<div dir="ltr"><div><div><div><div><div><div><div><div><br></div>I'm modeling a multifamily building that uses a campus plant for cooling. I'm familiar with the USGBC document for modeling DES plants, and am currently looking at Option 1, which is an energy neutral purchased chilled water plant. Because the building is residential, the normal baseline system is System 1-PTAC. The USGBC document says to change this to a 4-pipe fan coil in order to make use of the purchased chilled water. Fair enough.<br>
<br></div>My problem is how to calculate fan power for this new baseline system. FCUs are not a normal baseline system, so there's no direction in Appendix G. Has anyone come across this before? If so, what did you do to calculate the fan power?<br>
<br></div>For what it's worth, I see three options:<br></div>1) Since I'm replacing System 1, use the formula for System 1, Pfan=CFMs*0.3. The resulting fan power is much lower than my proposed, which is a bummer, though it's primarily due to 5 DOAS fans that of course aren't in the baseline.<br>
<br></div>2) Allow TRACE to calculate the fan power using its built-in 90.1 features. This number comes out much higher than the proposed fan power, which is what tipped me off to this issue. I'm currently trying to back out how Trace arrived at the fan power it did.<br>
<br></div>3) The proposed building uses fan coils. Since the new baseline also does, set the fan powers equal and only receive credit from reduced run hours due to improved envelope and such. This sounds like a nice way to guarantee reviewer comments.<br>
<br></div>Any thoughts?<br><br></div>Thanks,<br><div><div><div><div><div><div><div><div><div><div dir="ltr"><br><span style="font-family:times new roman,serif"><span style="background-color:rgb(255,255,255)"><font size="4"><span style="color:rgb(0,0,255)"><b>Jason Kirchhoff</b></span></font></span><br>
</span><span style="font-family:times new roman,serif">Technical Director<br></span><span style="font-family:times new roman,serif">Energize Analytics<br></span><span style="font-family:times new roman,serif"><a href="http://www.energizeanalytics.com" target="_blank">www.energizeanalytics.com</a></span><br>