<div dir="ltr">HI,<br><div><br>I faced a similar situation When I was modeling perimeter versus interior systems for an office floor plate, I saw that each zone and its loads are isolated in the calculations and eQUEST does not factor any sort of heat transfer between zones (adiabatic) in eQUEST. So for example if there is curtain wall facade, the solar loads only applied to that exterior zone and did not transfer into the interior zones. We therefore encountered issues with oversizing for the non-exterior zones of the office space when modeling as designed.<br>
<br>As I understand this appears to be case with roof loads being transferred to plenums only and not the occupied space below as well. <br><br>I dont remember exactly how we resolved this and infact I think we took that oversizing penalty in our model. But one of the suggestions we were toying with was that we make an opening or model the internal wall as an air film. <br>
<br></div><div>Ramya<br></div></div><div class="gmail_extra"><br><br><div class="gmail_quote">On Wed, Aug 21, 2013 at 4:01 PM,  <span dir="ltr"><<a href="mailto:bldg-sim-request@lists.onebuilding.org" target="_blank">bldg-sim-request@lists.onebuilding.org</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">Send Bldg-sim mailing list submissions to<br>
        <a href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a><br>
<br>
To subscribe or unsubscribe via the World Wide Web, visit<br>
        <a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
or, via email, send a message with subject or body 'help' to<br>
        <a href="mailto:bldg-sim-request@lists.onebuilding.org">bldg-sim-request@lists.onebuilding.org</a><br>
<br>
You can reach the person managing the list at<br>
        <a href="mailto:bldg-sim-owner@lists.onebuilding.org">bldg-sim-owner@lists.onebuilding.org</a><br>
<br>
When replying, please edit your Subject line so it is more specific<br>
than "Re: Contents of Bldg-sim digest..."<br>
<br>Today's Topics:<br>
<br>
   1. Re: [Equest-users] Roof Conduction Load (Joe Huang)<br>
   2. Job Posting: Senior Energy Engineer at Ecology Action<br>
      (Philip Boutelle)<br>
<br><br>---------- Forwarded message ----------<br>From: Joe Huang <<a href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>><br>To: Jeremiah Crossett <<a href="mailto:jcrossett@phasechange.com">jcrossett@phasechange.com</a>><br>
Cc: "<<a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>>" <<a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>>, "Bldg-sim2 \(<a href="mailto:Bldg-sim@lists.onebuilding.org">Bldg-sim@lists.onebuilding.org</a>\)" <<a href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a>>, Bhartendu Awasthi <<a href="mailto:bhartendu.awasthi90@gmail.com">bhartendu.awasthi90@gmail.com</a>><br>
Date: Tue, 20 Aug 2013 13:04:48 -0700<br>Subject: Re: [Bldg-sim] [Equest-users] Roof Conduction Load<br><u></u>

  
    
    
  
