    <div class="moz-cite-prefix">This data is way better than I can get,
      Aaron.  I don't know the CFMs these fans move, but for me it is
      normal to see the smallest H.P. for the smallest 1.5 / 2 ton fan
      coil at 1/5 H.P.  Seeing something lower than that would be a
      godsend.  Who made these fans and how much air do they move? 
      Typically the fan coil manufacturers that I work with don't bother
      giving fan H.P. (listed on your chart as Motor H.P.?) but rather
      jump right to the motor nominal H.P. which is always higher.<br>
      <br>
      But I agree with you regarding amps.  Typically the amps are much
      higher than the corresponding H.P. for unknown reasons.  Startup
      current?  Perhaps...<br>
      <br>
      I also note that your data has higher watts at higher voltages in
      some cases, for unknown reasons, along with "peak" watts at
      208/230 in other cases.  I can't explain that.<br>
      <br>
      Thanks for sending this, but if you can identify the manufacturer
      and the product, I would be very grateful.<br>
      <br>
      <br>
      Cheers!<br>
      <br>
      <br>
      <pre class="moz-signature" cols="72">Robert Wichert P.Eng. LEED AP BD&C
+1 916 966 9060
FAX +1 916 966 9068
===============================================
</pre>
      On 2/22/2013 1:51 PM, Aaron Smith wrote:<br>
    </div>
    <blockquote cite="mid:35FB29D828F34C56976BFF25EDB6B98B@MRENG.local"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      <meta name="Generator" content="Microsoft Word 11 (filtered
        medium)">
      <!--[if !mso]>
<style>
v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style>
<![endif]--><o:smarttagtype
        namespaceuri="urn:schemas-microsoft-com:office:smarttags"
        name="State">
        <o:smarttagtype
          namespaceuri="urn:schemas-microsoft-com:office:smarttags"
          name="place">
          <!--[if !mso]>
<style>
st1\:*{behavior:url(#default#ieooui) }
</style>
<![endif]-->
          <style>
<!--
 /* Style Definitions */
 p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:12.0pt;
        font-family:"Times New Roman";}
a:link, span.MsoHyperlink
        {color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {color:purple;
        text-decoration:underline;}
p.MsoPlainText, li.MsoPlainText, div.MsoPlainText
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:10.0pt;
        font-family:"Courier New";}
@page Section1
        {size:8.5in 11.0in;
        margin:1.0in 77.95pt 1.0in 77.95pt;}
div.Section1
        {page:Section1;}
-->
</style>
          <div class="Section1">
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">Robert,<o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt"><o:p> </o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">I’ve also run into problems obtaining combined
                  (fan and motor)
                  efficiency and input power, mostly with terminal units
                  such as heat pumps and
                  fan coil units but also with individual fans.  What
                  I’ve often done
                  is used the watts listed in their electrical tables. 
                  For example, below if
                  you take their size 20 at high fan speed, they
                  classify the motor HP at 1/30HP
                  or 25W (output power).  I’ve taken the subsequent
                  columns to mean
                  input power so the watts at 115V is then 57W which
                  would make the motor is 44%
                  efficient and that seems reasonable to me.  The listed
                  amps don’t necessarily
                  equate to the same wattages, they are usually higher
                  so my only theory is that
                  this is the starting amps.  <o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt"><o:p> </o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">I’d be interested in finding out what other
                  have to say.  I
                  have tried talking to some local equipment reps
                  without any luck.<o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt"><o:p> </o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">Aaron<o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt"><o:p> </o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt"><img id="_x0000_i1025"
                    src="cid:part1.09000801.07010206@wichert.org"
                    height="519" width="761"><o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt"><o:p> </o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt"> <o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">Aaron Smith, P.Eng <o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">M&R Engineering <o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt"><o:p> </o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">-----Original Message-----<br>
                  From: RobertWichert [<a class="moz-txt-link-freetext" href="mailto:robert@wichert.org">mailto:robert@wichert.org</a>] <br>
                  Sent: Friday, February 22, 2013 12:25 PM<br>
                  To: <a class="moz-txt-link-abbreviated" href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a>; Scott Blunk<br>
                  Subject: [Bldg-sim] Fan Power</span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt"><o:p> </o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">This is a DOE-2 question, I think, but I am
                  applying it to
                  EnergyPro.  I <o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">am asking here in the hopes that some will
                  have a more in-depth <o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">knowledge of DOE-2 and how it relates to fan
                  power.  I am also
                  hoping <o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">that some here will be able to reflect on the
                  theory and application of
                  <o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">fan power and energy as it relates to actual
                  systems and modeling.<o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt"><o:p> </o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">When inputting indoor fan power, I have used
                  many sources for the fan <o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">power.  I sometimes use the motor nameplate,
                  which I believe is
                  too high <o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">in every case.<o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt"><o:p> </o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">I also sometimes use <st1:state w:st="on"><st1:place
                      w:st="on">FLA</st1:place></st1:state>
                  or RLA, which I also do not believe are <o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">accurate, but sometimes give more realistic
                  numbers.<o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt"><o:p> </o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">Some manufacturers give fan BHP at design
                  conditions, which I find to
                  be <o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">very helpful, but not everybody is that
                  helpful.<o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt"><o:p> </o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">It has been suggested that I calculate the fan
                  BHP using the
                  theoretical <o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">formula *** Fan BHP = (cfm x static press
                  "w.c.) / (6356 x fan <o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">efficiency) *** and then use a conservative
                  fan efficiency (maybe 50%) <o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">for a good number.  This gives a much lower
                  value than the other <o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">methods, and I am trying to see if there is
                  anything wrong with this <o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">approach.<o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt"><o:p> </o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">As I understand the usage, indoor fan power is
                  divided by motor and <o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">drive efficiency to come up with fan energy. 
                  So the fan BHP is
                  the <o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">starting point.  Having this too high drives
                  up fan energy,
                  sometimes <o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">dramatically, and can influence the proposed
                  case quite a bit if there <o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">are lots of fans, even small fans.<o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt"><o:p> </o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt"><o:p> </o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">Any thoughts on this approach would be very
                  much appreciated.<o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt"><o:p> </o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt"><o:p> </o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt"><o:p> </o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">-- <o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">Robert Wichert P.Eng. LEED AP BD&C<o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">+1 916 966 9060<o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">FAX +1 916 966 9068<o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt"><o:p> </o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt"><o:p> </o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt"><o:p> </o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt"><o:p> </o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt"><o:p> </o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt"><o:p> </o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt"><o:p> </o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt">===============================================<o:p></o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt"><o:p> </o:p></span></font></p>
            <p class="MsoPlainText"><font face="Courier New" size="2"><span
                  style="font-size:
                  10.0pt"><o:p> </o:p></span></font></p>
          </div>
        </o:smarttagtype></o:smarttagtype></blockquote>
    <br>
  </body>
</html>