When you say "peak month in terms of load", do you mean the month
with the highest peak hourly load or the month with the largest
total load ? <br>
<br>
I need to add some caveats to Javed's response: <br>
1) he's assuming that you're using EnergyPlus or an
EnergyPlus-based simulation program. If so, then the comment about
looking at the DDY file makes sense.<br>
2) the DDY file is weakly linked to the simulation weather file
(EPW), and based not on the weather file but the design conditions
table in the ASHRAE Handbook of Fundamentals for the same WMO
station. These design conditions are calculated as near-extreme
conditions (0.4%, 1% for cooling, 99.6%, 99% for heating. etc.) from
long-term weather data and have little relationship with what's in
the simulation weather file. In addition, the DDY file contains only
Annual design conditions, and the only information on monthly
conditions are very general information on what are the coldest and
hottest months, based strictly on <br>
the average monthly temperatures.<br>
<br>
If you clarify what you're trying to determine, then I can tell you
more on what you could do.<br>
<br>
Joe<br>
<pre class="moz-signature" cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a class="moz-txt-link-freetext" href="http://weather.whiteboxtechnologies.com">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
<div class="moz-cite-prefix">On 6/22/2015 12:40 AM, Javed Iqbal
wrote:<br>
</div>
<blockquote
cite="mid:CAEF2+-nW_q-TOXkcykQC3PGzNE5zHc3W9wjvaYbJNwA2GktTQw@mail.gmail.com"
type="cite">
<div dir="ltr">
<div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;color:#0b5394">You
should check .<span class="" id=":11h.3" tabindex="-1">ddy</span>
file that comes with .<span class="" id=":11h.4" tabindex="-1">epw</span>
weather files. It has all the data that you are looking for.
Hope this helps!</div>
</div>
<div class="gmail_extra"><br>
<div class="gmail_quote">On Mon, Jun 22, 2015 at 11:23 AM,
Rasheed Ahmad <span dir="ltr"><<a moz-do-not-send="true"
href="mailto:rasheed.jmi@gmail.com" target="_blank">rasheed.jmi@gmail.com</a>></span>
wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0
.8ex;border-left:1px #ccc solid;padding-left:1ex">
<div dir="ltr">Dear all,
<div><br>
</div>
<div>I have a query , since i m doing simulations , i
want to know which month is the peak month in terms of
load for hot and cold climate regions. </div>
<div><br>
</div>
<div>The weather data which we uses , what extract does
the simulation tool takes from that weather data ,
except the relative humidity , Latitude and all.</div>
<div><br>
</div>
<div><br>
</div>
<div>It would be very helpful to me if all experts can
reply and make me understand all these points.</div>
<div><br>
</div>
<div>Thanks in advance.</div>
<div><br>
</div>
</div>
<br>
_______________________________________________<br>
Bldg-sim mailing list<br>
<a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org"
rel="noreferrer" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message
to <a moz-do-not-send="true"
href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br>
</blockquote>
</div>
<br>
<br clear="all">
<div><br>
</div>
-- <br>
<div class="gmail_signature">
<div dir="ltr"><font size="2">
<div style="font-style:italic"><i><font color="#0b5394"
face="arial, helvetica, sans-serif" size="2"><br>
</font></i></div>
<font color="#0b5394" face="arial, helvetica, sans-serif">Javed
Iqbal, LEED AP, CEA<br>
Sr. Energy Analyst</font><br>
<br>
</font></div>
</div>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
Bldg-sim mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a class="moz-txt-link-abbreviated" href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
</blockquote>
<br>
</body>
</html>