  <div text="#000000" bgcolor="#ffffff">
    Jeremiah,<br>
    <br>
    Your  question is not quite on the mark because what I've described
    is downstream from the calculation of room loads where techniques
    such as the Weighting Factor or the Heat Balance methods come into
    play.   Before I get to that issue, though, I want to point out that
    the "Adjust Loads" procedure I described is done automatically by
    DOE-2 and totally invisible to the User;  I did so only to explain
    why<span> Bhartendu</span> (the original poster) was not seeing any
    conduction loads through the ceiling.  <br>
    <br>
    Now, back to this "Adjust Loads" procedure, there is no simulation
    program I know of that solves simultaneously for the heat flows and
    the zone temperature.  DOE-2 does it in the two-step way that others
    and I have just described. When you said "compared to the Heat
    Balance Method", I assume you're thinking of EnergyPlus.  So, how
    does EnergyPlus meet this problem?  Whereas DOE-2 does one year of
    LOADS and then one year of SYSTEMS, EnergyPlus does them in the same
    time step, but also sequentially. Therefore,  EnergyPlus calculates
    the heat flows using the zone temperature from the previous time
    step which are then used in its HVAC simulation without adjustment.
    This should be okay when zone temperatures don't change, but what
    about at morning start-up when temperatures could change by 5-10 F
    within one hour?  I've always wondered whether that's why EnergyPlus
    gives much lower heating loads in mild California climates than does
    DOE-2?  As far as which procedure is "more realistic", I can't say.<br>
    <br>
    Joe<br>
    <pre cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
<a href="mailto:yjhuang@whiteboxtechnologies.com" target="_blank">yjhuang@whiteboxtechnologies.com</a>
<a href="http://weather.whiteboxtechnologies.com" target="_blank">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data
(o) <a href="tel:%28925%29388-0265" value="+19253880265" target="_blank">(925)388-0265</a>
(c) <a href="tel:%28510%29928-2683" value="+15109282683" target="_blank">(510)928-2683</a>
"building energy simulations at your fingertips"
</pre>
    <br>
    On 8/19/2013 9:57 PM, Jeremiah Crossett wrote:
    <blockquote type="cite">
      <div dir="ltr">
        <div class="gmail_default" style="font-family:tahoma,sans-serif;font-size:small;color:rgb(51,51,51)">Joe, Just
          wondering,  given your expertise how would you compare this to
          the heat balance method.., and what do you think is more
          realistic? </div>
        <div class="gmail_extra"><br clear="all">
          <div>
            <div><font color="#336666"><i><br>
                </i></font></div>
            <div><b><span><font color="#336666" size="1"><b style="font-family:Verdana,sans-serif"><br>
                    </b></font></span></b></div>
            <div>
              <div style="text-align:center"><b><span><font color="#000099" size="1"><b style="font-family:Verdana,sans-serif">Jeremiah D. Crossett</b><span style="font-family:Verdana,sans-serif">  </span><font face="Verdana, sans-serif">| Senior </font><font face="Verdana, sans-serif">Analyst</font><font face="Verdana, sans-serif">  |  Phase Change
                        Energy Solutions</font></font></span></b></div>
              <b>
                <div style="text-align:center"><b><span><font size="1"><font color="#000099" face="Verdana,
                          sans-serif">120 E. Pritchard St.  | Asheboro,
                          NC 27203  | Mobile <a href="tel:503-688-8951" value="+15036888951" target="_blank">503-688-8951</a></font></font></span></b></div>
                <span style="color:rgb(153,153,153)">
                  <div style="text-align:center"><b style="background-color:transparent"><b style="font-family:Verdana,sans-serif;font-size:8pt"><a href="http://www.phasechange.com" target="_blank">www.phasechange.com</a> </b></b></div>

