<p>Hello Joe,</p>
<p> </p>
<p>Yes, you can count the degree days and regress against that to show a correlation. However, one will get a better "fit" to the weather data if you regress to the degree day that is calculated for the balance point temperature of the building -- hence the
inverse model toolkit or the variable based degree day method.</p>
<p> </p>
<p>PRISM actually calculates the degree days to a variety of change points and actually provides a table for each location that you use as a look up. The IMT will actually perform a variable based degree day calculation that agrees well with PRISM. IMT will
also provide you with the average daily temperature for the billing period.</p>
<p> </p>
<p>When using DOE-2 for actual billing periods, one will have to extract the appropriate hourly variable, sum it to daily and then regroup to align with the billing periods. Here's a chunk of code that will create a dummy plant, display PV-A, PS-A, PS-E and
BEPS, and extract the relevant hourly variables to normalize the BEPS to the utility bills:</p>
<p> </p>
<font size="1" face="Arial"><font size="1" face="Arial">
<p align="left">INPUT PLANT ..</p>
<p align="left"> </p>
<p align="left">PLANT-REPORT VERIFICATION = (PV-A)</p>
<p align="left">$ PV-A, EQUIPMENT SIZES</p>
<p align="left"> </p>
<p align="left">SUMMARY = (PS-A,PS-E,BEPS)</p>
<p align="left"> </p>
<p align="left">$ PS-A, PLANT ENERGY UTILIZATION SUMMARY</p>
<p align="left">$ PS-E, MONTHLY ENERGY END USE SUMMARY</p>
<p align="left">$ BEPS, BUILDING ENERGY PERFORMANCE SUMMARY</p>
<p align="left"> </p>
<p align="left">HVAC=PLANT-ASSIGNMENT ..</p>
<p align="left"> </p>
<p align="left">$ EQUIPMENT DESCRIPTION</p>
<p align="left">$ ELECTRIC DOMESTIC WATER HEATER</p>
<p align="left"> </p>
<p align="left">BOIL-1 =PLANT-EQUIPMENT TYPE=ELEC-DHW-HEATER SIZE=-999 ..</p>
<p align="left"> </p>
<p align="left">$ ELECTRIC HOT-WATER BOILER</p>
<p align="left"> </p>
<p align="left">BOIL-2 =PLANT-EQUIPMENT TYPE=ELEC-HW-BOILER SIZE=-999 ..</p>
<p align="left"> </p>
<p align="left">$ HERMETICALLY SEALED CENT CHILLER</p>
<p align="left"> </p>
<p align="left">CHIL-1 =PLANT-EQUIPMENT TYPE=HERM-CENT-CHLR SIZE=-999 ..</p>
<p align="left"> </p>
<p align="left">$ Graphics block for Data Processing ***</p>
<p align="left"> </p>
<p align="left">RP-3 = SCHEDULE THRU DEC 31 (ALL) (1,24) (1) ..</p>
<p align="left"> </p>
<p align="left">$ 8 = Total PLANT heating load (Btu/h)</p>
<p align="left">$ 9 = Total PLANT cooling load (Btu/h)</p>
<p align="left">$ 10 = Total PLANT electric load (Btu/h)</p>
<p align="left"> </p>
<p align="left">BLOCK-3-1 = REPORT-BLOCK</p>
<p align="left">VARIABLE-TYPE = PLANT</p>
<p align="left">VARIABLE-LIST = (8,9,10) ..</p>
<p align="left">BLOCK-3-2 = REPORT-BLOCK</p>
<p align="left">VARIABLE-TYPE = GLOBAL</p>
<p align="left">VARIABLE-LIST = (1) ..</p>
<p align="left">HR-3 = HOURLY-REPORT</p>
<p align="left">REPORT-SCHEDULE = RP-3</p>
<p align="left">REPORT-BLOCK = (BLOCK-3-1,BLOCK-3-2) ..</p>
<p align="left"> </p>
<p align="left">END ..</p>
<p align="left"> </p>
<p align="left">COMPUTE PLANT ..</p>
<p> </p>
<p>STOP ..</p>
</font></font>
<p> </p>
<div>
<div style="FONT-SIZE: 13px; FONT-FAMILY: Tahoma">
<div><font color="#0000ff" size="2" face="Tahoma">8=! 8=) :=) 8=) ;=) 8=) 8=( 8=) 8=() 8=) 8=| 8=) :=') 8=) 8=?<br>
Jeff S. Haberl, Ph.D.,P.E.inactive,FASHRAE,FIBPSA,......<a href="mailto:........jhaberl@tamu.edu">jhaberl@tamu.edu</a><br>
Professor........................................................................Office Ph: 979-845-6507<br>
Department of Architecture............................................Lab Ph:979-845-6065<br>
Energy Systems Laboratory...........................................FAX: 979-862-2457<br>
Texas A&M University...................................................77843-3581<br>
College Station, Texas, USA, 77843.............................http://esl.tamu.edu<br>
