<div dir="ltr">Hi,<div><br>When sizing cooling equipment for apartments, the design team on my project used a worst case scenario approach of maxing out all internal loads. For instance, lighting would be on during the day, with full occupancy and all plug equipment running, while the sun is hitting the windows. Adjacent rooms would be considered without cooling.<br>
For LEED, the sizing for the baseline is based on schedules representing typical operations for occupancy, lighting, plug, etc. That leads the baseline to size equipment that has smaller capacity than what considered for the proposed design.<br>
There's an extra dimension, in the fact the design team sized equipment for each individual room, reaching their peak load at different times of the day. So the total cooling capacity is the sum of the worst possible scenarios. The model currently uses a single zone per apartment, with a not so worst case scenario.<br>
How do I solve this conundrum? Am I missing something?<br>Thanks,Patrick<br></div></div>