                </span></b></div>
            <div>
              <div style="text-align:center">  <img src="http://i.imgur.com/Sldxf.jpg"></div>
              <b><b style="font-family:Verdana,sans-serif"><font color="#0000fe"><br>
                  </font></b></b></div>
            <div><b style="color:rgb(0,0,254);font-size:13px;font-family:Verdana,sans-serif"><b><span style="font-size:10pt"><br>
                  </span></b></b></div>
            <div><font color="#0000fe" face="Verdana, sans-serif"><span style="font-weight:800"><br>
                </span></font></div>
          </div>
          <br>
          <br>
          <div class="gmail_quote">On Mon, Aug 19, 2013 at 6:14 PM, Joe
            Huang <span dir="ltr"><<a href="mailto:yjhuang@whiteboxtechnologies.com" target="_blank">yjhuang@whiteboxtechnologies.com</a>></span>
            wrote:<br>
            <blockquote class="gmail_quote" style="margin:0pt 0pt 0pt 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
              <div text="#000000" bgcolor="#ffffff"> Just to repeat what
                David and Rodrigo have already sad, DOE-2 calculates
                conduction loads in a two step process. In LOADS, a
                constant reference temperature is specified, which DOE-2
                uses to calculate the amount of heat flow through the
                surfaces. This is the LOADS loads summarized in the LS-E
                and LS-F reports.  In SYSTEMS, DOE-2 calculates the true
                temperature of the zone based on the loads passed from
                LOADS, as well as the actions of the HVAC system.  In
                the course of this calculation, the heat flows ("loads")
                from LOADS are adjusted, but this is not done surface by
                surface, but in total using the so-called "Zone
                Conductance" times the difference between the actual
                zone temperature and the reference temperature used in
                LOADS.  At this point, heat flows through internal walls
                are also considered, using the  difference between this
                hour's zone temperature and the previous hour's zone
                temperature of the adjacent space, e.g., the Attic or
                Plenum.  If you are interested in this number, I believe
                it can be extracted in an hourly report.  <br>
                <br>
                In reference to Rodrigo's question, I don't see any
                benefit in forcing a heat flow between the room and the
                attic by using different reference temperatures.   You
                will simply get a constant heat flow at that temperature
                difference throughout the simulation. In reality, attics
                are generally colder than the room in the winter and
                warmer than the room in the summer, so the derived heat
                flow with this temperature difference doesn't get you
                any closer to reality, in my opinion.<br>
                <br>
                Joe<br>
                <pre cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
<a href="mailto:yjhuang@whiteboxtechnologies.com" target="_blank">yjhuang@whiteboxtechnologies.com</a>
<a href="http://weather.whiteboxtechnologies.com" target="_blank">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data
(o) <a href="tel:%28925%29388-0265" value="+19253880265" target="_blank">(925)388-0265</a>
(c) <a href="tel:%28510%29928-2683" value="+15109282683" target="_blank">(510)928-2683</a>
"building energy simulations at your fingertips"
</pre>
                <div>
                  <div> <br>
                    On 8/19/2013 12:05 PM, David Wood wrote:
                    <blockquote type="cite">
                      <div>
                        <div>
                          <div>Hi All,<br>
                            <br>
                          </div>
                          The LS-C report comes from the LOADS
                          simulation portion of DOE 2.2. The plenum
                          reference temperature used in LOADS is
                          adjusted in the SYSTEMS portion of the program
                          and the loads in the spaces adjacent to the
                          plenum are corrected <br>
                          correspondingly.<br>
                          <br>
                        </div>
                        Dave Wood<br>
                      </div>
                      <div><br>
                        <br>
                        <div>On Thu, Aug 8, 2013 at 8:58 AM, Rodrigo
                          Cerqueira <span><<a href="mailto:rodrigo.cerqueira@mra.qc.ca" target="_blank">rodrigo.cerqueira@mra.qc.ca</a>></span>
                          wrote:<br>
                          <blockquote>
                            <div lang="FR-CA">
                              <div>
                                <p><span lang="EN-US">Hi, </span></p>
                                <p> <span lang="EN-US">This happens
                                    because the load calculation is made
                                    with a fixed temperature (see
                                    picture). All the spaces, include
                                    plenum zones, have the same
                                    temperature by default (70°F). So,
                                    all roof load appears in the plenum
                                    spaces. To considerate the roof
                                    load, you have to change this
                                    temperature in plenum spaces and a
                                    part of roof load will appear like
                                    "internal surface conduction". But
                                    I'm not sure if this is a good
                                    practice. </span><span>Maybe
                                    someone else has an opinion about
                                    that. </span></p>
                                <p><span>   </span></p>
                                <p><span><img></span><span>
                                  </span></p>
                                <p><span>   </span></p>
                                <p><b><span>Rodrigo Cerqueira, </span></b><span>ing.

                                    jr, M.Ing.<b> </b></span></p>
                                <p><b><span>Simulation énergétique </span></b></p>
                                <p><span>   </span></p>
                                <p><span><img alt="signatureCouriel"> </span></p>
                                <p><span>   </span></p>
                                <p><span>   </span></p>
                                <p><span>   </span></p>
                                <div>
                                  <p><b><span lang="FR">De :</span></b><span lang="FR"> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>
                                      [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>]
                                      <b>De la part de</b> Bhartendu
                                      Awasthi<br>
                                      <b>Envoyé :</b> 8 août 2013 06:35<br>
                                      <b>À :</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a>;
                                      <a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a><br>
                                      <b>Objet :</b> [Equest-users] Roof
                                      Conduction Load </span></p>
                                </div>
                                <p>   </p>
                                <div>
                                  <p>Hi All, </p>
                                  <div>
                                    <p>   </p>
                                  </div>
                                  <div>
                                    <pre><span>I am doing an energy simulation model in eQuest. I noticed that the load through roof conduction in LS-C is zero where as in LS-B (for plenum space) it is showing some load.</span><span>    </span></pre>