8=/ 8=) :=) 8=) ;=) 8=) 8=() 8=) :=) 8=) 8=! 8=) 8=? 8=) </font><font color="#0000ff" size="2" face="Tahoma">8=0<br>
</div>
</font></div>
</div>
<div style="FONT-SIZE: 16px; FONT-FAMILY: Times New Roman; COLOR: #000000">
<hr tabindex="-1">
<div id="divRpF51553" style="DIRECTION: ltr"><font color="#000000" size="2" face="Tahoma"><b>From:</b> Bldg-sim [bldg-sim-bounces@lists.onebuilding.org] on behalf of Joe Huang [yjhuang@whiteboxtechnologies.com]<br>
<b>Sent:</b> Monday, June 22, 2015 9:17 PM<br>
<b>To:</b> bldg-sim@lists.onebuilding.org<br>
<b>Subject:</b> Re: [Bldg-sim] Energy model calibration - normalizing the utility bills to month start-end<br>
</font><br>
</div>
<div></div>
<div>Maybe I'm missing something here, but why can't you just count up the degree days for the utility period?<br>
I hope you're not working with average or "typical year" degree days, but the degree days from the same time period.<br>
<br>
I also recall that the old Princeton Scorekeeping Method (PRISM) back in the 1980's allows the user to enter the degree days for that time period, so it's not a new problem.<br>
<br>
Joe<br>
<br>
<pre class="moz-signature" cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com" target="_blank">yjhuang@whiteboxtechnologies.com</a>
<a class="moz-txt-link-freetext" href="http://weather.whiteboxtechnologies.com" target="_blank">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
<div class="moz-cite-prefix">On 6/22/2015 6:09 AM, Jones, Christopher wrote:<br>
</div>
<blockquote type="cite"><style>@font-face {
font-family: Calibri;
}
@font-face {
font-family: Tahoma;
}
@font-face {
font-family: Franklin Gothic Book;
}
@font-face {
font-family: Consolas;
}
@page WordSection1 {margin: 1.0in 1.0in 1.0in 1.0in; }
P.MsoNormal {
FONT-SIZE: 12pt; FONT-FAMILY: "Times New Roman","serif"; COLOR: black; MARGIN: 0in 0in 0pt
}
LI.MsoNormal {
FONT-SIZE: 12pt; FONT-FAMILY: "Times New Roman","serif"; COLOR: black; MARGIN: 0in 0in 0pt
}
DIV.MsoNormal {
FONT-SIZE: 12pt; FONT-FAMILY: "Times New Roman","serif"; COLOR: black; MARGIN: 0in 0in 0pt
}
A:link {
TEXT-DECORATION: underline; COLOR: blue
}
SPAN.MsoHyperlink {
TEXT-DECORATION: underline; COLOR: blue
}
A:visited {
TEXT-DECORATION: underline; COLOR: purple
}
SPAN.MsoHyperlinkFollowed {
TEXT-DECORATION: underline; COLOR: purple
}
PRE {
FONT-SIZE: 10pt; FONT-FAMILY: "Courier New"; COLOR: black; MARGIN: 0in 0in 0pt
}
P.MsoAcetate {
FONT-SIZE: 8pt; FONT-FAMILY: "Tahoma","sans-serif"; COLOR: black; MARGIN: 0in 0in 0pt
}
LI.MsoAcetate {
FONT-SIZE: 8pt; FONT-FAMILY: "Tahoma","sans-serif"; COLOR: black; MARGIN: 0in 0in 0pt
}
DIV.MsoAcetate {
FONT-SIZE: 8pt; FONT-FAMILY: "Tahoma","sans-serif"; COLOR: black; MARGIN: 0in 0in 0pt
}
SPAN.HTMLPreformattedChar {
FONT-FAMILY: Consolas; COLOR: black
}
SPAN.BalloonTextChar {
FONT-FAMILY: "Tahoma","sans-serif"; COLOR: black
}
SPAN.EmailStyle21 {
FONT-FAMILY: "Franklin Gothic Book","sans-serif"; COLOR: #1f497d
}
.MsoChpDefault {
FONT-SIZE: 10pt
}
</style>
<div class="WordSection1">
<p class="MsoNormal"><span>When calibrating an energy model to utility bills the utility bills often don’t align with the month start and end. I have reviewed a couple methods to calendar normalize the utility bills but find them somewhat unsatisfactory.</span></p>
<p class="MsoNormal"><span></span> </p>
<p class="MsoNormal"><span>For example the method I am looking at does the following:</span></p>
<p class="MsoNormal"><span>The April gas bill runs from March 25 – April 24. The algorithm takes the average number of m3 per day from that bill, applies it to the days in April. Then it takes the average number of days from the May bill which runs from April
24 – May 25 and applies that average to the remaining days in April. </span></p>
<p class="MsoNormal"><span></span> </p>
