onebuilding.org<br>
<b>Subject:</b> Re: [Bldg-sim] deriving shorter timestep data from monthly or annual</font>
<div> </div>
</div>
<div>Jeff, Chris, <br>
<br>
I don't think RP-1404 sounds the same as what Chris is after. In RP-1404, the goal is to find the shortest monitoring period, e.g., 2 weeks, from which long-term annual performance can be reliably extrapolated. From Chris' post, I get the feeling that he
was interested in ways to take utility bills and somehow disaggregate them by end use and shorter time periods (daily or even hourly).
<br>
<br>
If all you're working with is monthly gas utility bills, I can't think of any other way than to regress them against variable-base degree days ala' the Princeton Scorekeeping Method (PRISM). Use the base temperature with the best R2. Then, take the average
of the gas consumption for those months with no degree days as the non-weather-related gas consumption. The regression slope then allows you to apportion the weather-related gas consumption by day.
<br>
<br>
All this assumes that both the base load and the heating load/degree-day are constant, which may be rather dubious, especially for something like a stadium.
<br>
<br>
That's all for my two-cents.<br>
<br>
Joe<br>
<br>
<br>
<pre class="moz-signature" cols="72">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a class="moz-txt-link-freetext" href="http://weather.whiteboxtechnologies.com">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data
<a class="moz-txt-link-freetext" href="http://www.whiteboxtechnologies.com">http://www.whiteboxtechnologies.com</a>
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
<div class="moz-cite-prefix">On 8/27/2015 1:17 PM, Jeff Haberl wrote:<br>
</div>
<blockquote type="cite">
<div style="direction:ltr; font-family:Tahoma; color:#000000; font-size:10pt">
<p class="MsoBodyText3" style="margin:0in 0in 0pt"><span style="text-decoration:none">Hello Chris,
</span></p>
<p class="MsoBodyText3" style="margin:0in 0in 0pt"><span style="text-decoration:none"></span> </p>
<p class="MsoBodyText3" style="margin:0in 0in 0pt"><span style="text-decoration:none">I think the definitive work on this was done as part of ASHRAE Research project 1404 by Bass Abushakra and Agami Reddy...(see below).</span></p>
<p class="MsoBodyText3" style="margin:0in 0in 0pt"><span style="text-decoration:none"></span> </p>
<p class="MsoBodyText3" style="margin:0in 0in 0pt"><span style="text-decoration:none">Jeff</span></p>
<p class="MsoNormal" style="text-align:justify"><b style=""><u><span style=""></span></u></b> </p>
<p class="MsoNormal" style="text-align:justify"><b style=""><u><span style="">1404-RP
</span></u></b></p>
<p class="MsoNormal" style="text-align:justify; margin:0in 0in
0pt"><b style=""><span style="">Measurement, Modeling, Analysis and Reporting Protocols for Short-term M&V of Whole Building Energy Performance</span></b><span style=""></span></p>
<p class="Document1" style="page-break-after:auto; margin:0in
0in 0pt">
<span style=""> </span></p>
<p class="Document1" style="page-break-after:auto; margin:0in
0in 0pt">
<span style="">Completed January 2014</span></p>
<p class="MsoNormal" style="text-align:justify"><span style="font-size:10pt; font-family:"Times New Roman","serif"">Milwaukee School of Engineering</span></p>
<p class="MsoNormal" style="text-align:justify"><span style="font-size:10pt; font-family:"Times New Roman","serif"">Principal Investigator, Bass Abushakra</span></p>
<p class="MsoNormal" style="text-align:justify"><span style="font-size:10pt; font-family:"Times New Roman","serif"">TC 4.7, Energy Calculations</span></p>
<p class="MsoNormal" style="text-align:justify"><span style="font-size:10pt; font-family:"Times New Roman","serif""> </span></p>
<p class="MsoNormal" style="text-align:justify; margin:0in 0in
0pt; text-autospace:">
<span style="">The objective of this research is to develop a new method to determine the shortest time period for energy use monitoring involving hourly (or sub-hourly) data that will yield reliable and accurate long term energy use estimates within acceptable
uncertainty limits. By evaluating the uncertainty in the measured data as the monitoring period progresses, the new method will allow users to evaluate the energy performance and calculate energy savings in commercial and institutional buildings, in a cost-effective
short-term monitoring period instead of the current year-long monitoring stipulated in most M&V protocols. The new approach would resolve the problem of needing long-term monitored data, which is often very costly to obtain and/or historically unavailable.