                                    <pre><span>     </span></pre>
                                    <pre><span>As per my understanding this load should appear in LS-C also.</span><span>    </span></pre>
                                    <pre><span>Also, if I reduce the U value of the roof, the load through roof reduces and can be accounted in LS-B only (plenum space).</span><span>    </span></pre>
                                    <pre><span>     </span></pre>
                                    <pre><span>Refer attached LS-C and LS-B reports.</span><span>    </span></pre>
                                    <pre><span>Any help will be appreciated.</span><span>    </span></pre>
                                    <pre><span>     </span></pre>
                                    <pre><span>     </span></pre>
                                    <pre><span>Thanks & Regards</span><span>    </span></pre>
                                    <pre><span>     </span></pre>
                                    <pre><span>Bhartendu Awasthi</span><span>    </span></pre>
                                  </div>
                                </div>
                              </div>
                            </div>
                            <br>
_______________________________________________<br>
                            Bldg-sim mailing list<br>
                            <a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
                            To unsubscribe from this mailing list send
                             a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
                            <br>
                          </blockquote>
                        </div>
                        <br>
                        <br>
                        <br>
                        -- <br>
                        <div>
                          <div><span><span><span></span></span><span><span></span></span><span><span>Regards,<br>
                                </span></span></span></div>
                          <div><span><span><span></span><br>
                                David S. Wood<br>
                                Principal<br>
                                Wood, Byk & Associates<br>
                                office:    <a href="tel:610.347.0710" value="+16103470710" target="_blank">610.347.0710</a><br>
                              </span></span></div>
                          <span><span>mobile:  <a href="tel:610.247.1208" value="+16102471208" target="_blank">610.247.1208</a></span></span><br>
                        </div>
                      </div>
                      <pre><fieldset></fieldset>
_______________________________________________
Bldg-sim mailing list
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
                    </blockquote>
                  </div>
                </div>
              </div>
              <br>
              _______________________________________________<br>
              Bldg-sim mailing list<br>
              <a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
              To unsubscribe from this mailing list send  a blank
              message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
              <br>
            </blockquote>
          </div>
          <br>
        </div>
      </div>
    </blockquote>
  </div>

<br><br>---------- Forwarded message ----------<br>From: Philip Boutelle <<a href="mailto:philboutelle@gmail.com">philboutelle@gmail.com</a>><br>To: <a href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a>, <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
Cc: <br>Date: Wed, 21 Aug 2013 09:51:03 -0700<br>Subject: [Bldg-sim] Job Posting: Senior Energy Engineer at Ecology Action<br><div dir="ltr"><div>Immediate opening for a full-time senior energy engineer at Ecology Action in Santa Cruz, CA</div>
<div><br></div><div>Job description and how to apply: <a href="http://ecoact.iapplicants.com/ViewJob-472387.html" target="_blank">http://ecoact.iapplicants.com/ViewJob-472387.html</a></div>

<div><br></div><div>About Ecology Action:</div>Ecology Action is a leading provider of innovative marketing and engagement programs that overcome barriers to reducing energy use and achieving environmental sustainability. Ecology Action delivers programs statewide to serve consumers, businesses, IOUs, government agencies and community partners. <br>


<div><br></div><div><p><b><span style="font-size:9pt;color:rgb(0,112,192)">--</span></b></p>

<p><b><span style="font-size:9pt;color:rgb(0,112,192)">Phil Boutelle</span></b><span style="font-size:9pt;color:rgb(0,112,192)"><span>  |  Energy Engineer 
|  Ecology Action  |  <span title="Call with Google Voice"><span title="Call with Google Voice"><a href="tel:831.515.1364" value="+18315151364" target="_blank">831.515.1364</a></span></span>  |  </span><a href="mailto:pboutelle@ecoact.org" target="_blank"><span style="color:rgb(0,112,192)">pboutelle@ecoact.org</span></a> 
|  <a href="http://www.ecoact.org/" target="_blank"><span style="color:rgb(0,112,192)">www.ecoact.org</span></a></span></p></div><div><br></div></div>
<br>_______________________________________________<br>
Bldg-sim mailing list<br>
<a href="mailto:Bldg-sim@lists.onebuilding.org">Bldg-sim@lists.onebuilding.org</a><br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
<br></blockquote></div><br></div>