<p class="MsoNormal"><span>The issue is that the March-April period has much higher HDD than the April-May period and the “normalized” gas usage is significantly lower than the simulation data for April.</span></p>
<p class="MsoNormal"><span></span> </p>
<p class="MsoNormal"><span>I am wondering if there are any papers or other sources of information as to how others approach this problem.</span></p>
<p class="MsoNormal"><span></span> </p>
<p class="MsoNormal"><span></span> </p>
<div>
<p class="MsoNormal"><span style="FONT-SIZE: 11pt; FONT-FAMILY: "Calibri","sans-serif"; COLOR: #1f497d"><img id="Picture_x0020_2" alt="cid:image003.png@01D09C46.E75BA0D0" src="cid:part1.08050307.08030902@whiteboxtechnologies.com" width="108" height="43"></span><b><span style="FONT-SIZE: 11pt; FONT-FAMILY: "Calibri","sans-serif"; COLOR: #1c467a"></span></b></p>
<p class="MsoNormal"><b><span style="FONT-SIZE: 10pt; FONT-FAMILY: "Arial","sans-serif"; COLOR: #1c467a">Christopher Jones,</span></b><b><span style="FONT-SIZE: 10pt; FONT-FAMILY: "Arial","sans-serif"; COLOR: #1f497d"></span></b><span style="FONT-SIZE: 10pt; FONT-FAMILY: "Arial","sans-serif"; COLOR: #1f497d">P.Eng.<i>
<br>
</i></span><span lang="EN-CA" style="FONT-SIZE: 10pt; FONT-FAMILY: "Arial","sans-serif"; COLOR: #1f497d">Senior Engineer<b></b></span></p>
<p class="MsoNormal"><b><span lang="EN-CA" style="FONT-SIZE: 10pt; FONT-FAMILY: "Arial","sans-serif"; COLOR: #1f497d"></span></b> </p>
<p class="MsoNormal"><b><span lang="EN-CA" style="FONT-SIZE: 10pt; FONT-FAMILY: "Arial","sans-serif"; COLOR: #1f497d">WSP Canada Inc.</span></b></p>
<p class="MsoNormal"><span lang="EN-CA" style="FONT-SIZE: 10pt; FONT-FAMILY: "Arial","sans-serif"; COLOR: #1f497d">2300 Yonge Street, Suite 2300</span></p>
<p class="MsoNormal"><span lang="EN-CA" style="FONT-SIZE: 10pt; FONT-FAMILY: "Arial","sans-serif"; COLOR: #1f497d">Toronto, ON M4P 1E4</span><span lang="EN-CA" style="FONT-SIZE: 10pt; FONT-FAMILY: "Arial","sans-serif"; COLOR: #595959"><br>
</span><span lang="EN-CA" style="FONT-SIZE: 10pt; FONT-FAMILY: "Arial","sans-serif"; COLOR: #1f497d">T +1 416-644-4226</span></p>
<p class="MsoNormal"><span lang="EN-CA" style="FONT-SIZE: 10pt; FONT-FAMILY: "Arial","sans-serif"; COLOR: #1f497d">F +1 416-487-9766</span></p>
<p class="MsoNormal"><span lang="EN-CA" style="FONT-SIZE: 10pt; FONT-FAMILY: "Arial","sans-serif"; COLOR: #1f497d">C +1 416-697-0065</span></p>
<p class="MsoNormal"><span lang="EN-CA" style="FONT-SIZE: 10pt; FONT-FAMILY: "Arial","sans-serif"; COLOR: #1f497d"></span> </p>
<p class="MsoNormal"><span lang="EN-CA" style="FONT-SIZE: 10pt; FONT-FAMILY: "Arial","sans-serif"; COLOR: #1f497d"><a href="http://www.wspgroup.com/" target="_blank">www.wspgroup.com</a>
</span><i><span lang="EN-CA" style="FONT-SIZE: 10pt; FONT-FAMILY: "Arial","sans-serif"; COLOR: #565656"></span></i></p>
</div>
<p class="MsoNormal"><span></span> </p>
</div>
<hr>
<div style="FONT-SIZE: 9pt; FONT-FAMILY: Arial,sans-serif; COLOR: gray"><br>
You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment
<a href="https://teesmail.tees.tamus.edu/owa/UrlBlockedError.aspx" target="_blank">
www.wspgroup.com/casl</a>. For any concern or if you believe you should not be receiving this message, please forward this message to us at
<a href="mailto:caslcompliance@wspgroup.com" target="_blank">caslcompliance@wspgroup.com</a> so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information
which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing,
distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.
<br>
<br>
WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership
</div>
<br>
<fieldset class="mimeAttachmentHeader" target="_blank"></fieldset> <br>
<pre>_______________________________________________
Bldg-sim mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a class="moz-txt-link-abbreviated" href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
</blockquote>
<br>
</div>
</div>
</div>
</body>
</html>