In addition, this measurement/extrapolation approach should be designed as simply as possible to meet the uncertainty targets in energy savings stipulated in M&V protocols such as ASHRAE Guideline 14.</span></p>
<p class="MsoNormal" style="text-align:justify; margin:0in 0in
0pt"> </p>
<div>
<div style="font-size:13px; font-family:Tahoma">
<div> </div>
<div><font size="2" color="#0000ff" face="Tahoma">8=! 8=) :=) 8=) ;=) 8=) 8=( 8=) 8=() 8=) 8=| 8=) :=') 8=) 8=?<br>
Jeff S. Haberl, Ph.D.,P.E.inactive,FASHRAE,FIBPSA,......<a href="mailto:........jhaberl@tamu.edu"></a><a class="moz-txt-link-abbreviated" href="mailto:jhaberl@tamu.edu">jhaberl@tamu.edu</a><br>
Professor........................................................................Office Ph: 979-845-6507<br>
Department of Architecture............................................Lab Ph:979-845-6065<br>
Energy Systems Laboratory...........................................FAX: 979-862-2457<br>
Texas A&M University...................................................77843-3581<br>
College Station, Texas, USA, 77843.............................http://esl.tamu.edu<br>
8=/ 8=) :=) 8=) ;=) 8=) 8=() 8=) :=) 8=) 8=! 8=) 8=? 8=) </font><font size="2" color="#0000ff" face="Tahoma">8=0<br>
</font></div>
<font size="2" color="#0000ff" face="Tahoma"></font></div>
</div>
<div style="font-size:16px; font-family:Times New Roman; color:#000000">
<hr tabindex="-1">
<div id="divRpF274620" style="direction:ltr"><font size="2" color="#000000" face="Tahoma"><b>From:</b> Bldg-sim [<a class="moz-txt-link-abbreviated" href="mailto:bldg-sim-bounces@lists.onebuilding.org">bldg-sim-bounces@lists.onebuilding.org</a>] on behalf of
Chris Yates [<a class="moz-txt-link-abbreviated" href="mailto:chris.malcolm.yates@gmail.com">chris.malcolm.yates@gmail.com</a>]<br>
<b>Sent:</b> Thursday, August 27, 2015 2:44 PM<br>
<b>To:</b> <a class="moz-txt-link-abbreviated" href="mailto:bldg-sim@lists.onebuilding.org">
bldg-sim@lists.onebuilding.org</a><br>
<b>Subject:</b> [Bldg-sim] deriving shorter timestep data from monthly or annual<br>
</font><br>
</div>
<div>Dear all,<br>
<br>
I have monthly gas data for a soccer stadium and I'm trying to develop it toward daily (or even hourly) data so this can be used in subsequent assessments.<br>
<br>
My own efforts on previous assessments have extended to relatively crude application of multipliers (possibly based on a simulation study) and an overall divisor. This is very limited, especially in this case.<br>
<br>
In an ideal world, it would be helpful to develop the daily consumption weighted with the following factors:<br>
<ul>
<li>Parasitic losses - these can be estimated from when the facility is largely closed during the off season
</li><li>Historic game fixtures - readily available from the web </li><li>Weather, including about 1MW of underpitch heating </li></ul>
<p>I'm surrendered to the possibility that this is well beyond me! But, can anybody suggest excel functions or other software tools they may have used, or even what math for me to look up on Google?
<br>
</p>
<p>Many thanks <br>
</p>
<p>Chris<br>
</p>
</div>
</div>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset> <br>
<pre>_______________________________________________
Bldg-sim mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a class="moz-txt-link-abbreviated" href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
</blockquote>
<br>
</div>
</div>
</div>
</body>
</html>