<div dir="ltr">Hi Felipe,<br><br>Heating tends to be much more critical than cooling. I recommend first checking local codes (building codes and associated such as housing or specific for housing depending on where you are and your type of building) and make sure you reach the threshold they might set on design day. If there is nothing, you could start with 17°C at night (if its housing) or 19°C during the day or if it's an office building. Anything below that will start to be uncomfortable. If it's a residential building you could eventually tolerate a margin for 1% of the time but I suggest making sure you don't get much lower than 17°C (I'd say 16°C tops at night) otherwise it'll really be very uncomfortable.<br>
<br>Best,<br></div><div class="gmail_extra"><br clear="all"><div><div dir="ltr"><div>--<br>Julien Marrec, EBCP, BPI MFBA<br>Ingénieur en efficacité énergétique du bâtiment<br>T: +33 6 95 14 42 13<br><a href="http://www.julienmarrec.com" target="_blank">www.julienmarrec.com</a><br>
<br>DoYouBuzz : <span style="color:rgb(0,0,0)"><a href="http://www.doyoubuzz.com/julien-marrec_1" target="_blank">www.doyoubuzz.com/julien-marrec_1</a><br>LinkedIn (fr) : <a href="http://www.linkedin.com/in/julienmarrec/fr" target="_blank">www.linkedin.com/in/julienmarrec/fr</a><br>
</span></div>LinkedIn (en) : <span style="color:rgb(0,0,0)"><a href="http://www.linkedin.com/in/julienmarrec" target="_blank">www.linkedin.com/in/julienmarrec</a></span></div></div>
<br><br><div class="gmail_quote">2014-02-17 17:28 GMT+01:00 Felipe Duran B-GREEN <span dir="ltr"><<a href="mailto:felipe@b-green.cl" target="_blank">felipe@b-green.cl</a>></span>:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div dir="ltr"><div>Dear Group,</div><div><br></div><div>I am wondering if there is a "overcooling" benchmark such as CIBSE overheating benchmark (1% of occupied period over 28C operative temperature). I am evaluating a naturally ventilated building and I need a benchmark to figure out if the building needs a heating system in a pretty moderated climate.</div>
<div><br></div><div>Many Thanks,</div><div><br clear="all"><div><div dir="ltr"><img src="http://www.b-green.cl/firmas/b-green_firma_F_Duran.jpg"></div></div>
</div></div>
<br>_______________________________________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br></div>